what will you suggest if i run this pump without batteries.
About inverter size and array setting
220 volts are used in Pakistan
frequency 50 hertz
Designing of off grid solar system
Collapse
X
-
I wants to run the pump from grid supply in case of emergency only. The pump will run on solar in day time it starts running from morning and keeps going till evening.
The pumps takes 35 amp at its start up and
settles at 15 amp at its running. It is a single phase and will run continuesly for 5-8 hrs every day.
Please advice accordingly.
240 @ 15A = 3600 running watts (starting is generally at least 5x this, or about 18,000watts, will need a very stout inverter, wires & batteries to supply this - 8400 w @ 48V = 175 amps starting, 75a running, from 48VDC)Leave a comment:
-
I wants to run the pump from grid supply in case of emergency only. The pump will run on solar in day time it starts running from morning and keeps going till evening. The pumps takes 35 amp at its start up and settles at 15 amp at its running. It is a single phase and will run continuesly for 5-8 hrs every day. Please advice accordingly.
Based on running 8 hour per day you are going to need
Panel wattage = 9600 watts divided into 3 systems of 3200 watts each with its own separate Charge Controller
Battery capacity configured @ 48 volts = 3000 AH, approx weight = 9000 lbs or 4100 Kg
Charge Controllers = 3 units 80 Amp MPPT
Inverter = Industrial Grade 10 KvaLeave a comment:
-
Then what you want is a Grid - Tie inverter. It feeds power into the grid, and will offset your pump's usage.
As for an inverter that can power a 5hp pump. It will be VERY expensive. It's likely a 3-phase motor, and consumes 6,000 watts, with several times that power needed to spin it up.Leave a comment:
-
Then what you want is a Grid - Tie inverter. It feeds power into the grid, and will offset your pump's usage.
As for an inverter that can power a 5hp pump. It will be VERY expensive. It's likely a 3-phase motor, and consumes 6,000 watts, with several times that power needed to spin it up.Leave a comment:
-
Quit with the nonsense! Things are very much the same in many ways. The design would be done the same and then local availability/conditions would be taken in to account.Leave a comment:
-
Leave a comment:
-
Leave a comment:
-
@ Naptown, Yes you are thinking right,it sounds mad, but things are much different in Pakistan than USA,
First of all, You must try to understand the power shortage problem & available solar products/solutions in Pakistan
then you will be at a better position to suggest & guide us members from Pakistan.
I have learned a lot on this forum & will appreciate any sort of help from you,
Thanks.
Step one identify daily load in Watt hours
Step 2 identify daily insolation.Leave a comment:
-
Leave a comment:
-
Leave a comment:
-
First of all, You must try to understand the power shortage problem & available solar products/solutions in Pakistan
then you will be at a better position to suggest & guide us members from Pakistan.
I have learned a lot on this forum & will appreciate any sort of help from you,
Thanks.Leave a comment:
-
Leave a comment:
-
Please describe the irrigation system
Open ditch, pressure sprinklers, Water tower or elevated storage and drip irrigation? how is the area irrigated?Leave a comment:
-
In case of agri pump I am not interested to run this on batteries,i just wants its working in day light with the help of inveter . There is no need of batteries. Yes I need batteries in home and fuel station model.Leave a comment:
Leave a comment: