what happens between OVD and CLV values of a controller?

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Sunking
    Solar Fanatic
    • Feb 2010
    • 23301

    #31
    Originally posted by racmaster
    1st step - connect cells in parallel over night, the lower the soc currently is, less time it takes, over night it should be much more time than realy needed. however, this will only balance them on unknown level of soc, right? the usefull point of this step is that at least we will be sure there is not a big diffference in soc of cells and it will be much more safe to hold them in planned 30-80soc. right? and also it will be much more safe to proceed to botom balance, next step...
    No you are not quite understanding what is happening. You are correct when finished you will not know the exact SOC, but there is no need to know exactly what the SOC is as that is not why you are doing it. The point is to get every battery at the same voltage or SOC if you want to call it that. They will not have the exact same capacity. I assume you have 4 cells maybe 8, does not matter. Your low cell maybe 3.2 volt, and high cell might be be 3.3 volts. When you connect them all in parallel the voltage will meet in the middle like 3.25 volts. Low cells will be charged by the high cells, and high cells will be discharged into the low cells. When done will be MIDDLE BALANCED. Sensij gave you the link to David's site how to BULK BALANCE the cells. Make sure you understand what David is telling you. Very first step is connect all the cells in parallel. You walk away to allow them to equalize to the same VOLTAGE. You could careless what voltage that is. You have Winston Cells aka Thundersky batteries and it will take them a few hours to EQ because of the high resistance time constant.

    Originally posted by racmaster
    2nd step - discharge them to the point, where NOW balanced cells (as described in 1st step) will become slightly different voltage. of course, with low discharge power and attended mode, as no balancer/bms/alarm are available. in fact, lover voltage will be shown, the lover should be discharging power to catch the moment some cell will fall from the hockey stick curve and start getting under lets say 3 volts. then disconnect it from the battery and similary discharge the remaining cells to the similar voltage. then, as soon as all fall out of the hocky curve on same voltage - very slowly discharge every(or maybe all together in serie if same voltage lets say 3vpc???) to the final 2.5vpc, where is the treshold 0%soc considered... then, connecting them again together in paralel, letting them auto-balanceat to absolute soc 0.01%... then start to charge them slowly and measure the ah, or kwh real capacity until we will get to the wanted 80%soc top disconnect value. then measured the resulting voltage of the serie and THIS will be reliable and secure value to be set as the charging limit for chargers of the particular one battery i have... the 30% value should be measured by the same way during the process... right?
    Again does not sound like you have your noodle wrapped around what is happening. You leave the cells in parallel. When in parallel every cell has the exact same VOLTAGE no Ifs ands or buts. You leave them connected in PARALLEL. At this point you either TOP or BOTTOM BALANCE with the cells in parallel. You either discharge them to 2.5 volts or charge them up to 3.65 volts. As of now I do not think you have any equipment to implement either method. I do not recall what AH rating your cells are. But for argument sake let's say they are 100 AH. Once you connect them in parallel to Equalize voltage the SOC ends up being roughly 50% so each cell is around 50 AH. ( I am just picking a number out of the sky) With them in parallel times 4 cells is 200 AH to discharge or charge. So let's say you have a 3.65 volt 20 amp power supply it will take 200 AH/ 20 Amp = 10 + hours to charge until current tapers off to 8 amps.

    To discharge is going to take a high wattage Power Resistor, For 20 amps will require 0.15 Ohm 75 watt Power Resistor. Again if the SOC is roughly 50% is going to take 10 plus hours. You want the finish rested voltage to be no greater than 2.5 volts and no lower than 2.4 volts. By rested I mean allow them to sit 1 hour.

    You can speed things up a bit with your cells connected in Series. If you decide to Bottom Balance connect them to an Inverter and put a large load on the Inverter and discharge the batteries down to 3 or so volts. Them connect them in Parallel, walk away, then come back and discharge them down to 2.5 volts. For Top Balance reverse the process. Charge them up to 3.4 volts, connect them in parallel, walk away, come back and finish charging with a 3.65 volt power supply until charge current tapers to 8 amps.


