    Could you explain to me what a shunt does . I found a curcuit breaker and they said the shunt went along side the breaker. Where does the shunt hook up to and what does it do.
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    The SHUNT is a calibrated piece of wire, used to measure AMPS flowing through the circuit. The can get warm or even hot, I don't know that I'd park it next to a circuit breaker. The voltage across it (just a couple of millivolts) is used to calculate the amps flowing.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • DeltaFox 25
      Solar Fanatic
      • Oct 2009
      • 315

      #3
      Thank you very much. I didn't know if I should buy the cercuit braker and the shunt togeather.

      Comment

      • Mike90250
        Moderator
        • May 2009
        • 16020

        #4
        You need a Ckt Bkr to protect your wires and prevent a fire.

        Shunts for amps, are optional measurements.

        Battery Temperature Sensor for your charge controller, should be present, to provide correct charge voltage for your battery.
        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

        solar: http://tinyurl.com/LMR-Solar
        gen: http://tinyurl.com/LMR-Lister

        Comment

        • DeltaFox 25
          Solar Fanatic
          • Oct 2009
          • 315

          #5
          I am buying a new Morningstar 60 AMP MPPT charge controler and a tempiture probe . It will be coming in December.
          I need to put a fuse between the charge controler and the batteries. I already have one from the batteries to the inverter.
          Thank you

          Comment

          • Mike90250
            Moderator
            • May 2009
            • 16020

            #6
            Originally posted by DeltaFox 25
            I am buying a new Morningstar 60 AMP MPPT charge controler and a tempiture probe . It will be coming in December.
            I need to put a fuse between the charge controler and the batteries. I already have one from the batteries to the inverter.
            Thank you
            Do you know your array size/wattage, and battery bank voltage? Just take your array watts, and divide by your battery bank voltage, and you will have MAX amps to size your fuse and wires to. This is a crude way, but likely within 10% of the "right" value.
            Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
            || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
            || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

            solar: http://tinyurl.com/LMR-Solar
            gen: http://tinyurl.com/LMR-Lister

            Comment

            • DeltaFox 25
              Solar Fanatic
              • Oct 2009
              • 315

              #7
              Thank you Mike.

              Comment

              Working...