low output from charge controller

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • SunEagle
    Super Moderator
    • Oct 2012
    • 15163

    #31
    Originally posted by Sunking
    I do not know of any multi-meters that can read 15 amps with an inline shunt, not even $400 units. They go up to 10 amps max. We have operator error Houston.

    You have to use either a Shunt or a Clamp-On Hall-Effect meter to read current with any accuracy. In other words all your test are invalid. If I had to bet your controller is PWM which means Input Current = Output Current. Makes not real difference with all your panels in parallel means you are going to be fighting undercharged batteries until they fail prematurely.
    What about using a DC clamp on meter. While not the most accurate device it is pretty good telling me the amount of amps being sent down a wire.

    DC Clamp on

    Comment

    • almac
      Solar Fanatic
      • May 2015
      • 314

      #32
      Originally posted by SunEagle
      What about using a DC clamp on meter. While not the most accurate device it is pretty good telling me the amount of amps being sent down a wire.

      DC Clamp on
      that what need, place that inline so i know what is going through the CC

      Comment

      • SunEagle
        Super Moderator
        • Oct 2012
        • 15163

        #33
        Originally posted by almac
        that what need, place that inline so i know what is going through the CC
        The jaws on that clamp on opens up so you can enclose any wire to measure DC amps.

        The inline amp meter I use in my RC systems is something like this.

        Comment

        • Sunking
          Solar Fanatic
          • Feb 2010
          • 23301

          #34
          Originally posted by almac
          that what need, place that inline so i know what is going through the CC
          They are not in-line, they are clamp-on.

          There are two types.

          1. That come as either an add-on to a multimeter.

          2. Permanent installation with a Hall Effect Transducer.



          However at the current ranges of solar they are not real accurate except for industrial models. The most accurate are shunts which are just precision power resistors.



          However all of them are pretty much toys and not of much use. For you save your coins and buy a good 150 Voc MPPT controller because what you have now is not going to work. With 3 panels you only have two options:

          1. Buy another 4th panel configure panels 2 x 2, and buy a real MPPT controller with a minimum 100 Voc input.

          2. The other option is to buy a MPPT controller with a 150 Voc input like a Midnite Solar Kid 30 amp controller, and wire your 3 panels in series.



          Take your pick.
          Attached Files
          MSEE, PE

          Comment

          • almac
            Solar Fanatic
            • May 2015
            • 314

            #35
            Originally posted by Sunking
            They are not in-line, they are clamp-on.

            There are two types.

            1. That come as either an add-on to a multimeter.

            2. Permanent installation with a Hall Effect Transducer.



            However at the current ranges of solar they are not real accurate except for industrial models. The most accurate are shunts which are just precision power resistors.



            However all of them are pretty much toys and not of much use. For you save your coins and buy a good 150 Voc MPPT controller because what you have now is not going to work. With 3 panels you only have two options:

            1. Buy another 4th panel configure panels 2 x 2, and buy a real MPPT controller with a minimum 100 Voc input.

            2. The other option is to buy a MPPT controller with a 150 Voc input like a Midnite Solar Kid 30 amp controller, and wire your 3 panels in series.



            Take your pick.
            thanks, i already have 7 x of these panels. so only need another CC

            Comment

            • almac
              Solar Fanatic
              • May 2015
              • 314

              #36
              thanks for all your replies and help with this, it seems i have corrected this problem, it was a loose connection on the gator clip on the end of the cable from the CC, i didnt solder the cable to the gator clip , instead had only crimped them on. i have soldered these and now i get full current. 15amps+

              Comment

              • inetdog
                Super Moderator
                • May 2012
                • 9909

                #37
                Originally posted by almac
                thanks for all your replies and help with this, it seems i have corrected this problem, it was a loose connection on the gator clip on the end of the cable from the CC, i didnt solder the cable to the gator clip , instead had only crimped them on. i have soldered these and now i get full current. 15amps+
                Glad to hear that you found it.
                If you used the proper connector and proper crimp tools (not just mashing with pliers) the connection should have been as good in terms of resistance as a soldered connection and would have better mechanical properties.
                One problem with soldering, especially with stranded wire, is that you get a stress concentration that will eventually break the wire unless you have strain relief beyond the point where the wire is coated with solder.
                SunnyBoy 3000 US, 18 BP Solar 175B panels.

