    8 Gauge to 10 Gauge Wire Reducer?

    The wires coming from our panels to our charge controller look a lot like coax on the outside. They are .25 in. (6.6 mm) in diameter, and inside are 19 separate copper conductors, twisted together, and surrounded by a single black jacket. The internal bundle of conductors is .17 in. (4.6 mm) in diameter, which is about the same as an 8 ga. wire. The bundle is too big to fit into the openings on the charge controller. I need some kind of wire reducer/adapter, to take the 8 ga. equivalent bundle down to about 10 ga. to fit into the charge controller. Replacing the wires is not an option. Anybody know of something that would work?
  • bob-n
    Solar Fanatic
    • Aug 2019
    • 569

    #2
    That sounds like standard stranded wire.

    You can get connector blocks that accept pairs of wires and connect them together. For example, Marathon 985-GP accepts from 4 gauge to 18 gauge and comes a few different models. The smallest is for two pairs 985-GP-02. 985-GP-03 is for 3 pairs, etc. Search Amazon or Newark Electronics for Marathon 985-GP. You put the #8 wire in one end and the #10 or #12 in the other, and tighten the screws to the factory specified torque. Simple and fast. There are other Marathon products that would also work, but this is probably the simplest choice. Here's a photo of the 985-GP-03, courtesy Amazon:
    71iIyXBIopL._SL1500_.jpg

    Another choice is to get "Pin Terminals". These are crimp devices which go around the wire and have a straight pin on the end of a smaller diameter. For example Digikey, Allied, Newark and Mouser sell TE Connectivity / AMP 180599 pin terminals. The advantage of these is that they're small and cheap. Unfortunately, to use these, you either need a crimp tool or you need to be extremely good with improvising. Search for "TE AMP 180599".
    inhouse_180599_t.jpg

    With any approach, you need to make sure that the connection is both secure and safe from fingers, dropped tools, etc.
    Attached Files
    Last edited by bob-n; 05-08-2020, 09:02 PM.
    7kW Roof PV, APsystems QS1 micros, Nissan Leaf EV

    Comment

    • Mike90250
      Moderator
      • May 2009
      • 16020

      #3
      If you don't have the right factory crimper, don't improvise a way to crimp the pin terminals. you will regret it if it causes a fire. You need a 5 ton hydraulic crimper, not a $4 automotive crimper.

      Solder is a NO-NO for high current applications. It can melt away if the connection heats up, and can wick up the wire strands and cause a hidden break under the insulation with only a little wire movement.

      Or use a splice block
      Buy splicer reducer lugs. Allows 14 AWG to 350 kcmil (4/0 AWG) copper or aluminum wire, and are CSA certified and UL recognized. Aluminum with tin plating. Made in the USA from domestic and imported parts

      or a split bolt (with the proper rating)

      or
      Made for both copper and aluminum wire, these copper split bolt connectors come in a variety of types. Shop electrical connectors at ElecDirect today!


      I now use copper loaded (or silver loaded) electrical grease at all connections to prevent mishaps. And there is a skill to using barely enough to provide results, not a terrible gloppy mess.
      McMaster-Carr is the complete source for your plant with over 595,000 products. 98% of products ordered ship from stock and deliver same or next day.

      Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
      || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
      || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

      solar: http://tinyurl.com/LMR-Solar
      gen: http://tinyurl.com/LMR-Lister

      Comment

      • eric@psmnv
        Member
        • Sep 2015
        • 93

        #4
        I love this forum. Knowledgable folks are so willing to help.

        I had considered pin terminals and I like that idea best, but when you look for pin terminals on Amazon they don't show an amperage rating. so I'm not sure if they're safe. Also, my crimper is a $20 hardware store special that I got for making coax cables for a cell phone booster. Do I really need an expensive hydrolic crimper?

