Hi All, We have an existing 15Kv grid tie with 3 - Sunny Boy 5.0 which supply our business with 3 phase 208V. I would like to convert to off grid but I do not know if the SB 5.0 will work in this application. Any suggestions?
Grid Tie to Off Grid Conversion
The Sunny Boy inverters can be converted to off-grid operation by using a technique called AC Coupling. Go purchase three SMA Sunny Island inverters and a large 48 volt battery bank and wire it all up..
The Sunny Islands will cause your normally grid-tied Sunny Boy's to make power as if the grid was still connected. You'll need three of the Sunny Island units.
If you are abandoning the grid connection, you will also need a large generator that can run the business AND recharge the batteries in bad weather. And with a generator over 50hp. many locations require Air Quality permits and inspectionsPowerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
We have a 22kv generator currently backing up the system. My problem is that even though we installed a 15Kv PV grid tied system, we still pay meter charges and demand even though in 8 months we back fed 15Mw back to the grid. I spoke with my utility and they said that we never get paid for the banked MW so we will always have to pay about $200 in meter charges and demand.Comment