    ok so a quick background...

    we have an off grid cabin... we use very very little electricity there. we currently have 200w of panels through a pwm controller charging a traditional 12v marine deep cycle battery. it meets our needs 9 months out of the year. during the summer that sucker is topped off by 9am. we typically use 40ah in a 4 day weekend between our led lights, cell phone chargers, radio, and our 12v pump. about 100 yards away i have a pavilion with 100w of panels and another deep cycle battery that runs led lights and car radio. again... plenty of power to get that thing topped off within an hour of sunrise.

    now, i mentioned the 9 months.... well the other 3 months, we have a trifecta of things that stress the cabin's system... 1, shorter daylight, so less charging, 2 its cold out so we arent hanging at the pavilion, so we are in the cabin the whole time, and 3. we are using a lot more lights in the cabin...

    so in the winter during hunting season we end up dropping the voltage down to 12v and we get nervous and start using propane lanterns. not ideal.

    but... we dont use the pavilion at all in the winter. so i was thinking i could move the battery up from there to cover our extra needs during those 3 winter weekends we go up there. we have figured out that a water pump and one other circuit is almost always close to half of our load. so we could easily move a pair of leads to the other battery on the "load" end of things... but for charging... how could we wire it so it kept the batteries isolated so they dont kill each other, but still both get the same amount of charge from the panels?

    we also plan on adding a 3rd 100w panel at the cabin. our controller can handle 4.

    thanks a lot for your advice!
  • Sunking
    Solar Fanatic
    • Feb 2010
    • 23301

    #2
    Your mistake is off grid systems are designed for worse case. You cannot use summer or annual usage because in winter you will go DARK. Sound familiar?

    You design for winter by knowing your daily watt hour usage. From that you then determine battery size and panel wattage. For you that means both more panel wattage and larger battery.

    So if you use 40 AH a day means you need a 200 AH battery. As for panel wattage depends on location, shade issues, and what controller type you use. Let' say you live south of Interstate 40 and use a MPPT controller would need a inexpensive GT 200 watt panel with a 15 amp MPPT controler. If you have a 15 amp PWM controller you must use expensive battery panels, of 300 watts using 100 or 150 watt panels in parallel.

    Now say you are in Gloomy Doomy Pacific NW winter you would need a 500 watt GT panel with 40 amp MPPT controller, or 750 watts of expensive battery panels with a 40 amp PWM controller. In addition to a lot more power wil also require a much more expensive AGM battery to handle the extremely high charge current.

    FWIW 12 volt is more than nervous. That means you have used just over 50% of the capacity which is a NO-NO. Limit daily use to no more than 25%. Just one cloudy day and you are toast.
    MSEE, PE

    Comment

    • idiggplants
      Junior Member
      • Mar 2011
      • 40

      #3
      Originally posted by Sunking
      Your mistake is off grid systems are designed for worse case. You cannot use summer or annual usage because in winter you will go DARK. Sound familiar?

      You design for winter by knowing your daily watt hour usage. From that you then determine battery size and panel wattage. For you that means both more panel wattage and larger battery.

      So if you use 40 AH a day means you need a 200 AH battery. As for panel wattage depends on location, shade issues, and what controller type you use. Let' say you live south of Interstate 40 and use a MPPT controller would need a inexpensive GT 200 watt panel with a 15 amp MPPT controler. If you have a 15 amp PWM controller you must use expensive battery panels, of 300 watts using 100 or 150 watt panels in parallel.

      Now say you are in Gloomy Doomy Pacific NW winter you would need a 500 watt GT panel with 40 amp MPPT controller, or 750 watts of expensive battery panels with a 40 amp PWM controller. In addition to a lot more power wil also require a much more expensive AGM battery to handle the extremely high charge current.

      FWIW 12 volt is more than nervous. That means you have used just over 50% of the capacity which is a NO-NO. Limit daily use to no more than 25%. Just one cloudy day and you are toast.
      you misread. 40ah in a 4 day weekend.

      according to our meter we are hitting 12v after much less than 50ah of draw. the battery is on its way out... but regardless. we arent using nearly half the battery's capacity in 2 days, let alone 1.

      idk. my numbers arent exactly accurate. id just like my actual question answered... how can i add that second battery to the charge controller while keeping the batteries separated, but the controller charging both.

