Is it OK to use solid copper wire between panels and charge controller?

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Chris_NH
    Junior Member
    • Aug 2012
    • 15

    #1

    Is it OK to use solid copper wire between panels and charge controller?

    Hi,
    It's a 125 watt 12v solar panel with 8 feet of solid copper 14 ga wire from the solar panel to the 10 amp charge controller.
    Is there any cause for concern here? Any significant lost power?
    Thanks!
  • Sunking
    Solar Fanatic
    • Feb 2010
    • 23301

    #2
    No problem if you use the right termination hardware like Wire Nuts of appropriate size. Every home built uses Wire Nuts and solid copper #12 AWG copper wire.
    MSEE, PE

    Comment

    • Chris_NH
      Junior Member
      • Aug 2012
      • 15

      #3
      Thanks.

      So it is largely a myth that solid copper wire is a poor choice for DC applications? I've heard from multiple sources that stranded wire is preferable (the more strands inside the better) because the electricity travels only on the outside of each strand and somehow DC requires it. Is this simply bad info?

      Comment

      • PowerSupplyGuy
        Banned
        • Mar 2013
        • 57

        #4
        AC travels on the outside of conductor. Google skin effect. Stranded wire doesn't do anything for ac current over solid wire unless each strand is individually insulated. Google "litz wire".

        Since you are dealing with DC then the complete conductor is utilized. Some may offer that Aluminum wire is less expensive /ohm/foot than
        copper. I use copper.


        regards,
        PSG

        Comment

        • Chris_NH
          Junior Member
          • Aug 2012
          • 15

          #5
          Thanks. That was some interesting reading. I assumed that stranded wire was somehow better for DC since everything that I've seen specifically for DC is stranded. All the PV cable that I've bought has been stranded and I assumed the reason was more than just flexibility of the cable.

          Comment

          • Naptown
            Solar Fanatic
            • Feb 2011
            • 6880

            #6
            Originally posted by Chris_NH
            Thanks. That was some interesting reading. I assumed that stranded wire was somehow better for DC since everything that I've seen specifically for DC is stranded. All the PV cable that I've bought has been stranded and I assumed the reason was more than just flexibility of the cable.
            that has more to do with crimping the terminals such as MC4 connectors to the wires. If running wires in conduit stranded are a bit easier to pull as they are more flexible.
            NABCEP certified Technical Sales Professional

            [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

            [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

            [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

            Comment

            • Sunking
              Solar Fanatic
              • Feb 2010
              • 23301

              #7
              Originally posted by Chris_NH
              Thanks. That was some interesting reading. I assumed that stranded wire was somehow better for DC since everything that I've seen specifically for DC is stranded.
              No stranded is just easier to work with and easier to terminate, but requires some expensive tools to terminate correctly. Once you get above 4 or 6 AWG it is all stranded. It would take a gorilla to work with otherwise. Well I know of a few electricians whose knuckles drag the ground.
              MSEE, PE

              Comment

              • Naptown
                Solar Fanatic
                • Feb 2011
                • 6880

                #8
                Originally posted by Sunking
                No stranded is just easier to work with and easier to terminate, but requires some expensive tools to terminate correctly. Once you get above 4 or 6 AWG it is all stranded. It would take a gorilla to work with otherwise. Well I know of a few electricians whose knuckles drag the ground.
                Tell me about it. MC4 hand crimper at $600.00
                NABCEP certified Technical Sales Professional

                [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

                [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

                [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

                Comment

                • Sunking
                  Solar Fanatic
                  • Feb 2010
                  • 23301

                  #9
                  Originally posted by Naptown
                  Tell me about it. MC4 hand crimper at $600.00
                  Sounds a little high there Rich. But I agree professional grade tools, especially those that are certified for UL systems are high. Be glad you do no tneed crimpers like these. Well maybe you do from time to tim eif working on battery systems. Here is a 15 ton crimper for 6 AWG up to 1000 MCM. Not shown is the electric pump.

                  MSEE, PE

                  Comment

                  • FloridaSun
                    Solar Fanatic
                    • Dec 2012
                    • 634

                    #10
                    Originally posted by Sunking
                    Sounds a little high there Rich. But I agree professional grade tools, especially those that are certified for UL systems are high. Be glad you do no tneed crimpers like these. Well maybe you do from time to tim eif working on battery systems. Here is a 15 ton crimper for 6 AWG up to 1000 MCM. Not shown is the electric pump.

                    The hydraulic power pack on my tube bender can twist up 2 inch pipe like limp spaghetti but for crimping I use my old english flywheel press. Needs no elect and squishes terminal ends on cable just fine. Course it's not so portable as the crimper in your photo. That cast iron flypress weighs over a quarter ton.

                    Comment

                    • Naptown
                      Solar Fanatic
                      • Feb 2011
                      • 6880

                      #11
                      Originally posted by Sunking
                      Sounds a little high there Rich. But I agree professional grade tools, especially those that are certified for UL systems are high. Be glad you do no tneed crimpers like these. Well maybe you do from time to tim eif working on battery systems. Here is a 15 ton crimper for 6 AWG up to 1000 MCM. Not shown is the electric pump.

                      Have a similar one to that too
                      Greenlee-HK12ID.jpg
                      NABCEP certified Technical Sales Professional

                      [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

                      [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

                      [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

                      Comment

                      • Sunking
                        Solar Fanatic
                        • Feb 2010
                        • 23301

                        #12
                        Originally posted by Naptown
                        Have a similar one to that too
                        [ATTACH=CONFIG]2747[/ATTACH]
                        That looks like the Greenlee version right?
                        MSEE, PE

                        Comment

                        • Naptown
                          Solar Fanatic
                          • Feb 2011
                          • 6880

                          #13
                          Originally posted by Sunking
                          That looks like the Greenlee version right?
                          That is similar to the one we have but not exactly. And yes that is the greenlee one in the picture
                          NABCEP certified Technical Sales Professional

                          [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

                          [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

                          [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

                          Comment

                          • SunEagle
                            Super Moderator
                            • Oct 2012
                            • 15192

                            #14
                            Originally posted by Naptown
                            That is similar to the one we have but not exactly. And yes that is the greenlee one in the picture
                            I picked up a smaller hydraulic unit from Harbor Freight. It only goes to #1/0 wire but it has 7 other smaller wire size chucks. I have to go check but I think it cost me less than $70.

                            Comment

                            • Sunking
                              Solar Fanatic
                              • Feb 2010
                              • 23301

                              #15
                              Originally posted by SunEagle
                              I picked up a smaller hydraulic unit from Harbor Freight. It only goes to #1/0 wire but it has 7 other smaller wire size chucks. I have to go check but I think it cost me less than $70.
                              Do the dies imprint UL codes on the terminals when compressed.
                              MSEE, PE

                              Comment

                              Working...