    Originally posted by billvon
    Alabama Power doesn't have a statewide policy on net metering, and you have to talk directly to the utility, but they can (and have) approved solar grid tie installations.

    That's going to be way more cost effective than a battery based system.

    You mean going guerilla? If you have an older bidirectional mechanical meter - maybe. But you risk disconnection, fines etc.
    Cool. I remember visiting the Alabama Power company website and it seemed to me like they purposefully left any information out on gt systems in their green energy section.

    I do get that it will save money on the long and short run. But saving money is only part of the point. I'm really trying to get a feel on whether it could possibly be a cost effective off grid, which so far I'm only getting a resounding "NO"

    Guerrilla? No, I'm just curious.

    Comment

    • Sunking
      Solar Fanatic
      • Feb 2010
      • 23301

      #17
      Originally posted by PhillyTitan
      There is no need to insult me sunking.
      Was not trying to Insult You, get your attention real fast before you make a huge mistake. By federal law, public utilities are required to off Grid Tie systems. What is not Law is that the utility must pay you retail for what you sell them. In my home state of TX you can connect to the Grid, but dpending on where you are located in TX you may only get 5-cents for what you sell, and buy at 13 cents. Where I was rates are 7.6-cents per Kwh for all you want up to 2000 Kwh then the price drops to 7.2-cents above 2000 Kwh. To grid tie rates go up to 13-cents for what you buy, and 5 cents for what you sell.

      You will have to call you local utility to get details. You should be thankful to live in AL where there is no state requirement for Net Metering. That means you have very low rates and abundant supplies of energy. In states with Net Metering Laws electric rates are much higher to cover the cost at your neighbors expense.

      However with Off-Grid there is no way possible to save any money. It will cost you many times more than buying it. 10 years ago 20 times more, today with government money pouring into panel manufacturing down to 10 times more. So don't take anything off-grid unless you have no other alternative. There is no justification for doing so.
      MSEE, PE

      Comment

      • PhillyTitan
        Member
        • Jul 2014
        • 66

        #18
        Originally posted by Sunking

        However with Off-Grid there is no way possible to save any money. It will cost you many times more than buying it. 10 years ago 20 times more, today with government money pouring into panel manufacturing down to 10 times more. So don't take anything off-grid unless you have no other alternative. There is no justification for doing so.
        I would agree with you if the cost of doing so were the only factor. In my opinion there can be tremendous
        Advantages of energy independence but that's a discussion for another thread.

        I'm really talking about the feasibility of making a low cost solution for air conditioning that happens to also be off grid. (This isn't a true off grid house, you know. I'm only talking about the addition.)Then maybe when the time is right, or if the unthinkable happens, apply what I've learned to take it to the next step.

        I'm not one of those geeky prepers who keeps a bug out vehicle, and a cabin in the woods with 1000 pounds of canned food. But if the US dollar ever collapsed, or I there is a super virus outbreak, or Iran takes us back to the Stone Age when they develop an EMP device, then I'd rather not be one of those who died immediately because I didn't have a plan B.

        If a low cost solution IS viable, then maybe I'll start looking into ways to make it more viable.
        EG building my own solar panels, and batteries, improving circuit designs and building the components myself, etc. I am trying to start small but I really have a grand vision if it works out.

        Comment

        • PhillyTitan
          Member
          • Jul 2014
          • 66

          #19
          So can someone run the math and apply it to my situation?
          I don't know the Ah rating of shockah's $300 battery, but let's say they're 200ah.

          2x 200ah batteries, for $600
          running 660 watts for 5-7 hours a day.
          150 days/ year average.

          Please show the math how you came up with the $ amount per KWh.

          Comment

          • Mike90250
            Moderator
            • May 2009
            • 16020

            #20
            Look to the old South, as to how people can live without Air Conditioning. It's nice to have, but seldom a "live or die" situation.

            Wide porches, build to take advantage of local breeze, shaded windows, insulated, thermal mass.

            We are going into our 3rd, 90+ day here, and passive design has our indoor temp at 72F, 4pm.
            Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
            || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
            || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

            solar: http://tinyurl.com/LMR-Solar
            gen: http://tinyurl.com/LMR-Lister

            Comment

            • PhillyTitan
              Member
              • Jul 2014
              • 66

              #21
              Originally posted by Mike90250
              Look to the old South, as to how people can live without Air Conditioning. It's nice to have, but seldom a "live or die" situation.