      Comment

      • SunEagle
        Super Moderator
        • Oct 2012
        • 15185

        #4
        Originally posted by idiggplants
        ok so a quick background...

        we have an off grid cabin... we use very very little electricity there. we currently have 200w of panels through a pwm controller charging a traditional 12v marine deep cycle battery. it meets our needs 9 months out of the year. during the summer that sucker is topped off by 9am. we typically use 40ah in a 4 day weekend between our led lights, cell phone chargers, radio, and our 12v pump. about 100 yards away i have a pavilion with 100w of panels and another deep cycle battery that runs led lights and car radio. again... plenty of power to get that thing topped off within an hour of sunrise.

        now, i mentioned the 9 months.... well the other 3 months, we have a trifecta of things that stress the cabin's system... 1, shorter daylight, so less charging, 2 its cold out so we arent hanging at the pavilion, so we are in the cabin the whole time, and 3. we are using a lot more lights in the cabin...

        so in the winter during hunting season we end up dropping the voltage down to 12v and we get nervous and start using propane lanterns. not ideal.

        but... we dont use the pavilion at all in the winter. so i was thinking i could move the battery up from there to cover our extra needs during those 3 winter weekends we go up there. we have figured out that a water pump and one other circuit is almost always close to half of our load. so we could easily move a pair of leads to the other battery on the "load" end of things... but for charging... how could we wire it so it kept the batteries isolated so they dont kill each other, but still both get the same amount of charge from the panels?

        we also plan on adding a 3rd 100w panel at the cabin. our controller can handle 4.

        thanks a lot for your advice!
        What you did not mention is the Ah rating of that marine deep cycle battery or the one out at the pavilion.

        With those 200 watts of panels and a PWM CC you are probably getting a maximum of 11 amps of charging which is good for a 100Ah to 150Ah battery.

        Now the problem I see is that you may not have enough charging amps from that 200 watts of panels to add the second battery. Also having longer leads on that second battery will only hurt you more and make the charging very unequal. (different charging paths with different resistance values is no good). Once those batteries are wired together to be charged you have no easy way of isolating them so one does not affect the other.

        Another thing to consider is that connecting two batteries with different usage patterns together will cause the "weaker" battery to hurt the "stronger" one. Battery systems should be all the same age and get all the same charging/discharging cycles or they deteriorate at different time lines.

        So if you want more power at the cabin then get a bigger Ah battery and increase your panel wattage so that it provide at least 1/10th the Ah rating for charing.

        Comment

        • Sunking
          Solar Fanatic
          • Feb 2010
          • 23301

          #5
          Originally posted by idiggplants

          you misread. 40ah in a 4 day weekend.

          according to our meter we are hitting 12v after much less than 50ah of draw. the battery is on its way out... but regardless. we arent using nearly half the battery's capacity in 2 days, let alone 1.

          idk. my numbers arent exactly accurate. id just like my actual question answered... how can i add that second battery to the charge controller while keeping the batteries separated, but the controller charging both.
          Does not change the answer. If the battery is shot, you do not have the capacity you think you have. You cannot mix batteries, and you must meet minimum charging requirements of the battery.

          For a 12 volt battery system for every 100 AH of battery capacity on a PWM system you must use 170 watts of panels and 10 amps of controller rating to meet the minimum charge requirements. You claim to have a 200 watt panel of unknown type being battery or GT with a PWM controller and unspecified battery capacity that is shot. You say the battery is a 12 volt Marine Battery. What size in AH. Not likely even 100 AH as that would be a huge battery.

          If it were me, I would buy new batteries, and a good charger 20 to 40 amp Float Charger. Take the batteries home with me, charge them up, take them with me and use whatever two solar chargers you have to supplement while at the camp. Last thing you want to do is mix batteries, use a common solar charger on site, and then split them up to use.

          MSEE, PE

          Comment

          • idiggplants
            Junior Member
            • Mar 2011
            • 40

            #6
            Originally posted by SunEagle


            Another thing to consider is that connecting two batteries with different usage patterns together will cause the "weaker" battery to hurt the "stronger" one. Battery systems should be all the same age and get all the same charging/discharging cycles or they deteriorate at different time lines.
            yeah, thats generally why we want them isolated. but it sounds like that isnt really an option.
            ive seen charge controllers such as these:
            https://www.amazon.com/RENOGY-Dual-B...rge+controller
            that are made for 2 batteries. i wasnt sure if there was something we could add to our charge controller that would do something similar.

            i think the batteries are 100ah. they are the typical deep cycle batteries that people get for their rv's and boats. the biggest ones readily available. id have to make a few phone calls to find out any more info.

