Conext XW6848+ - AC Overload when generator stops
  • extrafu
    • Apr 2016
    • 185
    Hi,
    The good old dark days are coming back for many weeks. Yesterday and today, I started the generator for about 1 hour. Each time it stopped (first time, max gen time reached, second time, I stopped it manually), the XW6848+ inverted threw a "AC Overload" error and turned off AC out for 2-3 seconds.
    What could cause that? I have changed absolutely nothing and at both times, AC loads were below 400W.
    Thanks,
  • extrafu
    • Apr 2016
    • 185
    I've fixed the issue. For those who even run into this, the Conext manual says:
    1. Check for loads above the inverter’s capacity. Turn off some loads if necessary.
    2. To clear the fault: Turn off the unit by holding the power button for 5 sec.
    3. Disconnect the Conext XW+ from the battery bank for 20 sec."
    While I didn't have a fault to clear and I wasn't in the 1st situation, I turned off the unit for 2 minutes and started it back up. I've done an other generator test and this time, all was fine. Looks like a software fart.
    • extrafu
      • Apr 2016
      • 185
      Looks like the problem is back today and was yesterday too. Inverter throws a F63 fault and clears it automatically right after the AGS turns off the generator.
      I'll open a ticket with Schneider and see what they say about that.