        Comment

        • bob-n
          Solar Fanatic
          • Aug 2019
          • 569

          #5
          Eric,

          As Mike said, the correct crimp tool is the only dependable way to go. It doesn't have to by hydraulic, but it needs the correct size and shape jaws. If your tool has the right jaws and you use it carefully, you will probably succeed. But why risk it?

          The splice blocks from Lugs Direct or Marathon are UL rated and inexpensive. They are also easy to rework. The Marathon block also has insulation. You won't regret either choice.

          Mike,

          I'd like to learn more about electrical grease. There's so much hype on grease in discussion groups but I haven't found anything authoritative on using it for terminals. Can you share your experiences and any good technical links?

          Thank you.
          7kW Roof PV, APsystems QS1 micros, Nissan Leaf EV

          Comment

          • eric@psmnv
            Member
            • Sep 2015
            • 93

            #6
            Could you link me to an appropriate crimp tool?

            Last edited by eric@psmnv; 05-09-2020, 10:41 AM.

            Comment

            • bob-n
              Solar Fanatic
              • Aug 2019
              • 569

              #7
              You can find that on the TE Connectivity / AMP website. https://www.te.com/usa-en/product-180599.html
              7kW Roof PV, APsystems QS1 micros, Nissan Leaf EV

              Comment

              • Mike90250
                Moderator
                • May 2009
                • 16020

                #8
                I use a $50, 8 ton rated tool from ebay. I also spent 35 years in aerospace using $2,000 crimpers that were calibrated every 6 months and I know what a good crimp is.
                A good crimp cold welds the wires to the shell, and leaves an uncrimped portion of the shell as a strain relief for the wire. The wire will break before it pulls out of the shell.

                There are several kinds of electrical grease, some are insulative, some are conductive. They come in silver, copper and carbon. Silver is used at power plants and substations to grease the double bolt threads and connection interfaces. The lugs are the size of your leg. Giant stuff. I used that till it ran out, I now have the copper from McMaster Carr. The Carbon I have no experience with and the numbers show it's not as conductive as silver or copper. But carbon is this years buzzword, so it must be good.
                this is hands on learning, too little and it's useless, too much and it runs out and causes a short in 2 years.
                Safest is the No-Oxid, warm the tub till it's liquid and dip the stripped wire in, then torque it down in the terminal. I've not used it for crimping, only have used the copper for crimping copper wire, you don't mix metals.

                The insulated splice blocks are the easiest way, with a dab of no-ox in the joint to protect the wires
                https://www.sanchem.com/electrical-c...lubricant.html NO-OX-ID "A-Special" is the stuff you melt and dip the wire into before torque. and you MUST use a torque tool. I use a gunsmiths tool. Too loose and the wires loosen and overheat from poor contact. Too tight, you strip threads or crush/cut strands and again, overheat.
                Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                solar: http://tinyurl.com/LMR-Solar
                gen: http://tinyurl.com/LMR-Lister

                Comment

                • eric@psmnv
                  Member
                  • Sep 2015
                  • 93

                  #9
                  Originally posted by bob-n
                  You can find that on the TE Connectivity / AMP website. https://www.te.com/usa-en/product-180599.html
                  Yikes, $1100 for a tool that squeezes a metal pin terminal onto a bundle of copper wires. That's way out of my league. If it's really that risky to use a consumer-grade crimper, then I guess the $2 splice blocks are the way to go.

                  Comment

                  • Ampster
                    Solar Fanatic
                    • Jun 2017
                    • 3649

                    #10
                    Originally posted by eric@psmnv

                    Yikes, $1100 for a tool that squeezes a metal pin terminal onto a bundle of copper wires. That's way out of my league. If it's really that risky to use a consumer-grade crimper, then I guess the $2 splice blocks are the way to go.
                    I bought a cheap Chinese hydraulic crimper that does everything from 4/0 to 12 Ga wire. Well worth the money, especially for the big Amp connections. It was less than $50.
                    9 kW solar, 42kWh LFP storage. EV owner since 2012

                    Comment

                    • eric@psmnv
                      Member
                      • Sep 2015
                      • 93

                      #11
                      Originally posted by Mike90250
                      I use a $50, 8 ton rated tool from ebay. I also spent 35 years in aerospace using $2,000 crimpers that were calibrated every 6 months and I know what a good crimp is.
                      A good crimp cold welds the wires to the shell, and leaves an uncrimped portion of the shell as a strain relief for the wire. The wire will break before it pulls out of the shell.