    Originally posted by racmaster
    pls note - the video link of jack rickard doesnt work, so the process above is just my guess of how that may be done, based on what i learned from this thread and the fine liionbms.com site you provided. so its a kind of test, if im getting into the picture finally at least a bit...
    My bad, try again with this link., then scroll down to close to the bottom of the ARCHIVE PAGE to November 13, 2009.

    Originally posted by racmaster
    3rd step we are there, safely cycling 30 to 80 soc, all we need to do is from time to time repeat the paralleling autobalance at lower-better soc to balancing happen in shorter time...right? anything else? is there some best practice of repeating to 0% balancing process again after some number of cycles? or anything else to do...?
    If you Bottom Balance, you take the cells apart and put in parallel again, If you TOP BALANCE the BMS will keep them Balanced if you run the voltage up to 14.4 volts

    Again you need to understand the difference between BOTTOM BALANCE and TOP BALANCE. With Top Balance the cell voltages are only equal at the TOP. All you know for sure is at the TOP is the cells are 100% SOC. You do not know what the capacity is. Capacity is dictated by the lowest capacity cell. With Chi-Com cells capacity is +/- 10%. So if you have 100 AH cells one maybe as low as 90 AH and one maybe 110 AH. The weakest cell dictates the PACK capacity and in this example would be 90 AH, not 100 AH.

    With Bottom Balance voltage of the cells is equal at the BOTTOM, not the TOP. However at 2.5 volt you know the SOC is 0% and you know the capacity is 0 AH. When the cells are wired in series, and charged you will know the Capacity, and the capacity will be whatever the lowest cell capacity is. So if the weakest is 90 AH and you charge to 90% is 81 AH for the pack. When you charge the first time you monitor each cell voltage so you can locate the weak cell. The weak cell will be the highest voltage when charged up. When you see th efirst cell reach 3.6 volts, note pack voltage and stop charging.
    Last edited by Sunking; 01-05-2018, 04:52 PM.
    MSEE, PE

    Comment

    • racmaster
      Member
      • Nov 2016
      • 67

      #32
      ok, so i went throu the site and downloading video, which will take a while as the internet is only 2g here. also, im currently midle-balancing the cells based on studied. after i disconnected them from serie, 3 of them sit at 3.27, one is 3.26 which seems not bad.

      the question im thinking about is, whether we really need to discharge it to absolute 0%SOC = 2.5vpc, if i plan to cycle the battery between 20-80 SOC. wouldnt it be enough, to consider it discharged at lets say 3.1 vpc, which we would consider to be 10%soc with another 10% reserve... in fact it doesnt matter, as we will not go in the future down to 10%soc, as we will set the charge limit on 20%soc. where exactly this 20%soc limit is? we will measure that by capacity that will be charged from this point to up to lets say 90soc, which means point, where the curve will no longer be flat and the vpc will start to increase much faster under similar charging current...

      so in fact it would mean we will not bottom balance, not even top balance, but we will instead notice when the charging curve starts to turn faster and immediately at those break-points middle balance on 10% soc +/-10%soc reserve then midle ballance it at 90%soc +/- 10%soc reserve with the same way. therefore +/-10%soc reserve, because the final cycling interval will be set to 20-80%soc... got my point? wouldnt it be usefull, if we just do not plan to use full capacity of the battery? and charging limit values will be monitored and set by measured voltages at this stages between charging process from cca 10 to 90%soc - as mentioned...

      by my understanding we will find where are the 20-80%soc limits and fullfill them in the future, we will not find the real capacity, but we will find where the safe interval is with some reserve of course, as this in not exact. doesnt matter, if that interval will mean 40ah, 50ah or 70ah of real capacity... just safe 20-80%soc of this one particullar battery...

      Comment

      • sensij
        Solar Fanatic
        • Sep 2014
        • 5074

        #33
        Guys, please keep this discussion on topic. I'm cleaning out the tangent from the past couple posts, op is not engaging in that exchange at all.

        Sunking, the NASA paper you linked is for Li-Ion, not LFP, irrelevant to the OP. Please start a new thread if you want to continue on that point.

