Question on adding circuit breaker to solar panels

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • dilligaf13
    Junior Member
    • Sep 2026
    • 1

    #1

    Question on adding circuit breaker to solar panels

    I've got 9 Hyundai Hid-S305 solar panels wired in series (each panel is max rated for 305 watts, 40.1 Volts, 9.9 amps) and I'm looking to put a circuit breaker and quick disconnect between the panels and inverter. The circuit breaker and QD are each rated for 1000 volts and 40 amps and want to make sure they will be able to handle the power produced from the 9 panels. TIA

    [DIHOOL DC 1000V Circuit Breaker, Non Polarized, 40 Amp, 2 Pole, AC DC Disconnect Switch Box Outdoor, Battery Cutoff Isolator, PV Array MCB: Amazon.com: Tools & Home Improvement](https://www.amazon.com/dp/B0DJNNYG4D...ding=UTF8&th=1)
  • bcroe
    Solar Fanatic
    • Jan 2012
    • 5246

    #2
    Is that the open circuit rating at 25C? Be aware the voltage rises a lot at very low temps, and
    at open circuit vs MPPT. Make sure the circuit breaking devices are DC rated for your system,
    which is generally much lower than the AC rating. The combiner box here uses fuses instead
    of breakers for panel strings, as DC breakers over 500 VDC are quite large and expensive.
    Bruce Roe

    Comment

    • adrianfen45
      Junior Member
      • Oct 2026
      • 5

      #3
      Your current and voltage headroom both look fine. Nine of the Hid-S305 in series at 40.1 Voc is about 361 V, and even with the cold-weather Voc rise you will stay well under the 1000 V rating, so the 1000 V / 40 A pair is not being pushed by a 9.9 A string. The one thing worth double checking on that DIHOOL is the DC interrupting rating on the nameplate rather than the AC number, since a DC arc does not self-extinguish at a zero crossing and cheap swing-handle disconnects are sometimes AC only.
      If it is marked for DC, you are good. I would still keep the disconnect within sight of the inverter.

      Comment

      Working...