Ok so I plan to submit a claim to Schneider in the morning, But wanted to know before I do if this is typical of a 3400 watt split 240v Inverter.
The Schneider Conext SW 4024 Inverter should be enough to handle what i am doing.
This is a 240 split 3400 watt inverter capable of 41 amps AC peak current split over 2 legs - L1 and L2.
My 1/2 HP well pump runs on 240 split with 4 amps or less on each leg. Start up surge measures with a Clamp on Max Hold Amp meter is 14.7 amps total (about 7.3 amps per leg).
A resistive load from a 1150 watt 120v water heater element at 9.5 amps also flashes the lights.
So Why are my lights flashing (in some cases going completely off) with this inverter? These loads are well within the specs of the Inverter that should handle a 41 amp surge and 29 amps continuous over both legs. I could possibly see this with the Inductive startup load of the Well pump as my Clamp Max Hold meter may not be showing me the true surge amps. But this should not be happening with the resistive 9.5 amp water heater element as 9.5 amps is well below the 14.1 continuous amps per leg.
The system, inverter, and battery bank is no more than 4 months old ... all new.
The battery bank consists of 4 Trojan L16H AC 435ah 6v batteries in series for a 24v battery bank. The test in the video was with the batteries fully charged and tested for 100% Specific Gravity. So this is very frustrating. I have rewired everything. Tested and checked all wire connections. I have confirmed that when the inverter is in by pass mode and getting power from the gird (thus the pump and water heater element are using all the same wiring but using grid power passed thru the SW) that there is NO flashing of lights. So this is definitely only occurring on the 24v battery bank, when the SW 4024 is in Inverter mode.
Watch the Video Here
I also have created a Spread Sheet Log File done in 5 second internals from the SW during the tests that where done during the video.
Before I send this to Schneider ... Any ideas? Maybe this is just typical?
The Schneider Conext SW 4024 Inverter should be enough to handle what i am doing.
This is a 240 split 3400 watt inverter capable of 41 amps AC peak current split over 2 legs - L1 and L2.
My 1/2 HP well pump runs on 240 split with 4 amps or less on each leg. Start up surge measures with a Clamp on Max Hold Amp meter is 14.7 amps total (about 7.3 amps per leg).
A resistive load from a 1150 watt 120v water heater element at 9.5 amps also flashes the lights.
So Why are my lights flashing (in some cases going completely off) with this inverter? These loads are well within the specs of the Inverter that should handle a 41 amp surge and 29 amps continuous over both legs. I could possibly see this with the Inductive startup load of the Well pump as my Clamp Max Hold meter may not be showing me the true surge amps. But this should not be happening with the resistive 9.5 amp water heater element as 9.5 amps is well below the 14.1 continuous amps per leg.
The system, inverter, and battery bank is no more than 4 months old ... all new.
The battery bank consists of 4 Trojan L16H AC 435ah 6v batteries in series for a 24v battery bank. The test in the video was with the batteries fully charged and tested for 100% Specific Gravity. So this is very frustrating. I have rewired everything. Tested and checked all wire connections. I have confirmed that when the inverter is in by pass mode and getting power from the gird (thus the pump and water heater element are using all the same wiring but using grid power passed thru the SW) that there is NO flashing of lights. So this is definitely only occurring on the 24v battery bank, when the SW 4024 is in Inverter mode.
Watch the Video Here
I also have created a Spread Sheet Log File done in 5 second internals from the SW during the tests that where done during the video.
Before I send this to Schneider ... Any ideas? Maybe this is just typical?