            we are at the cabin 3 times a year for the weekends we have trouble with.

            my issue with the advice of needing more panels that is always the advice i get from solar forums... more panels... more panels... that that was the advice we got before we did anything. people were saying... ohh, you need 1000w of panels and 3 batteries, all this nonsense... and our 200w + single battery setup is pretty much enough. our battery has lasted 4 years on this setup? and probably another 2 years previous to that of use as a carry in- use for 3 days... take home and charge on the trickle charger. so im a bit suspicious when i get recommendations to add more panels.

            all we are looking to do is add a slight bit more capacity with a battery that we have that isnt being used., not reinvent the wheel. i figure if the panels have to charge 10ah? from one battery vs 5ah from 1 battery +5ah from another battery, it shouldnt matter too much. it just lets us drain each battery a bit less. and again... this is 3 times a year. actually more than likely, 2 times a year. rifle season and muzzleloader season.

            anyways. sorry if i sound rude or unappreciative. i just feel like i know that we arent that far away from a completely sustainable setup. buying a simple isolator is one thing... but adding $200 in panels and another $120 battery to the setup... ill just stick with propane lights!

            Comment

            • idiggplants
              Junior Member
              • Mar 2011
              • 40

              #7
              Originally posted by Sunking
              Last thing you want to do is mix batteries, use a common solar charger on site, and then split them up to use.
              i mean... thats why i asked about an isolator of sorts.

              Comment

              • Sunking
                Solar Fanatic
                • Feb 2010
                • 23301

                #8
                Battery Isolators are used in RV's and Trucks that use a Starter battery (SLI) and House battery (Deep Cycle) charged from a alternator. They use different charge voltages because a deep cycle battery voltage is lower than a SLI starter battery. The Isolator takes the voltage regulator control out of the alternator and uses the Isolator regulator to control the alternator voltage output. Not compatible with a Solar Charge Controller.

                You can charge two parallel batteries with a Solar Charge controller. But to do so both batteries must be the same make, model, age, and work together so they are always at the same State of charge sharing a common load so they charge and discharge at the same rate or identical twins. Otherwise they just fight each other and the stronger battery is weakened by the weaker battery. You can get away with it for a while, but soon you will notice each battery declines and significantly shorter battery life if you are OK with that. Instead if 3 to 4 years service, 1 or 2 years.
                Last edited by Sunking; 01-26-2017, 03:09 PM.
                MSEE, PE

                Comment

                • idiggplants
                  Junior Member
                  • Mar 2011
                  • 40

                  #9
                  Originally posted by Sunking
                  Battery Isolators are used in RV's and Trucks that use a Starter battery (SLI) and House battery (Deep Cycle) charged from a alternator. They use different charge voltages because a deep cycle battery voltage is lower than a SLI starter battery. The Isolator takes the voltage regulator control out of the alternator and uses the Isolator regulator to control the alternator voltage output. Not compatible with a Solar Charge Controller.

                  You can charge two parallel batteries with a Solar Charge controller. But to do so both batteries must be the same make, model, age, and work together so they are always at the same State of charge sharing a common load so they charge and discharge at the same rate or identical twins. Otherwise they just fight each other and the stronger battery is weakened by the weaker battery. You can get away with it for a while, but soon you will notice each battery declines and significantly shorter battery life if you are OK with that. Instead if 3 to 4 years service, 1 or 2 years.
                  i guess my term of "isolator" was more of a generic term... a way for me to isolate 2 batteries from one another... with some device... .not necessarily an "isolator" in the official sense.

                  what about one of these:
                  https://www.amazon.com/RENOGY-Dual-B...rge+controller

                  which seems to do what im looking to do... and charge 2 batteries separately... i would think it wouldnt be impossible to have a charge "manager" that would direct the charge input to 2 different batteries based off of what the 2 batteries voltages were. but i guess they dont make anything like that... so i guess im a t a dead end.