              Wide porches, build to take advantage of local breeze, shaded windows, insulated, thermal mass.

              We are going into our 3rd, 90+ day here, and passive design has our indoor temp at 72F, 4pm.
              Mike you are correct. But the old movies where they are sitting on the porch fanning themselves in the 95* weather with >95% humidity, and sweating like pigs doesn't appeal to me. They looked really miserable. The only wind in central Alabama is in the city or on top of a mountain (other than our infamous tornados).

              I'd be interested to read more on the setup for your "passive design". Care to share any more details?

              Comment

              • Sunking
                Solar Fanatic
                • Feb 2010
                • 23301

                #22
                Originally posted by PhillyTitan
                So can someone run the math and apply it to my situation?
                I don't know the Ah rating of shockah's $300 battery, but let's say they're 200ah.

                2x 200ah batteries, for $600
                running 660 watts for 5-7 hours a day.
                150 days/ year average.
                200 AH is meaningless without a voltage. So I can only assume you are talking about 6 volt 200 AH golf cart batteries wired in series to make 12 volts. 12 volts x 200 AH = 2400 watt hours. For an off-grid battery system you size the battery to give you 5 days run time. In reality this only gives you 2.5 days as you never want to discharge the batteries more than 50%. Put another way you only discharge your batteries 20% each day.

                Battery cycle life and Depth of Discharge is directly related. The deeper you discharge them, the fewer cycles you will get out of them. Here is a chart to display:



                Discharge 20% each day and you get about 5 years, 50%just over a year, 100% just a couple of months. In your case using a 12 volt 200 AH is 2400 watt hours and you want to drain 600 watts x 7 hours = 4200 watt hours. Not going to work.

                So your air conditioner uses 600 watts and you want to run it 7 hours per day. 600 watts x 7 hours = 4200 watt hours. That means you need a minimum of 4200 watt hours x 5 days = 21,000 watt hours or 21 Kwh. To find the battery AH capacity is easy Amp Hours = Watt Hours / Battery Voltage. So you get:

                1750 AH @ 12 volts
                875 AH @ 24 volts
                438 AH @ 48 volts

                To determine cost a good 5 year battery will cost you $220/Kwh and weighs roughly 55 pounds per Kwh. So for a 21 Kwh battery will cost around 21 x $220 = $4620 and weigh in around 21 x 55 pounds = 1155 pounds.
                MSEE, PE

                Comment

                • PhillyTitan
                  Member
                  • Jul 2014
                  • 66

                  #23
                  Sorry sunking I had to reread each section of your post a couple times and still didn't get it all.
                  First, I was talking about 2x 200 ah agm batteries at 12v each. I don't have the knowledge what is proper. Whether to wire them in series to make 24volts or in parallel to stay at 12v. Advantages/disadvantages??
                  I know that the lower priced, all-inclusive 1Kw solar kits come with a 12v charge controller, so I was aiming at keeping the system at that.

                  I am totally flexible and purchase a higher rated controller and inverter if it means I can get down to under 1000 lbs of batteries.

                  Comment

                  • Sunking
                    Solar Fanatic
                    • Feb 2010
                    • 23301

                    #24
                    Originally posted by PhillyTitan
                    Sorry sunking I had to reread each section of your post a couple times and still didn't get it all.
                    First, I was talking about 2x 200 ah agm batteries at 12v each. I don't have the knowledge what is proper. Whether to wire them in series to make 24volts or in parallel to stay at 12v. Advantages/disadvantages??
                    I know that the lower priced, all-inclusive 1Kw solar kits come with a 12v charge controller, so I was aiming at keeping the system at that.

                    I am totally flexible and purchase a higher rated controller and inverter if it means I can get down to under 1000 lbs of batteries.
                    Inverter, panels, and controllers have nothing to do with battery weight and size. Battery capacity is totally dependent on daily watt hour usage. So if you use 4200 watt hours each day, you are going to need a 21,000 wh (21 Kwh) battery.

                    For a system of 1000 watts o rmore will require a minimum of 24 volt battery. However 48 volt is more economical and more efficient. So for a 21 Kwh battery the required Amp Hours are:

                    875 AH @ 24 volts
                    475 AH @ 48 volts.

                    For a 24 volt system you are looking at using 4 Rolls 6 volt 820 AH batteries (6CS25PS) wired in series to make 24 volts.
                    MSEE, PE

                    Comment

                    • PhillyTitan
                      Member
                      • Jul 2014
                      • 66

                      #25
                      Originally posted by Sunking
                      Inverter, panels, and controllers have nothing to do with battery weight and size. Battery capacity is totally dependent on daily watt hour usage. So if you use 4200 watt hours each day, you are going to need a 21,000 wh (21 Kwh) battery.
                      Holy smokes! So technically, this is just the case if I wanted the bank to last 5 years?