                Comment

                • almac
                  Solar Fanatic
                  • May 2015
                  • 314

                  #38
                  Originally posted by inetdog
                  Glad to hear that you found it.
                  If you used the proper connector and proper crimp tools (not just mashing with pliers) the connection should have been as good in terms of resistance as a soldered connection and would have better mechanical properties.
                  One problem with soldering, especially with stranded wire, is that you get a stress concentration that will eventually break the wire unless you have strain relief beyond the point where the wire is coated with solder.
                  yes these gator clamps have an extended bracket for anchoring the cable over the insulated part of the wire

                  Comment

                  • inetdog
                    Super Moderator
                    • May 2012
                    • 9909

                    #39
                    Originally posted by almac
                    yes these gator clamps have an extended bracket for anchoring the cable over the insulated part of the wire
                    Which brings up another important point:
                    At the current values common with CCs and especially with inverters, any kind of spring loaded clamp (at either the battery or the CC end) should NOT be used.
                    Spade or ring lug terminals and bolts or binding posts are the way to go.
                    Any spring clamp will not provide a consistent low resistance in the face of time and vibration. And when it starts to heat up you will have real problems, not just poor battery charging.
                    SunnyBoy 3000 US, 18 BP Solar 175B panels.

                    Comment

                    • Sunking
                      Solar Fanatic
                      • Feb 2010
                      • 23301

                      #40
                      Reminds me of a 60/70's band.

                      Earth Wind and Fire
                      MSEE, PE

                      Comment

                      • almac
                        Solar Fanatic
                        • May 2015
                        • 314

                        #41
                        Originally posted by inetdog
                        Which brings up another important point:
                        At the current values common with CCs and especially with inverters, any kind of spring loaded clamp (at either the battery or the CC end) should NOT be used.
                        Spade or ring lug terminals and bolts or binding posts are the way to go.
                        Any spring clamp will not provide a consistent low resistance in the face of time and vibration. And when it starts to heat up you will have real problems, not just poor battery charging.
                        thanks, iv used ring lug terminals with bolts where i can. the gator clips are on the CC cables and .. yes .. a 2000w inverter. they are 200amp gator clips on the inverter and the reason i use gator clips is because of frequent reconfiguration, so they dont get left for long enough to suffer the effects of time and vibration. i always check these connections. already had some melted copper strands that came into contact with the battery post on the inside of a gator clip

                        Comment

                        • inetdog
                          Super Moderator
                          • May 2012
                          • 9909

                          #42
                          Originally posted by almac
                          thanks, iv used ring lug terminals with bolts where i can. the gator clips are on the CC cables and .. yes .. a 2000w inverter. they are 200amp gator clips on the inverter and the reason i use gator clips is because of frequent reconfiguration, so they dont get left for long enough to suffer the effects of time and vibration. i always check these connections. already had some melted copper strands that came into contact with the battery post on the inside of a gator clip
                          200 amp gator clips are a marketing fiction. Except for one time short usage like jump starting.

                          Even if the clamps can handle the current, the interface to the battery posts cannot.
                          SunnyBoy 3000 US, 18 BP Solar 175B panels.

                          Comment

                          • almac
                            Solar Fanatic
                            • May 2015
                            • 314

                            #43
                            Originally posted by inetdog
                            200 amp gator clips are a marketing fiction. Except for one time short usage like jump starting.

                            Even if the clamps can handle the current, the interface to the battery posts cannot.
                            maximum i load on these is 75amps when using an 1800w chainsaw

                            Comment

                            • inetdog
                              Super Moderator
                              • May 2012
                              • 9909

                              #44
                              Originally posted by almac
                              maximum i load on these is 75amps when using an 1800w chainsaw
                              Do you have the DC wiring from battery to inverter fused accordingly?
                              SunnyBoy 3000 US, 18 BP Solar 175B panels.

                              Comment

                              • almac
                                Solar Fanatic
                                • May 2015
                                • 314

                                #45
                                Originally posted by inetdog
                                Do you have the DC wiring from battery to inverter fused accordingly?
                                no, but fire has been on my mind, shall ask at the local store for appropriate fuse

                                Comment

                                Working...