Working on a system to charge bats on a boat used for electric outboard trolling motor. The panels will be mounted at a dock, with the bats on the boat. --- My questions are: Where should I mount the control system or box? Boils down to, is it OK to have the panels wired to the control box and unplug the output leading to the batteries on the boat? Would it be better to unplug the the panels to the control box, which would be mounted on and wired to the bats on the boat? ---- In general, is it OK to short the outputs of a panel, will it hurt the panels? Is it OK to leave the panels with no connection, or the outputs with no load? These are smaller panels, around one amp per panel, made for a 12 volt system. Thinking about six in parallel. TNX
Try our solar cost and savings calculator
Solar panel damaging ??
Collapse
X
-
-
Put the charger with the batteries, and disconnect the solar from the chargers. This allows the charger to be properly loaded.
If the battery is disconnected the charger has no way to regulate the voltage from the solar panels and can be damaged.Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister
Copyright © 2014 SolarReviews All rights reserved.
Powered by vBulletin® Version 6.1.3
Copyright © 2025 MH Sub I, LLC dba vBulletin. All rights reserved.
Copyright © 2025 MH Sub I, LLC dba vBulletin. All rights reserved.
All times are GMT-5. This page was generated at 06:44 AM.
Comment