hello, i trying to design an off grid pv system for a telecoms off grid bts with battery back up.I would like to know if my calculations are in order
My system voltage will be 48v and my total electrical load is 2.7kw, assuming the pv will supply for 10 hrs, it will mean a load of 27kwh.
battery capacity for a 24 hours backup
2.7kw x 24hrs =64.8kwh. PSH=5, Batt efficiency=0.85, and cycle discharge =0.5. therefore Ah rating =64.8k/(48x0.5x0.85)= 3,200Ah
solar panel data
250Wp, Vmp=31,Voc=37.9 Isc=8.76, Imp=8.07,
Therefore number of panels in series= 48/31= 2 approx
load current= 64.8Kwh/(48x0.8x5) =338A
Therefore number of pv panels in parallel = 338/8.76=39 panels
total panels = 39x2 =78
array size = 250x78=19.5Kwp
My system voltage will be 48v and my total electrical load is 2.7kw, assuming the pv will supply for 10 hrs, it will mean a load of 27kwh.
battery capacity for a 24 hours backup
2.7kw x 24hrs =64.8kwh. PSH=5, Batt efficiency=0.85, and cycle discharge =0.5. therefore Ah rating =64.8k/(48x0.5x0.85)= 3,200Ah
solar panel data
250Wp, Vmp=31,Voc=37.9 Isc=8.76, Imp=8.07,
Therefore number of panels in series= 48/31= 2 approx
load current= 64.8Kwh/(48x0.8x5) =338A
Therefore number of pv panels in parallel = 338/8.76=39 panels
total panels = 39x2 =78
array size = 250x78=19.5Kwp