solar system catastrophe and rebuild

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #16
    i suspect your charge controller is not a true MPPT controller. You typed MPP, which is close enough for a sales scam/pitch, but it won't downconvert your 41V to 30V for charging. Measure your Amps in from the solar, vs the Amps out from the controller to the batteries, (without any loads on)

    > 6 flex panels, 160w each, 22.8 voc, 8.6 amps per panel.
    > Wired 3 groups of 2 in series parallel for a desired total of 41v and ~25amps.

    4 panels wires 2S2P would produce a mess. 22.8Voc is not a usable power measurement, We need the Vmp voltage, which I will guess is about 18V
    160W @ 8.6A = 18.6Vmp
    With panels , voltage is easily achieved, and as sun gets stronger, the amps increase. in real life, you can expect to harvest only about 80% of the panel nameplate rating.
    160 x 4 = 640w / 80% = 512watts @ 37.2V = 14 amps. A true MPPT controller will increase those amps a bit, as it matches the charging voltage of the batteries around 30V

    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • Jayson
      Junior Member
      • Mar 2020
      • 29

      #17
      Thanks for all of this input Bala and Mike.

      I will test individual panels for short circuit current today. I need a little more instruction on this. Initially I tested each panel in moderate sun, and I was achieving the ~80% output getting 21v and 5.6 amps (around 120w). I will post panel specs shortly <vmp, voc, imp and so on).

      As far as the controller, let's get those details clear. Yes, this is a true mppt charging system. MPP Solar is the brand.

      Attached Files

      Comment

      • Jayson
        Junior Member
        • Mar 2020
        • 29

        #18

        Specifications:
        Main Color:black
        Item Size: 118/54/0.2cm
        Package Size:120/59/3cm
        Maximum Power: 160W
        Maximum System Voltage: 600V DC (UL)
        Optimum Operating Voltage (Vmp): 18.6V
        Open-Circuit Voltage (Voc): 22.8V
        Optimum Operating Current (Imp): 8.6A
        Short-Circuit Current (Isc): 9.47A


        Comment

        • Jayson
          Junior Member
          • Mar 2020
          • 29

          #19
          You guys are helping already! Got a nice hazy sun and getting the best numbers so far, although still not ideal. Maybe a panel or 2 was damaged in the accident....

          Currently showing 150w pv input, with 33v, 5a. I suspect this is the mppt converting some of the voltage to higher amps.

          Mike, would there be a better way to wire the array e.g. one group in parallel or ?

          I think if I could get the expected 500w, it would supply my loads and keep me charged up.

          Bala, unfortunately the clamp meter I bought was ac only. Luckily I do enough residential ac so it's not a complete loss...but yes I need a DC version. Recommendation?

          Comment

          • Mike90250
            Moderator
            • May 2009
            • 16020

            #20
            You are at an awkward voltage with only 2 panels in series. That is barely enough voltage to activate a MPPT controller. But if the controller is actually working properly (which you cannot tell without a DC amp meter) it's as good as you can expect
            Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
            || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
            || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

            solar: http://tinyurl.com/LMR-Solar
            gen: http://tinyurl.com/LMR-Lister

            Comment

            • Jayson
              Junior Member
              • Mar 2020
              • 29

              #21
              Thanks Mike for trying to help. I'm a bit confused about this being an awkward voltage, as I thought my initial (6 panels, 3 groups of 2 in series) was ideal. The voltage has not changed since losing 2 panels from the array (41v) Here is exactly what I have now:

              2 groups of 2 panels wired in series, connected together in parallel. The array produces 41 volts with varying amperage. I was expecting ~ 12 amps at peak performance.

              The controller shows 30 to 41 volts with varying amperage.

              Best so far is 168w at 32v , ~6 amps.

              Also, I do have the hall effect sensor which measures DC up to 100 amps. I can relocate this to any part of the circuit I need a reading, just a pain with the closed loop sensor. It is working properly currently connected to the incoming pv +.





              Comment

              • Mike90250
                Moderator
                • May 2009
                • 16020

                #22
                (Vmp): 18.6V = nearly ideal voltage for a PWM controller to charge a 12v battery

                with a 24v battery, 37.2v is only slightly higher than the charging voltage (31V, only 6 volts to play with) When the battery is low, at 25V, then there is more spread for the MPPT function to work, but it relies on the difference from the solar PV voltage from the current battery voltage, and so it converts some of the extra volts, to amps. As that difference lessens, there is less "overhead" for the MPPT to function, and it eventually reverts to PWM charging. If it's a warm day, the panel voltage decreases from heat, so there is even less advantage to MPPT.
                Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                solar: http://tinyurl.com/LMR-Solar
                gen: http://tinyurl.com/LMR-Lister

                Comment

                • Jayson
                  Junior Member
                  • Mar 2020
                  • 29

                  #23
                  That helps so much and kind of what I figured was going on, but my knowledge of how the mppt algorithm works is very novice. Also other factors as you mentioned (heat, battery level, loads) can muddle my interpretation of the readings and what the system is doing. This is compounded by the different stages of auto charging modes...

