Originally posted by mjlef
the wire loop to the meter would be 1500 feet long. Running that distance at 240VAC would require twice as
much copper as running panel 360VDC for the same losses, I would NOT call that, no difference. But that is
NOT the only issue. The PoCo loves to run the line at or above the legal maximum voltage. Any drop in the
line fed by inverters adds to that, often enough causing inverter monitors to cause overvoltage shutdown. The
DC line losses do not contribute to the effect, so it is minimized by running as much of the length as possible
with panel DC voltage.
Are string systems more fire prone, where is that reported? What about all those micros each a potential fire,
especially if not individually fused?
MPPT may be a point at any given instant, but the curve running very close to that same efficiency is
somewhat broad. I have measured enough panel operating voltages to see that. The only way to approach
20% loss in a string is with extremely mismatched panels or a fault. I doubt I exceed 2% anywhere.
If shade is a serious problem, go with micros. Here I sometimes lose a string at a time sun is fading, the
overall loss is only a few percent, and micros could only recover a fraction of that. Gaining a tiny bit more
is pointless if more is burned up in the power transmission.
In my case expansion was actually easier with a string system, because no inverters or
consolidated power wire was added. Added strings aligned to peak at different times
of day may share the same inverter(s), which also happens under cloudy skies. Micros
are essentially unable to do this, resulting in much more idle equipment. Bruce Roe