Just completing my powerwall 2 install along with my 7.4kw PC system. Here are some.pictures of the powerwall install. No data yet as it will be a few weeks before the inspections are completed and the system becomes functional and I can keep you all posted
Powerwall 2 install.
Would you share costs/performance numbers? What are those batteries part #, capacity, voltage, charge controller, dimensions? It's hard to make anything from the pic itself. The wires look like they belong to some comm equipment instead of 7.4 kW power plant.Comment
Could you also share the goal of your energy storage solution? Is it primarily time shifting your consumption to work around your PoCo's TOU plans? What's net metering like in your area? Does the system provide backup power in the event of a PoCo outage? If so, how do you manage load shedding? Did you have to install a second panel board and move circuits into / out of the battery protected load center?
It appears you have two Powerwall batteries. What size is the battery's DC to AC inverter? How many continuous amps can it supply at 240 VAC? for how long?
Thank you! Just curious. I have a lot of experience with large commercial UPS systems (208V & 480V 3-phase, 20kW-250kW) . The UPS systems themselves are generally not too expensive ($20K-$200K) but properly wiring the feeders and loads can be very expensive.
In a residential setting, you'd want to minimize the wiring cost (and the space it takes up) as much as possible. But unlike whole house natural gas generators which are cost effective and large enough (usu 10kW-22kW) to pickup the entire panel board using a simple manual or automatic transfer switch
For example this 22kW 1800-rpm natural gas unit from Generac -- $8800 -- will put out 92 amps @ 240VAC continuously
https://www.electricgeneratorsdirect.com/Generac-Protector-RG02224ANAX-Standby-Generator/p15945.htmlThe Generac Protector® QS Series 22kW Automatic Standby Generator (Premium-Grade) w/ Mobile Link™ (120/240V Single-Phase) RG02224ANAX has been discontinued. Check out Expert's recommended alternatives for another top standby generators liquid-cooled generator.
None of the Solar PV / Storage solutions I've seen have been very large. Meaning that a lot of additional wiring would be necessary to separate out the protected vs non-protected circuits. And run times would be only a few hours -- aka good for a blip and maybe a downed pole. But not for a hurricane, ice storm, etc.
But, if all you want to do is shift your usage later in the evening to work around a TOU plan, then this wouldn't be necessary. Though, at least in the US, I haven't yet seen evidence that using storage for time shifting was cost effective, yet.Comment
Sounds like you have a plan. Please let us know roughly where you live and about what the cost was to install that system. I appreciate you sharing your information.Comment
The cost of the install was 17k just for the 2 powerwall installs. State of California sgip rebate was 9400 and with the federal credit of 30% the total out of.pocket is 17k - 5.1k - 9.4k = 2.5k.Comment
Here's another picture with the wiring diagram. I'll get the additional detail and post. This is the AC powerwall with the built in inverter. One of the first units shipped from the gigafactory in sparks NV.
Attached FilesComment
I dont have any actual numbers but from the calculations and assumptions we made, These 2 units put out enough to power my whole home for 15 hours. As such There's no separate subset of appliances and lights that are powered by these units. And assuming that the sun comes back in 15 hours which is a good bet ? here in norcal my PV system should kick back in power these units and my home. And if I cut my consumption in this scenario, which I don't but I can if needed, I can be off grid indefinitely if needed is the plan.Comment
Do you have any clouds in San Ramon? Those can easily stretch longer than 15 hrs so I think fully off the grid is still not realistic here but these should help to mitigate TOU rates differences. I'm not sure though if that will worth $2.5k spent on the system which would supposedly need replacement in 5(?) years.
( 17k - 9,400 ) x 0.7 = $5,320OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNHComment
Yes assumption is that the AC unit is not on. Which works for most of the year here. Mostly cloudless days and sunshine year around.
Bottom line there is no realworld data as these units are brand new. I'll get actuals in the next few months. Everything else is speculation.Comment
Fwiw Tesla has a 10 year warranty. But the warranty is vague in that it does not guarantee output rate.Comment