        Lastly, if you are going to cite someone else's work, please have the courtesy to get their name correct. (Davide vs David)
        Last edited by sensij; 01-06-2018, 10:27 PM.
        CS6P-260P/SE3000 - http://tiny.cc/ed5ozx

        Comment

        • Sunking
          Solar Fanatic
          • Feb 2010
          • 23301

          #34
          Originally posted by racmaster
          the question im thinking about is, whether we really need to discharge it to absolute 0%SOC = 2.5vpc, if i plan to cycle the battery between 20-80 SOC. wouldnt it be enough, to consider it discharged at lets say 3.1 vpc, which we would consider to be 10%soc with another 10% reserve... in fact it doesnt matter, as we will not go in the future down to 10%soc, as we will set the charge limit on 20%soc. where exactly this 20%soc limit is? we will measure that by capacity that will be charged from this point to up to lets say 90soc, which means point, where the curve will no longer be flat and the vpc will start to increase much faster under similar charging current...

          so in fact it would mean we will not bottom balance, not even top balance, but we will instead notice when the charging curve starts to turn faster and immediately at those break-points middle balance on 10% soc +/-10%soc reserve then midle ballance it at 90%soc +/- 10%soc reserve with the same way. therefore +/-10%soc reserve, because the final cycling interval will be set to 20-80%soc... got my point? wouldnt it be usefull, if we just do not plan to use full capacity of the battery? and charging limit values will be monitored and set by measured voltages at this stages between charging process from cca 10 to 90%soc - as mentioned...
          You cannot do Middle Balance without unacceptable risk because the capacity tolerance of your batteries falls outside acceptable limits. You would need cells within +/- 2%. Chi-Coms are +/- 10%. You have to pick Top or Bottom. You cannot define what 3.1 volts capacity is with LFP. You have to pick a known REFERENCE POINT of either 2.5 volts or 3.65 volts.

          To be frank the real issue here is you do not have the equipment, skills, and knowledge necessary to use any lithium battery type which will most likely lead to destroying one or more cells. LFP cells are somewhat tolerant to over charging. But like all lithium batteries will not tolerate over discharge. For equipment you will need to have a means to discharge to 2.5 volts, or a DC power supply with a precision regulator to charge to 3.65 volts.

          My suggestion since you already have your cells is to buy a Revolectrix Power Lab 6 Charger and use your 12 volt battery charger to supply the PL6 with Power. It will charge any battery of today and tomorrow of 6S Lithium (any lithium), 19S Nickel, and 6,12, and 24 volt Pb from 10 ma up to 360 AH. Additionally will allow you to Bottom Balance worry free. Just wire the cells in parallel, set disconnect voltage to 2.5 volts, discharge current to 10 amps, and go to bed.
          MSEE, PE

          Comment

          • karrak
            Junior Member
            • May 2015
            • 528

            #35
            Originally posted by racmaster
            the question im thinking about is, whether we really need to discharge it to absolute 0%SOC = 2.5vpc, if i plan to cycle the battery between 20-80 SOC. wouldnt it be enough, to consider it discharged at lets say 3.1 vpc, which we would consider to be 10%soc with another 10% reserve... in fact it doesnt matter, as we will not go in the future down to 10%soc, as we will set the charge limit on 20%soc. where exactly this 20%soc limit is? we will measure that by capacity that will be charged from this point to up to lets say 90soc, which means point, where the curve will no longer be flat and the vpc will start to increase much faster under similar charging current...
            You do not need to go down to 2.5V or up to 3.6V to balance the battery but doing so will balance your battery to an accuracy better than 1%. I balance my battery at 3.45V which will balance it to within 1%, if you picked to bottom balance at 3.1V you could get accuracy to within 2%. At a voltage any higher than this the accuracy decreases very rapidly as you are getting into the flat part of the charge/discharge curves.

