I trying to finalize the configuration on an off-grid PV system and I've encountered a couple of issues with sizing the charge controllers with the batteries The design overview is as follows:
7050 watt array – 30 ea. Sharp 235’s – 2 strings (3 series - 5 parallel)
Inverter peak requirements – 7800 Watts
Battery Bank: 48 volt @ 2,700 AH – 24 Rolls Surrette 4KS-25PS @ 1350Ah: 2 strings parallel with 12 series
Genset – Generac Guardian 25kW - 120/240V - 107Amp Output
1 ea. - Outback Radian GS8048 Inverter/Charger
1 ea. – Outback Radian GS Load Center – GSL175-PV-120/240
2 ea. – Outback FX80 Charge Controllers
1 ea. – Outback Mate3 Display/Controller
1 ea. – Outback Hub4 Communications Manager
Other Considerations:
The Genset is already obtained.
This is an Off-Grid installation, thus no grid tie. All AC power will be generated by the Genset.
Each FX80 charger connected to one PV string (3525 watts)
Rolls Surrette recommends the 4KS-25PS batteries be charged at the C/10 rate, which is either 135 Amps or 270 amps. Obviously, which one makes a huge difference in the practicality of this configuration.
My questions are:
Is the charge controller sized to the Ah capacity of the individual battery capacity or the total storage in bank?
If the controllers are sized to the individual battery Ah, are there other considerations I should consider with this configuration?
If the controllers are sized to the bank, are there any alternatives to this configuration that could address the charging issue, such as, intermittent use of the Genset, other charge controllers, etc. ?
Finally, does anyone have any experience with the Outback Radian equipment?
Thanks Anawa - in Georgia
7050 watt array – 30 ea. Sharp 235’s – 2 strings (3 series - 5 parallel)
Inverter peak requirements – 7800 Watts
Battery Bank: 48 volt @ 2,700 AH – 24 Rolls Surrette 4KS-25PS @ 1350Ah: 2 strings parallel with 12 series
Genset – Generac Guardian 25kW - 120/240V - 107Amp Output
1 ea. - Outback Radian GS8048 Inverter/Charger
1 ea. – Outback Radian GS Load Center – GSL175-PV-120/240
2 ea. – Outback FX80 Charge Controllers
1 ea. – Outback Mate3 Display/Controller
1 ea. – Outback Hub4 Communications Manager
Other Considerations:
The Genset is already obtained.
This is an Off-Grid installation, thus no grid tie. All AC power will be generated by the Genset.
Each FX80 charger connected to one PV string (3525 watts)
Rolls Surrette recommends the 4KS-25PS batteries be charged at the C/10 rate, which is either 135 Amps or 270 amps. Obviously, which one makes a huge difference in the practicality of this configuration.
My questions are:
Is the charge controller sized to the Ah capacity of the individual battery capacity or the total storage in bank?
If the controllers are sized to the individual battery Ah, are there other considerations I should consider with this configuration?
If the controllers are sized to the bank, are there any alternatives to this configuration that could address the charging issue, such as, intermittent use of the Genset, other charge controllers, etc. ?
Finally, does anyone have any experience with the Outback Radian equipment?
Thanks Anawa - in Georgia