Why is this happening?

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • miahallen
    Solar Fanatic
    • Apr 2014
    • 108

    #1

    Why is this happening?

    Brand new system installed last month.
    FlexMax80 CC, Tripp Lite APS2448UL Inverter.
    This is the last battery in the string of 8 (48V system).
    Eight 280W solar panels getting great solar exposure.
    Home is not yet being lived in, and the system has been floating for 85% of the day most days.

    The string is connected to a positive & negative shunt, to which the CC & inverter are both connected. But I do not know why the battery terminal is melting, the battery is getting ruined, but I don't know why or how to fix the problem, any help is appreciated.

    burnt (1).jpg burnt (2).jpg
    3680W - FLEXmax 80 - FX3048T - 8x L16P-AC 435Ah
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    Well, the battery IS ruined.

    Heat from a bad connection is the cause. Either the bolt to the terminal was bad, or the crimp of the lug to the wire was bad. My $ says the Lug Crimp to Wire was bad. Wire is not scorched, but most folks would notice a loose terminal bolt, but not a bad crimp hidden under heat shrink.

    Distant 3rd possibility is that there is an internal flaw in the battery causing heat, and it melted.


    Now to get that heat, would require lots of amps. Get yourself a thermal IR thermometer, run some amps (charge or discharge, doesn't matter) and start measuring. And save up for a new battery. Damage is the one reason to add a new battery to an existing bank of old ones.

    real bummer.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • Mike90250
      Moderator
      • May 2009
      • 16020

      #3
      re: shunts. you only need one shunt, unless your sister-in-law is a good looking shunt salesperson
      Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
      || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
      || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

      solar: http://tinyurl.com/LMR-Solar
      gen: http://tinyurl.com/LMR-Lister

      Comment

      • miahallen
        Solar Fanatic
        • Apr 2014
        • 108

        #4
        Thanks Mike...luckily, I have a spare....is there no way to revive the battery...it's just toast?
        3680W - FLEXmax 80 - FX3048T - 8x L16P-AC 435Ah

        Comment

        • Willy T
          Solar Fanatic
          • Jun 2014
          • 405

          #5
          That is obviously not the terminal that came on the battery, correct ? Did the original terminal get twisted off ? They are hard to make repairs on with any degree of success. Getting the bolt deep enough into the lead without it pulling out is tough to do. You have to flatten the lead mating surfaces with a counter bore and add a copper spacer to get the terminal up off the battery top.

          Comment

          • Sunking
            Solar Fanatic
            • Feb 2010
            • 23301

            #6
            The battery is done. It was destroyed from improper installation. Poor connections create a lot of heat. Enough to melt lead and and boil thermoplastic.
            MSEE, PE

            Comment

            • Sunking
              Solar Fanatic
              • Feb 2010
              • 23301

              #7
              Originally posted by miahallen
              Eight 280V solar panels getting great solar exposure.
              I sure hope this is a typo error because there is no way to operate at 280 volts on your controller.
              MSEE, PE

              Comment

              • thastinger
                Solar Fanatic
                • Oct 2012
                • 804

                #8
                You need to unhook that before you burn the place down, then buy a new battery, then buy the proper wire (that is auto speaker wire you have there), then buy the proper wire lugs and have them done properly in a hydraulic press, then look up the torque spec for the terminals and use a tq wrench when you install the new connections with some no-ox id to prevent corrosion.

                Finial thing to do is kick the installer in the nuts.
                1150W, Midnite Classic 200, Cotek PSW, 8 T-605s

                Comment

                • miahallen
                  Solar Fanatic
                  • Apr 2014
                  • 108

                  #9
                  Originally posted by Sunking
                  I sure hope this is a typo error because there is no way to operate at 280 volts on your controller.
                  Yes, thanks...280W

                  Originally posted by thastinger
                  You need to unhook that before you burn the place down, then buy a new battery, then buy the proper wire (that is auto speaker wire you have there), then buy the proper wire lugs and have them done properly in a hydraulic press, then look up the torque spec for the terminals and use a tq wrench when you install the new connections with some no-ox id to prevent corrosion.