                      There are several kinds of electrical grease, some are insulative, some are conductive. They come in silver, copper and carbon. Silver is used at power plants and substations to grease the double bolt threads and connection interfaces. The lugs are the size of your leg. Giant stuff. I used that till it ran out, I now have the copper from McMaster Carr. The Carbon I have no experience with and the numbers show it's not as conductive as silver or copper. But carbon is this years buzzword, so it must be good.
                      this is hands on learning, too little and it's useless, too much and it runs out and causes a short in 2 years.
                      Safest is the No-Oxid, warm the tub till it's liquid and dip the stripped wire in, then torque it down in the terminal. I've not used it for crimping, only have used the copper for crimping copper wire, you don't mix metals.

                      The insulated splice blocks are the easiest way, with a dab of no-ox in the joint to protect the wires
                      https://www.sanchem.com/electrical-c...lubricant.html NO-OX-ID "A-Special" is the stuff you melt and dip the wire into before torque. and you MUST use a torque tool. I use a gunsmiths tool. Too loose and the wires loosen and overheat from poor contact. Too tight, you strip threads or crush/cut strands and again, overheat.

                      If the binding of the pin-terminal to the wire bundle is that critical, it makes me wonder about where the bundle plugs into the charge controller. The wire bundle is just jammed into a square hole, and a simple Phillips-head screw inside the controller gets turned, which narrows the metal contacts inside (flat metal surfaces) and clamps down on the bundle. If that works okay at the connection to the charge controller, I wonder why the pin terminal just an inch or so away needs an industrial-quality crimp job.

                      If you wouldn't mind linking me to a tool like yours, that would be helpful.

                      Comment

                      • eric@psmnv
                        Member
                        • Sep 2015
                        • 93

                        #12
                        Originally posted by Ampster

                        I bought a cheap Chinese hydraulic crimper that does everything from 4/0 to 12 Ga wire. Well worth the money, especially for the big Amp connections. It was less than $50.
                        Can you send me a link to one like you bought?

                        Comment

                        • Ampster
                          Solar Fanatic
                          • Jun 2017
                          • 3649

                          #13
                          Check to make sure it has the die sizes you need. I had to grind one die in order to do 4/0 cable crimps.
                          https://www.amazon.com/Hydraulic-Bat...NsaWNrPXRydWU=

                          Crimper.jpg
                          Last edited by Ampster; 05-09-2020, 01:56 PM.
                          9 kW solar, 42kWh LFP storage. EV owner since 2012

                          Comment

                          • eric@psmnv
                            Member
                            • Sep 2015
                            • 93

                            #14
                            Thanks much, Ampster!

                            Comment

                            • Mike90250
                              Moderator
                              • May 2009
                              • 16020

                              #15
                              This is really such a delicate subject, because you have to know what a proper crimp looks like
                              this article covers small multi pin connectors, not power cable lugs. https://www.molex.com/tnotes/crimp.html

                              Here's some more commercial data on crimping
                              THORNE & DERRICK are UK and international specialist distributors of LV, MV & HV Cable Installation, Jointing, Substation & Electrical Equipment – we service UK and global businesses involved in cable installations, cable jointing, substation, overhead line and electrical construction at LV, 11kV, 33kV and EHV.

                              Crimping Cables With Cembre Cable Lugs & Crimping Tools | BS7609 - REQUEST QUOTE | Thorne & Derrick UK & Exports for best prices, customer service & fast delivery worldwide. +44 191 410 4292



                              I've just not been able to find any decent sites with pics for you.
                              Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||