                      Did you calculate the fact that this will only be running 150-200 days/year? Could you say roughly 10 kWh supply would last 5 years if you only needed that much kWh would be running for half the days of the year or am I off base?

                      Comment

                      • russ
                        Solar Fanatic
                        • Jul 2009
                        • 10360

                        #26
                        For your standby/emergency system you want a generator - not solar
                        [SIGPIC][/SIGPIC]

                        Comment

                        • jony101
                          Member
                          • Jun 2014
                          • 99

                          #27
                          I build many 12 volt swamp coolers to stay cool here in california, humidity rarely gets over 50 so they work great. I always look at youtube among other areas to learn ways to improve on the design of the swamp coolers I make.
                          There was a design I saw on youtube of someone using a heater core radiator with hoses going into a ice chest filled with cold water, he had a fan blowing on the radiator. the pump circulated the cold water through the radiator. He had a thermometer showing a drop in temperature. This is a very primitive A/C. The only downfall I saw was feeding ice to the ice chest to keep it cold. In my mind I had and idea, what if you just filled a 12 volt fridge full of water and ran hoses from there instead of an ice chest. You would always have cold water without needing ice.
                          12 volt fridge only uses 4 to 5 amps when its running. Water pump uses 1 amp, you can use a endless breeze fantastic fan that produces 900 cfm of airflow at less that 3 amps as the air source. I know something like that would easily run off my 240 watt solar panel.
                          Your idea to get AC on solar/batteries is possible but you need to think outside the box and maybe build something on your own.
                          If I really needed AC, I would definitely build something like the above. For me it would be a challenge that I could not refuse, I would not give up too easily.
                          But also dont overlook swamp coolers, growing up in texas with high humidity and temperatures in the 100's, and giant mosquitos we never had an AC, all we had was a giant swamp cooler in the living room and that kept the whole house cool. You can build your own 12 volt one cheaply and they are very solar friendly.

                          Comment

                          • PhillyTitan
                            Member
                            • Jul 2014
                            • 66

                            #28
                            Originally posted by russ
                            For your standby/emergency system you want a generator - not solar
                            That's not really what I'm going for either (oil dependence)

                            Comment

                            • PhillyTitan
                              Member
                              • Jul 2014
                              • 66

                              #29
                              Originally posted by jony101
                              I build many 12 volt swamp coolers to stay cool here in california, humidity rarely gets over 50 so they work great. I always look at youtube among other areas to learn ways to improve on the design of the swamp coolers I make.
                              There was a design I saw on youtube of someone using a heater core radiator with hoses going into a ice chest filled with cold water, he had a fan blowing on the radiator. the pump circulated the cold water through the radiator. He had a thermometer showing a drop in temperature. This is a very primitive A/C. The only downfall I saw was feeding ice to the ice chest to keep it cold. In my mind I had and idea, what if you just filled a 12 volt fridge full of water and ran hoses from there instead of an ice chest. You would always have cold water without needing ice.
                              12 volt fridge only uses 4 to 5 amps when its running. Water pump uses 1 amp, you can use a endless breeze fantastic fan that produces 900 cfm of airflow at less that 3 amps as the air source. I know something like that would easily run off my 240 watt solar panel.
                              Your idea to get AC on solar/batteries is possible but you need to think outside the box and maybe build something on your own.
                              If I really needed AC, I would definitely build something like the above. For me it would be a challenge that I could not refuse, I would not give up too easily.
                              But also dont overlook swamp coolers, growing up in texas with high humidity and temperatures in the 100's, and giant mosquitos we never had an AC, all we had was a giant swamp cooler in the living room and that kept the whole house cool. You can build your own 12 volt one cheaply and they are very solar friendly.
                              I wish swamp coolers would do the trick, but they can't even cool my 11x4' laundry room (converted storage room). That primitive AC sounds like a neat idea though.

                              Comment

                              • russ
                                Solar Fanatic
                                • Jul 2009
                                • 10360

                                #30
                                Preppers? I have been hearing that BS as long as I can remember - I am 69 so that goes back a ways.
                                [SIGPIC][/SIGPIC]