            The question I have for you is how do you reliably charge your battery up to 80% using solar as your charge source?


            by my understanding we will find where are the 20-80%soc limits and fullfill them in the future, we will not find the real capacity, but we will find where the safe interval is with some reserve of course, as this in not exact. doesnt matter, if that interval will mean 40ah, 50ah or 70ah of real capacity... just safe 20-80%soc of this one particullar battery...
            You are correct, as long is you make sure that the individual cell voltages don't diverge too far apart and stay within the range 3.6V to 2.8V within the SOC range that you are operating in you won't have any problems.

            From the information and graphs you supplied in an earlier post I would say you have already had your battery up to an SOC of ~95% which did not cause any problems, if you are prepared to do this again and are interested I can tell you how to balance your battery using the same or similar charge settings.

            Simon

            Off grid 24V system, 6x190W Solar Panels, 32x90ah Winston LiFeYPO4 batteries installed April 2013
            BMS - Homemade Battery logger github.com/simat/BatteryMonitor/wiki
            Latronics 4kW Inverter, homemade MPPT controller
            Off-Grid LFP(LiFePO4) system since April 2013

            Comment

            • racmaster
              Member
              • Nov 2016
              • 67

              #36
              im considering something cheaper - like this:

              Find many great new & used options and get the best deals for IMAX B6 AC Digital LCD RC Lipo NiMH NiCd Battery Balance Charger Power Adapter at the best online prices at eBay! Free shipping for many products!


              classical imax b6, 6A any battery charger/discharger/balancer dc to dc

              also one question with that - will connecting 2 chargers like this in parallel to one battery result in double charging current? or it will not work because they will be changing the measured voltage/amperes to each other and fake themselves?

              SUNKING - im not sure, if it was easy to understand, what i proposed... il try on example

              ive got your point with top/bottom balance. that means 100% accuracy and safe 90-100%soc cycling of battery, which will provide me with more usable capacity in - repeat - safe conditions. my question was, whether it is not possible to balance them by connecting to parallel somewhere NEAR to top/bottom, but not so far as 2.5/3.65vpc.?? by my understanding this could be possible - BUT with decreased accuracy of SOC determination. determination of what SOC currently measured voltage is - is it right, or absolutely not?

              EXAMPLE 100ah lifepo4 battery:
              i know that for example at 3.1vpc it still can mean, that REMAINING capacity at this voltage can be for example
              C1=20ah
              C2=30ah
              C3=10ah
              C4=22ah

              which should not be a problem at this moment, but if i will then consider this 3,1vpc to be 20%soc, then the problem will occure as soon as i will charge this 100ah battery with +80ah, as cell 2 and 3 will be overcharged then. (or even less than +80ah, as there is the problem of dividing the current between unbalanced cells on the end of the chraging curve, i know, i know. lets forget that for this example and hold this scenario values)

              my point is, that i will NOT charge it in such a manner. instead of - i will charge it slowly, attended, by small amperes until they come to 3,4vpc, which will take lets say 50AH of charging. then the same cells should be (based on previously choosed start-charging state of charge/capaciity)

              C1=20ah + 50ah=70ah
              C2=30ah + 50ah=80ah
              C3=10ah + 50ah=60ah
              C4=22ah + 50ah=72ah

              still much far enough from 100ah(100% soc in this example).

              than, the cells if being charged slowly, slowly on and on with another lets say safe +1ah will continuously start becoming more and more disballanced, as they will be moving out of the flat part of the curve. CELL2 voltage will NOW raise faster than other. THIS is the point where i could consider tha battery to be charged ENOUGH (not fully), measure the actual voltage at lets say it will be 3.50vpc and set the charging voltage limit to 4x3.5=14.00v

              so we would have - by this scenario - lov voltage disconnect at 3.1x4=12.4v and charging limit voltage 14,00v. because we will know, that here they start to become disbalanced and HERE they are getting out of the flat part of the curve. NEXT, to be even more safe and to include the inaccuracy of this process, we will change these values even more to conservative, safe area.

              lvd=12.6
              clv=13.8

              which could give us a lot of reserve to compensate the inaccuracy. ALL future cycling will be between these values. in fact cell 2 will be cycled in about 30-90%soc, while cell3 in 10-70%soc as highest and lowest cell, but it still should be safe, if really kept there.

              i hope this concept is easier to understand now.


