    Need ideas on how to keep a 24V batery bank warm in the winter (6V x 4 bat)

    I've seen charts that show battery banks at only 35% of rated capacity when the outside temp. hits -20 degrees F, which is about how cold it gets where I live on the coldest couple days of each winter. But in order to stay safe and keep a FLA battery bank vented I'm assuming that the vented enclosure must be located outside of the home. If that is the case, how do you keep them warm so they deliver their rated capacity (to 50% max) in the winter? Need some ideas.
  • inetdog
    Super Moderator
    • May 2012
    • 9909

    #2
    Originally posted by Silver_Is_Money
    I've seen charts that show battery banks at only 35% of rated capacity when the outside temp. hits -20 degrees F, which is about how cold it gets where I live on the coldest couple days of each winter. But in order to stay safe and keep a FLA battery bank vented I'm assuming that the vented enclosure must be located outside of the home. If that is the case, how do you keep them warm so they deliver their rated capacity (to 50% max) in the winter? Need some ideas.
    You can keep an FLA battery bank inside as long as you keep the box ventilated to the outside. The acid mist and sulfur gasses given off during end of charge and equalization are more of a concern than the hydrogen given off. Just do not seal the box without any ventilation exits from the very top where hydrogen could collect.
    It actually diffuses so well that with any ventilation at all the concentration should not get dangerously high.

    If you put your batteries outside and insulate them very well the normal heat from charging and discharge might keep them at a usable temperature range anyway.
    SunnyBoy 3000 US, 18 BP Solar 175B panels.

    Comment

    • Silver_Is_Money
      Solar Fanatic
      • Aug 2014
      • 148

      #3
      Originally posted by inetdog
      If you put your batteries outside and insulate them very well the normal heat from charging and discharge might keep them at a usable temperature range anyway.
      Does anyone have direct experience here?

      Comment

      • Sunking
        Solar Fanatic
        • Feb 2010
        • 23301

        #4
        Done every day around the world, routine with outdoor cellular cell sites, not so much with Solar but a few. I have several sites in NN and AZ at altitude. Some AGM, some FLA.

        When outdoors you just have to design for it. Batteries are odd things. When hot they have higher capacity but shorter lives. In cold they have lower capacity and longer lived.

        -20 is not extremely cold for a battery if it is charged up. AGM is almost impossible to freeze. Trick is to select the right battery type, and adjust capacity for the temperature. -20 F is no problem for FLA assuming you can get it charged. Even less of a problem if you are only talking brief dips to -20 infrequently. Insulation will help coupled with proper charging will heat the battery, and thermal mass all help.

        What you have to do is size the battery to account for the capacity loss, and up size the panel wattage to account for larger battery and short days of winter. That could bring about exceeding C/8 charging and force you to use AGM.

        Completely workable, all it takes is money.

        Smart money is bring the batteries inside as Dave suggested.
        MSEE, PE

        Comment

        • Silver_Is_Money
          Solar Fanatic
          • Aug 2014
          • 148

          #5
          Originally posted by Sunking
          Smart money is bring the batteries inside as Dave suggested.
          Does bringing them inside the home require going with AGM?

          Comment

          • inetdog
            Super Moderator
            • May 2012
            • 9909

            #6
            Originally posted by Silver_Is_Money
            Does bringing them inside the home require going with AGM?
            Not as long as they are properly enclosed and ventilated.
            And even AGMs can vent if abused, so some provision should be made for that occurrence anyway.
            SunnyBoy 3000 US, 18 BP Solar 175B panels.

            Comment

            • Mike90250
              Moderator
              • May 2009
              • 16020

              #7
              Originally posted by Silver_Is_Money
              Does bringing them inside the home require going with AGM?
              No. Because AGM can also vent, you will need a robust battery containment system for either type. So I'd just use Flooded.
              The box needs to be a swimming pool to contain spilled acid, and the lid needs to direct fumes outside the dwelling.
              Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
              || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
              || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

              solar: http://tinyurl.com/LMR-Solar
              gen: http://tinyurl.com/LMR-Lister

              Comment

              • lkruper
                Solar Fanatic
                • May 2015
                • 892

                #8
                Originally posted by Mike90250
                No. Because AGM can also vent, you will need a robust battery containment system for either type. So I'd just use Flooded.
                The box needs to be a swimming pool to contain spilled acid, and the lid needs to direct fumes outside the dwelling.
                Would you use flooded inside a van converted to rv (Class B) with the same battery containment system?

                Comment

                • Mike90250
                  Moderator
                  • May 2009
                  • 16020

                  #9
                  Originally posted by lkruper
                  Would you use flooded inside a van converted to rv (Class B) with the same battery containment system?
                  Van & RV applications need battery tie downs, and in case of roll-over, a way to contain the acid I suspect. Or have it outside the occupied portion.
                  Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                  || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                  || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                  solar: http://tinyurl.com/LMR-Solar
                  gen: http://tinyurl.com/LMR-Lister

                  Comment

                  • Sunking
                    Solar Fanatic
                    • Feb 2010
                    • 23301

                    #10
                    Silver bringing FLA batteries inside is no more dangerous than having a wood/coal burning stove or fireplace in the house. Figure it out, you are smart enough.
                    MSEE, PE

                    Comment

                    • lkruper
                      Solar Fanatic
                      • May 2015
                      • 892

                      #11
                      Originally posted by Mike90250
                      Van & RV applications need battery tie downs, and in case of roll-over, a way to contain the acid I suspect. Or have it outside the occupied portion.
                      Did not consider roll-over. That's a high bar! AGM's would have the same requirement?

                      Comment

                      • Sunking
                        Solar Fanatic
                        • Feb 2010
                        • 23301

                        #12
                        Originally posted by lkruper
                        Did not consider roll-over. That's a high bar! AGM's would have the same requirement?
                        AGM have niche applications. They can be installed at unusual orientation like on their sides an inverted where spills cannto be tolerated. They were developed for the Aircraft military industry where extreme temps and orientation are an issue. They also have very low internal resistance so they can run very high speed heated air to start jet engines.

                        Also good choices for EV's. Trick is they cost big bucks. So use then where you can justify the expense.
                        MSEE, PE

                        Comment

                        • Mike90250
                          Moderator
                          • May 2009
                          • 16020

                          #13
                          Originally posted by lkruper
                          Did not consider roll-over. That's a high bar! AGM's would have the same requirement?
                          Vehicle batteries have to be tied down or restrained. Bouncing down a road can bring terminals into contact with something that could short them out, or tear them loose from the cables.
                          Since AGM can vent under certain conditions, their box must be vented outside the inhabited space, like you would plain flooded.


                          But you can insulate an outdoor battery case for winter usage.
                          Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                          || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                          || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                          solar: http://tinyurl.com/LMR-Solar
                          gen: http://tinyurl.com/LMR-Lister

                          Comment

                          • Silver_Is_Money
                            Solar Fanatic
                            • Aug 2014
                            • 148

                            #14
                            Does adding water to FLA's require that they be disconnected to any degree in order to do so?

                            Comment

                            • Sunking
                              Solar Fanatic
                              • Feb 2010
                              • 23301

                              #15
                              Originally posted by lkruper
                              Did not consider roll-over. That's a high bar! AGM's would have the same requirement?
                              AGM batteries were invented for military aircraft industry. The best AGM battery made is by the company who invented them. Concorde makes a full line of AGM batteries. They make awesome RV, Wheelchair, Sun Extender, Marine, and Racing AGM batteries.