    Metallic conduit for DC

    Another electrician friend of mine pointed out a change in the 2020 NEC that I was not aware of. Article 690.31(D) now has an exception that appears to allow PVC conduit for the DC conductors between the roof penetration and the Rapid Shutdown device (inverter in a SE system). What is your interpretation of this new rule?


    "Exception: PV hazard control systems installed in accordance with 690.12(B)(2)(1) shall be permitted to be provided with or listed use with nonmetallic enclosure(s), nonmetallic raceway(s), and cables other than Type MC metal-clad cable(s), at the point of penetration of the surface of the building to the PV hazard control actuator."
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    I interpret that as allowing the hazard control conductors to be in PVC, is says nothing about the DC power lines
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • MichaelK!
      Solar Fanatic
      • Jul 2015
      • 117

      #3
      Does "hazard control conductors" mean the ground wire?

      Comment

      • Mike90250
        Moderator
        • May 2009
        • 16020

        #4
        Possibly. However, I read it as the control signals that command the DC be cut off. An important signal like that - you would want protected.
        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||