                  Finial thing to do is kick the installer in the nuts.
                  Noted...thanks

                  BTW, it is 4ga 12V power wire...not speaker wire.
                  3680W - FLEXmax 80 - FX3048T - 8x L16P-AC 435Ah

                  Comment

                  • miahallen
                    Solar Fanatic
                    • Apr 2014
                    • 108

                    #10
                    Originally posted by Willy T
                    That is obviously not the terminal that came on the battery, correct ? Did the original terminal get twisted off ? They are hard to make repairs on with any degree of success. Getting the bolt deep enough into the lead without it pulling out is tough to do. You have to flatten the lead mating surfaces with a counter bore and add a copper spacer to get the terminal up off the battery top.
                    Yes, that is the terminal that came on the battery.
                    3680W - FLEXmax 80 - FX3048T - 8x L16P-AC 435Ah

                    Comment

                    • Willy T
                      Solar Fanatic
                      • Jun 2014
                      • 405

                      #11
                      Originally posted by miahallen
                      Yes, that is the terminal that came on the battery.
                      It's sure not the terminal on the Trojan L16-P's I am familiar with. Do all the rest of them look like the same terminal ?? I guess they could always change. Post a picture of the other terminals, always willing to learn.

                      I did see that the AGM version can be ordered with different terminals, but that is not what your's show to be.

                      ScreenHunter_989.jpg

                      ScreenHunter_990.jpg


                      AGM Battery

                      ScreenHunter_987.jpg

                      Comment

                      • miahallen
                        Solar Fanatic
                        • Apr 2014
                        • 108

                        #12
                        These are the L16P-AC batteries.
                        500x500.jpg

                        This is the wire I used:
                        3680W - FLEXmax 80 - FX3048T - 8x L16P-AC 435Ah

                        Comment

                        • Willy T
                          Solar Fanatic
                          • Jun 2014
                          • 405

                          #13
                          Originally posted by miahallen
                          These are the L16H-AC batteries.
                          [ATTACH=CONFIG]5959[/ATTACH]

                          This is the wire I used:
                          http://www.amazon.com/gp/product/B00...?ie=UTF8&psc=1
                          I stand corrected. Heat is caused by a loose connection usually. The lug could be loose and without a lock washer the heat will thermal cycle and loosen it. The wire may need to be recrimped. If the other post is good then use it with a tapered battery terminal.

                          The Battery you showed in your picture is a L 16 P, the ones you have here are L16H-AC, confusing at best.

                          ScreenHunter_991.jpg

                          Comment

                          • Sunking
                            Solar Fanatic
                            • Feb 2010
                            • 23301

                            #14
                            Originally posted by miahallen
                            Home is not yet being lived in, and the system has been floating for 85% of the day most days.

                            The string is connected to a positive & negative shunt, to which the CC & inverter are both connected.
                            I am having a little trouble with these two statements as they conflict with the pictures.

                            To have this kind of damage takes a lot of current flowing. So here is where I am puzzled:

                            How does a system rarely being used ever have much current flowing?

                            Once batteries are charged up, they are not going to take much in the way of current from the controller other than just a couple of amps in the morning after sun rise.

                            Second thing that bothers me is you state you have shunts and an Inverter in the system. I think you stated the melted battery post is at the end of the string that is connected to the Charge Controller and Inverter.

                            So why is there only 1 Cable terminated to the battery Post?

                            Are you using a Distribution Buss Bar to Home Run the Inverter and battery to?
                            MSEE, PE

                            Comment

                            • miahallen
                              Solar Fanatic
                              • Apr 2014
                              • 108

                              #15
                              Originally posted by Willy T
                              I stand corrected. Heat is caused by a loose connection usually. The lug could be loose and without a lock washer the heat will thermal cycle and loosen it. The wire may need to be recrimped. If the other post is good then use it with a tapered battery terminal.

                              The Battery you showed in your picture is a L 16 P, the ones you have here are L16H-AC, confusing at best.

                              [ATTACH=CONFIG]5962[/ATTACH]
                              Sorry, they are L16P-AC

                              Originally posted by Sunking
                              I am having a little trouble with these two statements as they conflict with the pictures.

                              To have this kind of damage takes a lot of current flowing. So here is where I am puzzled:

                              How does a system rarely being used ever have much current flowing?

                              Once batteries are charged up, they are not going to take much in the way of current from the controller other than just a couple of amps in the morning after sun rise.

                              Second thing that bothers me is you state you have shunts and an Inverter in the system. I think you stated the melted battery post is at the end of the string that is connected to the Charge Controller and Inverter.

                              So why is there only 1 Cable terminated to the battery Post?

                              Are you using a Distribution Buss Bar to Home Run the Inverter and battery to?
                              I'm sorry, I stated "shunt", but I think what I should have said is a distribution block (just a steel lug where the inverter & CC are both combined with the battery cable).
                              3680W - FLEXmax 80 - FX3048T - 8x L16P-AC 435Ah

                              Comment

                              Working...