              KARRAK - why do you mean i have reached 95%soc? based on that graph you cant see detailed voltages curve...

              and ok, if yes, then maybe we found a safe way throught the mined field by luck, as we allready went throught without knowing its mined there... if that was really 95, then it is safe to charge it until then, right?

              of course, give your idea how would you do that balancing based on existing equipment/limits of scc. i am interested, more info to consider the better...

              Comment

              • karrak
                Junior Member
                • May 2015
                • 528

                #37
                Originally posted by racmaster
                KARRAK - why do you mean i have reached 95%soc? based on that graph you cant see detailed voltages curve...

                and ok, if yes, then maybe we found a safe way throught the mined field by luck, as we allready went throught without knowing its mined there... if that was really 95, then it is safe to charge it until then, right?
                I base the 95% on the fact that from the computer screenshot the solar controller stated the maximum charge voltage was 13.95V (3.49V/cell). If the 3.49V/cell occurred with the maximum charge current of around 12A (~0.13C) using my graphs gives an SOC of ~94%-95%. If the current dropping off from 12:05 is still at 3.49V/cell the SOC will be even higher.

                If the cells are like the ones in my system and the system I set up for a friend I doubt that the difference in the capacity of the individual cells will be greater than a couple of % so charging them to 95% and even a little higher should not have caused a problem. You are lucky that you got away with it though. I think it is really important to have some sort of cell monitoring at all times to warn you if a disaster is just about to happen, that is why I suggested the cellog 8. An accurate multimeter is also important.

                of course, give your idea how would you do that balancing based on existing equipment/limits of scc. i am interested, more info to consider the better...
                Not sure what a scc is.?
                OK,
                1. Set the charge parameters back to what you have in your first post
                2. Let the battery charge, check the individual cell voltages while it is charging to make sure none go above 3.6V, this still gives you plenty of safety margin. The cell voltage has to get well above 4.0V before bad things start to happen
                3. When the controller has switched to float and the charge current has reduced below C/50 (~1.8A) measure all the individual cell voltages. Lets say the highest cell reads 3.45V and the lowest reads 3.40V.
                4. You have to remove some of the charge from the 3.45V cell to drop the voltage down to 3.40V. To do this you have to connect a resistor across the cell. A 3.3 Ohm 5W resistor works well or you could use the high beam filament of a tungsten car headlight which should be 65W @12.8V (~5A) which would be ~1.3A @3.4V.
                5. I would remove a fixed amount of charge from the cell by timing the amount of time that the bulb is connected. For each 0.01V above the lowest cell reading I would connect the bulb/resistor up for 1 minute so in the case of our 3.45V cell I would connect it up for 5 minutes. It is important to set an alarm timer when you do this as it is easy to forget and leave the resistor on for too long.
                6. After disconnecting move onto the next highest cell etc.
                7. The time I have specified will not be enough so you will have to do this several times. This can be done over several days


                This is pretty much the procedure I use to keep my battery balanced with a charging voltage of 3.45V/cell. I use the daily maximum cell voltages logged by my voltage monitor as a guide as to when to to the balancing. I had to remove about 0.4%SOC (~1.5Ah) from 2 cells in my battery last year to keep it balanced.

                Simon

                Off grid 24V system, 6x190W Solar Panels, 32x90ah Winston LiFeYPO4 batteries installed April 2013
                BMS - Homemade Battery logger github.com/simat/BatteryMonitor/wiki
                Latronics 4kW Inverter, homemade MPPT controller
                Last edited by karrak; 01-08-2018, 10:05 AM.
                Off-Grid LFP(LiFePO4) system since April 2013

                Comment

                • karrak
                  Junior Member
                  • May 2015
                  • 528

                  #38
                  Originally posted by racmaster
                  im considering something cheaper - like this:

                  https://www.ebay.com/itm/iMAX-B6-AC-...oAAOSwUchaRkTs

                  classical imax b6, 6A any battery charger/discharger/balancer dc to dc

                  also one question with that - will connecting 2 chargers like this in parallel to one battery result in double charging current? or it will not work because they will be changing the measured voltage/amperes to each other and fake themselves?
                  Yes that should work with a couple of reservations.
                  • The one being advertised is a copy of the original, what is the accuracy like and how well built is it?
                  • If you want to do discharge testing the discharge current is severely limited
                  • There is no data logging

                  I can't see any reason why you couldn't use two of these units in parallel

                  I would still recommend the 20A Reaktor 300W as it has regenerative discharge and logging. It is what I did the charge/discharge tests with.

