Hi All, We have an existing 15Kv grid tie with 3 - Sunny Boy 5.0 which supply our business with 3 phase 208V. I would like to convert to off grid but I do not know if the SB 5.0 will work in this application. Any suggestions?
Try our solar cost and savings calculator
Grid Tie to Off Grid Conversion
Collapse
X
-
-
The Sunny Boy inverters can be converted to off-grid operation by using a technique called AC Coupling. Go purchase three SMA Sunny Island inverters and a large 48 volt battery bank and wire it all up..
The Sunny Islands will cause your normally grid-tied Sunny Boy's to make power as if the grid was still connected. You'll need three of the Sunny Island units.
-
If you are abandoning the grid connection, you will also need a large generator that can run the business AND recharge the batteries in bad weather. And with a generator over 50hp. many locations require Air Quality permits and inspectionsPowerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
We have a 22kv generator currently backing up the system. My problem is that even though we installed a 15Kv PV grid tied system, we still pay meter charges and demand even though in 8 months we back fed 15Mw back to the grid. I spoke with my utility and they said that we never get paid for the banked MW so we will always have to pay about $200 in meter charges and demand.Comment