Designing of off grid solar system
Collapse
X
-
-
Comment
-
Quit with the nonsense! Things are very much the same in many ways. The design would be done the same and then local availability/conditions would be taken in to account.[SIGPIC][/SIGPIC]Comment
-
Then what you want is a Grid - Tie inverter. It feeds power into the grid, and will offset your pump's usage.
As for an inverter that can power a 5hp pump. It will be VERY expensive. It's likely a 3-phase motor, and consumes 6,000 watts, with several times that power needed to spin it up.Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
Then what you want is a Grid - Tie inverter. It feeds power into the grid, and will offset your pump's usage.
As for an inverter that can power a 5hp pump. It will be VERY expensive. It's likely a 3-phase motor, and consumes 6,000 watts, with several times that power needed to spin it up.Comment
-
I wants to run the pump from grid supply in case of emergency only. The pump will run on solar in day time it starts running from morning and keeps going till evening. The pumps takes 35 amp at its start up and settles at 15 amp at its running. It is a single phase and will run continuesly for 5-8 hrs every day. Please advice accordingly.
Based on running 8 hour per day you are going to need
Panel wattage = 9600 watts divided into 3 systems of 3200 watts each with its own separate Charge Controller
Battery capacity configured @ 48 volts = 3000 AH, approx weight = 9000 lbs or 4100 Kg
Charge Controllers = 3 units 80 Amp MPPT
Inverter = Industrial Grade 10 KvaMSEE, PEComment
-
I wants to run the pump from grid supply in case of emergency only. The pump will run on solar in day time it starts running from morning and keeps going till evening.
The pumps takes 35 amp at its start up and
settles at 15 amp at its running. It is a single phase and will run continuesly for 5-8 hrs every day.
Please advice accordingly.
240 @ 15A = 3600 running watts (starting is generally at least 5x this, or about 18,000watts, will need a very stout inverter, wires & batteries to supply this - 8400 w @ 48V = 175 amps starting, 75a running, from 48VDC)Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
240VAC @ 35A = 8400 starting watts for 5 seconds (likely much higher, but your meter can't read it)
240 @ 15A = 3600 running watts (starting is generally at least 5x this, or about 18,000watts, will need a very stout inverter, wires & batteries to supply this - 8400 w @ 48V = 175 amps starting, 75a running, from 48VDC)
About inverter size and array setting
220 volts are used in Pakistan
frequency 50 hertzComment
-
generic Grid-Tie (batteryless)
or
Off-Grid with batteries, PV and inverter that Sunking listed
Panel wattage = 9600 watts divided into 3 systems of 3200 watts each with its own separate Charge Controller
Battery capacity configured @ 48 volts = 3000 AH, approx weight = 9000 lbs or 4100 Kg
Charge Controllers = 3 units 80 Amp MPPT
Inverter = Industrial Grade 10 Kva
Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
Comment
-
Comment
-
Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
Solar Pumps
For the 5 HP pump, you can use amorphous panels, just connect series of them to have the grid voltage ( if it is 230 V 50 Hz, I don't know) you will need 230*SQRT(2)=330 Volts aprox. Then connect others series in parallel to reach the amps needed.
Then connect the output from the solar pannels to the DC input of the VFD and you have it, connect the electrical motor in a star configuration if it is rated to 230 V star. The VFD will do the rest.
For providing a better control use a LDR (Light dependant resistor, in a voltage divider) connect the voltage divider to the DC source included with most of the inverters, and the output to the potentiometer input of the VFD. The VFD will control the frequency depending on the solar light falling into the LDR (the LDR must be at the same place as the amorphous panels, same orientation and inclination). Thus you will have more pumping hours, but don't be confused, less frequency lower water flow. And this has a limit, when there is not enough power the VFD will stop the motor. You will have to change some parameters in the VFD, in order to automatically restart the motor, in case there are some passing clouds. Only if there is no life threatening due to motor automatic restart.
I will be delighted to hear from this if you try.
Good luck!!!
Wedge.Comment
-
What a joke. I get it though.MSEE, PEComment
-