                  Simon

                  Off grid 24V system, 6x190W Solar Panels, 32x90ah Winston LiFeYPO4 batteries installed April 2013
                  BMS - Homemade Battery logger github.com/simat/BatteryMonitor/wiki
                  Latronics 4kW Inverter, homemade MPPT controller
                  Off-Grid LFP(LiFePO4) system since April 2013

                  Comment

                  • Sunking
                    Solar Fanatic
                    • Feb 2010
                    • 23301

                    #39
                    Originally posted by racmaster
                    im considering something cheaper - like this:

                    Find many great new & used options and get the best deals for IMAX B6 AC Digital LCD RC Lipo NiMH NiCd Battery Balance Charger Power Adapter at the best online prices at eBay! Free shipping for many products!


                    classical imax b6, 6A any battery charger/discharger/balancer dc to dc

                    also one question with that - will connecting 2 chargers like this in parallel to one battery result in double charging current? or it will not work because they will be changing the measured voltage/amperes to each other and fake themselves?
                    You made a huge mistake buying two of those chargers and listening to a pretender. I know you bought them already. I am out of here. Karrak is your man. He will teach you how to destroy your batteries.

                    MSEE, PE

                    Comment

                    • racmaster
                      Member
                      • Nov 2016
                      • 67

                      #40
                      karrak, one think before i go through your answer - you may missed. the voltage shown during charging process on solar controller was 0.2v higher, than the voltage measured by hand multimeter and few other voltmeters. so in fact i believe the solar charger just measures more then real. also the charging curve of used/stored watts seems to be confirming it just wasnt so high. just the inaccuracy of solar charger controler - btw = scc

                      im just checking the reactor 300w and this alternative


                      Comment

                      • racmaster
                        Member
                        • Nov 2016
                        • 67

                        #41
                        sunking, theres no need for such a reaction. i would appreciate your answer to the presented scenario example.

                        Comment

                        • karrak
                          Junior Member
                          • May 2015
                          • 528

                          #42
                          Originally posted by racmaster
                          karrak, one think before i go through your answer - you may missed. the voltage shown during charging process on solar controller was 0.2v higher, than the voltage measured by hand multimeter and few other voltmeters. so in fact i believe the solar charger just measures more then real. also the charging curve of used/stored watts seems to be confirming it just wasnt so high. just the inaccuracy of solar charger controler - btw = scc
                          I did think about that, even if you use the lower 13.75V (~3.44V/cell) if you look at my charge/discharge curves at a current of 12A (~0.13C) you get an SOC of ~90%, if the voltage had stayed at 13.75V and the current tapered down to 0.05C (4.5A) the SOC would be up around 97%.

                          That alternative does not have regenerative discharge, discharge limited to 5A. The Reaktor is around the same price, has been around for a while, was designed by a well respected company and there is a large community of hackers that are doing some amazing things with it including working out how to calibrate it.

                          Doing the initial balance with a charger like the Reaktor will make it highly unlikely that you will have any unpleasant surprises when you first charge you battery from your solar controller but as you have already charged your battery with the solar controller without incident in makes the need for a charger like the Reaktor less important. I would still recommend you get an accurate multimeter, a cellog 8 or some other cell voltage monitor and an SOC meter that uses a current shunt to measure the current.

                          Simon

                          Off grid 24V system, 6x190W Solar Panels, 32x90ah Winston LiFeYPO4 batteries installed April 2013
                          BMS - Homemade Battery logger github.com/simat/BatteryMonitor/wiki
                          Latronics 4kW Inverter, homemade MPPT controller
                          Off-Grid LFP(LiFePO4) system since April 2013

                          Comment

                          • Sunking
                            Solar Fanatic
                            • Feb 2010
                            • 23301

                            #43
                            Originally posted by racmaster
                            SUNKING - im not sure, if it was easy to understand, what i proposed... il try on example

                            ive got your point with top/bottom balance. that means 100% accuracy and safe 90-100%soc cycling of battery, which will provide me with more usable capacity in - repeat - safe conditions. my question was, whether it is not possible to balance them by connecting to parallel somewhere NEAR to top/bottom, but not so far as 2.5/3.65vpc.?? by my understanding this could be possible - BUT with decreased accuracy of SOC determination. determination of what SOC currently measured voltage is - is it right, or absolutely not?
                            I understood the first time. Comes down to this. You are trying to cut corners, risking your batteries, and just being lazy. There is no excuse for that. If you have the time to Discharge to 3 or 3.1 volts, then you have time to go to 2.5 to do it right. Same goes for 3.65 volts. Once you are Balanced, you are done and will not have to do it again for quite some time if ever.

                            Example the Reactor is a Chi-Com knock-off of iCharger 1010B+. Take a look at both and you will see what I mean. At least the iCharger has regenerative Discharge so if you had a few days you could either Top or Bottom Balance. [moderator note - iCharger is made in China too. Reaktor and iCharger may be the same, just badged differently]

                            The 6 amp unit you are looking at I do not know if it can Discharge or not, nor do I care. I assume your cells are 100 AH and you have 4 of them? If that is a true statement with all 4 in parallel is 400 AH. If the cells were say at 50% SOC is 200 AH. Well there is some math you need to do.

                            Amp Hours = Amps x Hours
                            Amps = Amp Hours / Amps
                            Hours = Amp Hours / Amps.

                            Makes no difference if you Top or Bottom with a 6 amp Discharge/Charge you are looking at 200 AH / 6 A = 33.3 hours. Additionally if you were to Top Balance how the hell are you going to detect when they are fully charged? To initially Top Balance a Lithium battery you charge at some reasonable rate like C/10 (10 amps on a 100 AH battery) and terminate at C/20 or 5 amps on a 100 AH battery.

                            One last thing. Disconnecting at 3.1 will work, but not like you think it will. When you apply a load to a battery, you will have voltage sag on the batteries. Couple that with voltage drop on the wires, and your Inverter will prematurely trip of line from under voltage. When it happens will leave you scratching your head, because when you go look at the cell voltages, you will see they are higher than 3.1 volts. Say 3.2 volts. The mistake in your thinking, is you are using Open Circuit Voltage to determine SOC on a battery under load. It will not work espeicially on Winston cells which have a high Internal Resistance which is why battery voltage sags under load. Davide website clearly discusses the subject. Look at the drawing he uses to determine voltage per cell of 2.0 volts under load. Myself I would not go quite that low because you are not running an EV. Somewhere between 2.5 and 3 volts. Seeing how most 12 volt Inverters default LVD is 10.5 volts works. Myself I would use 11 volts or 2.75 volts per cell. 3 volts is ultra conservative.

                            I sincerely do wish you good luck, but I cannot help you do a half arse job.

                            Hint. 100 Watt .01 Ohm power resistors are cheap.

                            [moderator note - please leave comments on other forum members out of your posts, unless you are addressing something specific that was posted]
                            Last edited by sensij; 01-09-2018, 01:09 AM.
                            MSEE, PE

                            Comment

                            • racmaster
                              Member
                              • Nov 2016
                              • 67

                              #44
                              sunking, thanx for coming back. im not sure why you try to see the things in worst possible angles. reason why im thinking about presented scenario isnt lack of time as i have so much time for this as i want. also my lazyness is out of discussion. if i was lazy, i would just leave it on default lifepo4 values of the charger and not even open this thread, not writing and reading a lot of texts on different sites in foreign language, watching videos, googling... dont you think so?

