over charger batteries???? 12v now is over 17v??????:(
Collapse
This topic is closed.
X
X
-
-
batteries??
Those batteries you have are completely inappropriate for Renewable energy applications, and you configuration of using 20 in parallel is insane just asking to be killed.
What you have is batteries designed for UPS systems emergency Stand By Power. They are not made for cycle service. . At best they have maybe 100 to 200 cycles in them or less than 1 year service in a cycle RE service.
When you replace them by batteries for cycle service and sized so you only need 1 string.
I also agree with John it would be almost impossible to get a 12 volt battery up to 17 volts. Only way to do that is they are open circuited (destroyed). Take one out and measure the voltage after it has rested for a few hours. Bet it will be less than 12.6 volts. If so you now have an expensive boat anchor.
what kind of bateries are good what brand name?
and what is the best conection?
12v
24v
48v
right now i have everything 12v
my power inverter is for 12v
thanks again
gracias!!Comment
-
inapropriate? sorry i didnt know??
Those batteries you have are completely inappropriate for Renewable energy applications, and you configuration of using 20 in parallel is insane just asking to be killed.
What you have is batteries designed for UPS systems emergency Stand By Power. They are not made for cycle service. . At best they have maybe 100 to 200 cycles in them or less than 1 year service in a cycle RE service.
When you replace them by batteries for cycle service and sized so you only need 1 string.
I also agree with John it would be almost impossible to get a 12 volt battery up to 17 volts. Only way to do that is they are open circuited (destroyed). Take one out and measure the voltage after it has rested for a few hours. Bet it will be less than 12.6 volts. If so you now have an expensive boat anchor.
hopely is ok...?
whats is the best thing to do?
do i have to buy a " 24v POWER INVERTER"
(sorry my english im spanish never went to school for english just spanish)
i would like to learn how the solar panels and bank of batteries work
in mexico cost of electricity is so expensive!
i just call a company for a new charger controller from germany 30A
Solar
Solarix MPPT ?010
i dont have yet but i will....
if you have any sugestion and how to line up my bateries in what kind of?
12v ?
24v ?
48v ?
and what brand of inverter do i have to buy?
sutf like that i will really apreciate and thank you to everyone
that kindly try to help me on my solar ...
and to help the planet heart
thank you to everyone!!!!!!!!!!!!!!!!!!!!Comment
-
disconected all
Luisito. it very hard to offer you a controler without knowing the following..
you using a solar panel array??? if yes what is total wattage??
you using a wind generator?? if yes its rated output,?
Do you have th e AMPHOUR rating of each of those batteries??
What size inverter you using??
What loads are you using on the inverter??
With regards to to batteries as you may have 20 of them a 40a charger is only ever going to put 2a into each one... enough to replace self loss in the battery.. with very little available to power an inverter..
my invereter is pure sine 1500 watts 12V
i have only one solar panel 80 watts
i will make a video doing on my problem so other people can get some help too
like me i was going to buy $150.00 on a 24v inverter of 400 watts
then somebody toll me that just to buy a 12v lightbuld and coenected directly to only one battery.? but is taking so much time to drope????
or ? i should go and buy the 24 v inverter puresine???
in ge it ???
que dolor de cabezA????
thanks again !!
looking forward:LuisComment
-
charger controller?
Sunking I agree with you 1001% That is why I have asked him the questions I have.. Each question is as important as the other, .You will notice he was asking about a "diversion load charger" That may indicate wind generator.???? I did note if he had a 40a charger at best it will just support battery self losses only.
We as yet have no idea as to what his loads are on the unknown inverter.
but if i do? i thing if better the highter of amper is much better? no?
i do have a wind turbine but is not install yet i rather expend more time to get some info
or i will damage my all things better charger controller a least 160A my wind turbine is
700 watts ...
im still im new to the solar windturbine and solar batterys?????
anyway
frist is to fix my baterys then i will move on the wind turbine....
and VOILA! (french expresion)
i will be really happy!
thank you!Comment
-
Comment
-
charger controller?
John it looks like he is using 20 of GNB S12V300. which is a 300 AH 12 volt battery made for UPS systems. He claims 20 of them for a 12 volt @ 6000 AH. There is no panel wattage he can run to support that much battery, at least not with any single charge controller.
It would take at least a 6000 watt solar panel array using 6 80 amp amp MPPT charge controllers to support that much battery at 12 volts, and no one who knows anything about RE battery application would use this battery, or use that much battery at 12 volts. It screams for 48 and 96 volt battery configuration.Comment
-
It is not mean, it is fact. If you have 20 of the 12 volt 300 AH batteries you need 6000 watts of solar panels and a minimum of 6 80 amp charge controllers. Not 1 or 2 40 amp CC's, 6 of them with with 6000 watts of solar panels.
So something is very wrong with what you claim Just having 1 charge controller is not enough to even over come the self discharge rate. No chance you could have ever over charged the batteries to begin with.MSEE, PEComment
-
Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
Comment
-
hello???
John it looks like he is using 20 of GNB S12V300. which is a 300 AH 12 volt battery made for UPS systems. He claims 20 of them for a 12 volt @ 6000 AH. There is no panel wattage he can run to support that much battery, at least not with any single charge controller.
It would take at least a 6000 watt solar panel array using 6 80 amp amp MPPT charge controllers to support that much battery at 12 volts, and no one who knows anything about RE battery application would use this battery, or use that much battery at 12 volts. It screams for 48 and 96 volt battery configuration.
but i dont understand???
what do i need to do?
to config my bateries at 48 v
so thats mean i have to buy a higher charger controller??
whats a mean MPPT???
ThanksComment
-
i just bought 160 A charge controller
It is not mean, it is fact. If you have 20 of the 12 volt 300 AH batteries you need 6000 watts of solar panels and a minimum of 6 80 amp charge controllers. Not 1 or 2 40 amp CC's, 6 of them with with 6000 watts of solar panels.
So something is very wrong with what you claim Just having 1 charge controller is not enough to even over come the self discharge rate. No chance you could have ever over charged the batteries to begin with.
to fill the baterie how much they to be?
13v or 14v?
mys batries still disconected when i get my new charger controller i will coected
all my bateries
how can i know if my bateries are damage???
thanlk you!!Comment
-
Comment
-
During part of the charge cycle, 14.5V will be fed to the batteries to "push" the charge into a 12V battery. This is NOT something you can do by hand with a voltmeter. (well, if you could, you would not be here asking)
You should let the charge controller manage your batteries for 3 sunny days with no loads on them at night, that should fully charge the batteries.
Then you can use them overnight, if the are dead (below 11.5V ) in the morning, the batteries are either damaged, or you don't have enough capacity for your loads.Attached FilesPowerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
thank you
You need a charge controller that performs 3 stage charging, Bulk, Absorb, Float
During part of the charge cycle, 14.5V will be fed to the batteries to "push" the charge into a 12V battery. This is NOT something you can do by hand with a voltmeter. (well, if you could, you would not be here asking)
You should let the charge controller manage your batteries for 3 sunny days with no loads on them at night, that should fully charge the batteries.
Then you can use them overnight, if the are dead (below 11.5V ) in the morning, the batteries are either damaged, or you don't have enough capacity for your loads.
i bought
160 AMPS
MAYBE one week i will get my charger contrroller
you think
i should config my batteries for 24V????
looking forward: LuisComment