                  I do get a steady 41 volts from the array into the controller so maybe a good 10v of play.

                  My float voltage is set at 27.1. I'm at 27.0 now and it seems to decrease charging effort as I near the float setting.

                  So what I'm wondering now as I prepare for individual panel testing is about the pv readout on the controller. Will it typically show the actual wattage being produced or some equation of what the mppt is using?
                  Also if I have the amp meter on the incoming pv +, is this the best location to meter incoming pv amps?

                  Thanks very much for your time.

                  Comment

                  • Mike90250
                    Moderator
                    • May 2009
                    • 16020

                    #24
                    Never trust the controllers, many items with built in metering, skew the data in their favor. That's why using a clamp on DC amp meter is so important
                    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                    solar: http://tinyurl.com/LMR-Solar
                    gen: http://tinyurl.com/LMR-Lister

                    Comment

                    • Bala
                      Solar Fanatic
                      • Dec 2010
                      • 734

                      #25
                      Originally posted by Jayson

                      Bala, unfortunately the clamp meter I bought was ac only. Luckily I do enough residential ac so it's not a complete loss...but yes I need a DC version. Recommendation?
                      AC/DC Clamp meters are now available from most large hardware, auto parts, or electronics shops. Mine is 40A and 400A DC and was about $100Aud 2 years ago.

                      I would say its A accuracy is + - 1A but it is fine for Stand alone solar and Auto work.

                      Just make sure it actually has DC A. Looking at ones on Walmart website many dont seem to have DC amps.

                      Comment

                      • Jayson
                        Junior Member
                        • Mar 2020
                        • 29

                        #26
                        Thanks Bala, trying to hunt one down now. This bayite ampmeter is pretty accurate and easy to use, but it's a closed loop as opposed to a clamp...so disconnecting and all that is a pain but I currently have it hooked up on the pv positive from the array, prior to the breaker and mppt. Is this the best location?

                        Comment

                        • Bala
                          Solar Fanatic
                          • Dec 2010
                          • 734

                          #27
                          Originally posted by Jayson
                          Thanks Bala, trying to hunt one down now. This bayite ampmeter is pretty accurate and easy to use, but it's a closed loop as opposed to a clamp...so disconnecting and all that is a pain but I currently have it hooked up on the pv positive from the array, prior to the breaker and mppt. Is this the best location?
                          My reasoning for testing individual panels was because you said your system has never really performed well.

                          Testing for A where you are will tell what A you are getting but I dont think it will help determine why it is low.

                          It looks like Mike is all over what is likely your problem but by testing panel short circuit current individually and in their configuration you can rule them in or out then move on in fault finding.

                          My theory of fault finding anything is to start at the start and work through.

                          If your panels do test good and all your connections are correct and good quality then you are looking at the controller for current delivery and the batteries for accepting that current.

                          Comment

                          • Jayson
                            Junior Member
                            • Mar 2020
                            • 29

                            #28
                            Pretty full charge today at 27.0. I will test each panel individually tomorrow. Do I just perform the test at best sun or how can I test the short circuit current reliably? Do I need to connect a load or something?

                            Give thanks for your time!

                            Comment

                            • Bala
                              Solar Fanatic
                              • Dec 2010
                              • 734

                              #29
                              Originally posted by Jayson
                              Pretty full charge today at 27.0. I will test each panel individually tomorrow. Do I just perform the test at best sun or how can I test the short circuit current reliably? Do I need to connect a load or something?

                              Give thanks for your time!
                              Short circuit current is as the name suggests. If you are using the multimeter with probes when set on amps + lead from panel to + lead on meter and - to -..

                              If using a clamp meter just join the panel leads together then measure, you may be able to do this with your bayite?

                              NOTE: Do not connect or disconnect the leads unless the panel is covered or arcing will occur.

                              The highest sun/ noon will give you your best reading, if practical you could take readings at 10am and 3pm so you know what to expect from them at that sun angle.

                              This is form the Battleborn site: Two BB10012 batteries mounted in series to form a nominally 24V system should be charged using a bulk and absorption voltage of 28.8V, and a float voltage of 27.2V

                              Comment

                              • Jayson
                                Junior Member
                                • Mar 2020
                                • 29

                                #30
                                Excellent. I used the same Battleborn resource to verify settings. 28.8 is my bulk/absorb setting and I went with 27.1 just to be safe as they said anything under 27.2 is good and the "float” mode is kinda arbitrary for lifepo4.

                                I will cover the panels with a moving blanket, disconnect and test all panels. If I'm getting this, all panels should test the same, not necessarily at the short circuit current.
                                I will use the multimeter just as I did upon receiving and testing the panels.

                                What happens if the panels are disconnected "under load" and arcing occurs? Will the panels become damaged or suffer permanently in some way?

                                Very much appreciate your direct and thorough help. Knowledge breeds confidence