    hello, i trying to design an off grid pv system for a telecoms off grid bts with battery back up.I would like to know if my calculations are in order

    My system voltage will be 48v and my total electrical load is 2.7kw, assuming the pv will supply for 10 hrs, it will mean a load of 27kwh.

    battery capacity for a 24 hours backup
    2.7kw x 24hrs =64.8kwh. PSH=5, Batt efficiency=0.85, and cycle discharge =0.5. therefore Ah rating =64.8k/(48x0.5x0.85)= 3,200Ah

    solar panel data
    250Wp, Vmp=31,Voc=37.9 Isc=8.76, Imp=8.07,

    Therefore number of panels in series= 48/31= 2 approx
    load current= 64.8Kwh/(48x0.8x5) =338A
    Therefore number of pv panels in parallel = 338/8.76=39 panels
    total panels = 39x2 =78
    array size = 250x78=19.5Kwp

  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    Whoa.
    Ain't going to happen with existing tech, in any affordable manner. You gots to learn the maths first
    > load current= 64.8Kwh/(48x0.8x5) =338A
    or is it :
    > for 10 hrs, it will mean a load of 27kwh.

    and what is "array size = 250x78=19.5Kwp"

    If you want us to do your homework, you have to use conventional terms.
    You have left out the many solar charge controllers needed to convert the PV voltage to battery charging voltage.

    > assuming the pv will supply for 10 hrs
    Not on planet earth, won't happen. You might get 5 or 6 hours of production at the equator. Morning sun and evening sun go through too much atmospheric soup to be useful. Your prime solar hours are 9am - 3pm
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • Geopart
      Junior Member
      • Apr 2016
      • 2

      #3
      The total load to be supplied is 2.7Kw and the location is close to the equator with minimum peak solar hour of about 5.
      I want to design a solar system with 48V dc system voltage and a battery backup for 24 hours, so my battery will supply 2.7kw x 24 hours =64.8kwh.

      with a 50% depth of discharge and 85% efficiency, my battery amp hour rating will be 64.8Kwh/(48x0.85X0.5)= 3200Ah

      solar panel data
      250Wp, Vmp=31,Voc=37.9 Isc=8.76, Imp=8.07

      number of panels in series= 48 v/ 37.9 = 2
      current supplied by the battery banks = 64.8Kwh/(48x0.8x5) = 337.5A
      current in one panel = 338/8.76= 39A,
      Does this mean i would require 39 panels in parallel??
      making a total of 2x39=78 panels

      for the charge controller, considering a 25% safety factor, current rating will be 1.25x8.76x39= 427.05A

      Thanks


      Comment

      • SunEagle
        Super Moderator
        • Oct 2012
        • 15124

        #4
        Originally posted by Geopart
        The total load to be supplied is 2.7Kw and the location is close to the equator with minimum peak solar hour of about 5.
        I want to design a solar system with 48V dc system voltage and a battery backup for 24 hours, so my battery will supply 2.7kw x 24 hours =64.8kwh.

        with a 50% depth of discharge and 85% efficiency, my battery amp hour rating will be 64.8Kwh/(48x0.85X0.5)= 3200Ah

        solar panel data
        250Wp, Vmp=31,Voc=37.9 Isc=8.76, Imp=8.07

        number of panels in series= 48 v/ 37.9 = 2
        current supplied by the battery banks = 64.8Kwh/(48x0.8x5) = 337.5A
        current in one panel = 338/8.76= 39A,
        Does this mean i would require 39 panels in parallel??
        making a total of 2x39=78 panels

        for the charge controller, considering a 25% safety factor, current rating will be 1.25x8.76x39= 427.05A

        Thanks

        With a system that large you would be using MPPT Type charge controllers. A simple way to size that CC is to divide the total panel wattage by the battery system voltage.

        So for a 3200Ah 48v battery system you will need around 320 amp of charging power or 320a x 48v = 15.4kw of panels.With 62 of those 250 watt panels you get 15.5kw total.

        Working backward that 15.5kw system will yield ~ 323 amps (15.5kw / 48v = 323amps). That would require 4 x 80amp CC's. Which would require each to have 15 to 16 of those 250 watt panels wired to it. Depending on the max DC voltage input they would probably be set up as 4 sets of 4 wired in series / parallel.

        All that can be done but I am worried about how you plan on creating that 3200Ah 48volt battery system. That is huge and would require both environmental permits and toxic waste approvals.