                              the main reasson is the basic law ive got imprinted into my mind regarding cycling of batteries, doesnt matter if lead acid or lithium. only a final number off cycles changes, but what stays is depth of cycling. lets say lifepo4 has 1000 cycles at 90dod, 2000 at 80 and 8000 at 50%dod. smaller discharge, higher cycle life.... therefore im searching for scenario, which doesnt need to discharge the battery to zero = 2.5vpc. to get some solution, which will balance the battery and prevent future disbalance related risks, but in the same time not to push battery to zero, max discharge, max cycling depth...

                              Comment

                              • Sunking
                                Solar Fanatic
                                • Feb 2010
                                • 23301

                                #45
                                Originally posted by racmaster
                                the main reasson is the basic law ive got imprinted into my mind regarding cycling of batteries, doesnt matter if lead acid or lithium. only a final number off cycles changes, but what stays is depth of cycling. lets say lifepo4 has 1000 cycles at 90dod, 2000 at 80 and 8000 at 50%dod. smaller discharge, higher cycle life.... therefore im searching for scenario, which doesnt need to discharge the battery to zero = 2.5vpc. to get some solution, which will balance the battery and prevent future disbalance related risks, but in the same time not to push battery to zero, max discharge, max cycling depth...
                                I understand what you are trying to do. But lithium ion batteries do not work like you think.

                                Example you are stuck thinking discharging a cell to 2.5 volts will damage the cell which is a half truth. I have already proven to you that number is a manufacture CYA claim to cover their butts as the real number is 2.0 volts. Granted their is no significant energy left below 2.5 volts, but 2.5 volts is the 0% SOC value. You are not going to hurt the batteries if you Bottom Balance them occasionally. Quite the opposite, you eliminate the chance of over discharging them if Bottom Balanced as that is the whole point of Bottom Balance. Nor does it hurt them to Top Balance once in a while when needed. Either way has to be done initially. Take your pick of Bottom or Top. I really do not care what you do and I am not going to keep repeating myself.

                                As for discharging no deeper than sat 80% DOD again I understand. However there are a couple of things you do not understand, nor does the pretender. It is done by design, and selecting the right battery capacity and to a much lessor degree LVD value. A LVD is a Fail Safe only mostly for cloudy days and expected loads outside the design range. Think of it like a wing on an airplane G-Load where you design the wing for 150% G-Load. They do that to cover their arse for that unexpected turbulence or crash avoidance high G turn.

                                The first step is to determine how many days of Autonomy to size the batteries. Example say you only need 320 Watt Hours per day. You would size the battery to a minimum 4 days of capacity or 1280 kWh. That gives you roughly 3 days of run time for cloudy days without a recharge. On a 12 volt system is a 100 AH battery. Under normal operation you would never get close to 2.5 volts or even 3.1 volts. It is by design, not luck or guessing.

                                The other thing you and the pretender do not understand is you do not use an OCV (open circuit voltage) to select LVD. OCV means a rested battery disconnect from everything. When any battery is under discharge, there will be voltage sag and wire voltage loses. You can literally have a fully charged battery, apply a heavy load, the Inverter will trip off-line from under-voltage if you set LVD to high. Why because you did not allow for voltage sag and loss under load. So if you set LVD for say 12.4 volts (3.1 vpc), you are going to have LVD operation from time to time. It will have you scratching your head because when you shut down the Inverter and look at cell voltages they will be greater than 3.1 volts. The LVD is NOT there to necessarily limit discharge to some DOD percentage, it is a FAIL SAFE to prevent damaging your batteries. An occasional discharge to 2.5 volts is not going to hurt the batteries unless you do not recharge quickly.

                                To limit DOD is a design of sizing the batteries, not selecting a LVD voltage. On a 4S LFP a good number is 11 to 12 volts which is significantly greater than 8 to 9 volts of danger zone. Even the default 10.5 volts most Inverters can work with a Bottom Balanced battery, but asking for trouble on a Top Balanced battery.
                                Last edited by Sunking; 01-09-2018, 01:13 PM.
                                MSEE, PE

                                Comment