                  Comment

                  • Mike90250
                    Moderator
                    • May 2009
                    • 16020

                    #10
                    Ok, so now the battery is toast
                    Future, you need to plan for the winter days, and need more PV panels, Shade will completely shut down a panel, so make sure there is no shade on the panel, even the shadow of a small twig is enough to halt output.
                    Sounds like you are using a Group 27 size battery (about as large as you can lift and about 100ah) Group 24 are about 80ah.
                    If you add more battery, you have to add more PV to recharge it, thinking that 4 idle days will recharge it, just walks the capacity slowly down as it sulfates a little bit each day it's below 80%.
                    And likely there's a few more cell phones and such, loads always seem to expand!
                    But the solution is more solar, either remove shade, or add more panels. Or can you haul it to the car and run the engine to recharge it a bit ?
                    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                    solar: http://tinyurl.com/LMR-Solar
                    gen: http://tinyurl.com/LMR-Lister

                    Comment

                    • bcroe
                      Solar Fanatic
                      • Jan 2012
                      • 5221

                      #11
                      If you move the battery, the pavilion panels are still needed to keep it up. With the whole system moved to
                      the cabin, you could split your loads into the 2 systems. Or you could even use a diode from each battery
                      to feed all the loads if they will tolerate another 3/4V loss; the diodes would be reversed from the type isolator
                      used to charge 2 batteries.

                      Leaving the pavilion panels in place would result in big loss in the wiring out to them. You could beat that
                      by having say 3 panels in series out there to get the V up and the I down; then use a good MPPT controller
                      for this system.

                      I see the step after that is adding panels, with some facing east or west to in effect lengthen your day, and
                      to collect more under clouds (like here). Bruce Roe

                      Comment

                      • idiggplants
                        Junior Member
                        • Mar 2011
                        • 40

                        #12
                        Originally posted by bcroe

                        Leaving the pavilion panels in place would result in big loss in the wiring out to them.
                        could you expand on that?

                        ok, so lets assume we go with 4 panels in the cabin. we only really need those extra 2 in the winter time. but they will be there all the time. the battery, however, can be moved back and fourth pretty easily. it would be really nice to not have a 3rd battery... considering we dont need one at all out there during the winter. and we dont need one at all in the cabin during the summer. so... completely ignoring the panels, and if we have enough... lets completely forget about that.

                        is there ANY way to isolate the batteries, but charge them with the same charge controller?

                        Comment

                        • bcroe
                          Solar Fanatic
                          • Jan 2012
                          • 5221

                          #13
                          Like the Power Co, you will find transmission over any distance is far easier at higher voltages. Just
                          take the resistance of the wire you hoped to use, use ohms law at 12V and 36V, and you will see about
                          a 9:1 difference in loss. That difference will be even bigger including the change to MPPT.

                          As others have said, the extra battery isn't going to work out if you don't have the extra power to
                          maintain the increased load. And you can have isolated or not isolated, but not at the same time.
                          Bruce Roe

                          Comment

                          • idiggplants
                            Junior Member
                            • Mar 2011
                            • 40

                            #14
                            Originally posted by bcroe
                            Like the Power Co, you will find transmission over any distance is far easier at higher voltages. Just
                            take the resistance of the wire you hoped to use, use ohms law at 12V and 36V, and you will see about
                            a 9:1 difference in loss. That difference will be even bigger including the change to MPPT.

                            As others have said, the extra battery isn't going to work out if you don't have the extra power to
                            maintain the increased load. And you can have isolated or not isolated, but not at the same time.
                            Bruce Roe
                            ohh, i see, so you are saying i could tie the solar panels at the pavilion into the cabin if i upped the voltage and got an mppt... nahh... its about 300' away. after paying for a mppt, we could just get a couple extra panels at the cabin.

                            Comment

                            • Sunking
                              Solar Fanatic
                              • Feb 2010
                              • 23301

                              #15
                              Originally posted by idiggplants
                              ohh, i see, so you are saying i could tie the solar panels at the pavilion into the cabin if i upped the voltage and got an mppt... nahh... its about 300' away. after paying for a mppt, we could just get a couple extra panels at the cabin.
                              No I do no think you understand. No controller is going to overcome 300 feet distance. Perhaps thi smight click. It takes a 300 watt system to equal a 200 watt MPPT system. A real MPPT 15 amp controller like a Morningstar SunSaver 15 amp model is around $200 and at 12 volt battery can input 200 watts, and 400 watts at 24 volt battery. Cheaper than a another over priced battery panel. The advantage of MPPT allows you to use much higher voltage grid tied panels which cost 1/2 of what low voltage battery panels cost. A 300 Watt PWM system will cost you around $600 to $700. A 200 watt MPPT system only needs a single 200 watt panel, or as many battery panels as you want wired in series. Use a GT panel cost $400 to $500. PWM is just antiquated and to expensive for anything less than 200 watts.

                              MSEE, PE

                              Comment