Aquion Energy batteries
Collapse
X
-
No guessing about it. Got the link and I will tell you. Ri does not change from charge to discharge.Leave a comment:
-
At first guess, I would say that the internal resistance should be pretty symmetric between charge and discharge (not all chemistries do this, of course. Non-rechargeable batteries in particular).
That means that you can just take the difference in voltage between the zero current line and the current you are interested in and add that difference to the zero current line instead of subtracting.
In the case of flooded lead acid cells, this method is reasonably accurate as long as the terminal voltage does not go above the gassing voltage. At that point another parallel current path becomes available which is not present during discharge.
It would also be interesting to see how the charge acceptance tapers off as the stack approaches full charge, and to see what the recommended "absorb" voltage is.Leave a comment:
-
).
That means that you can just take the difference in voltage between the zero current line and the current you are interested in and add that difference to the zero current line instead of subtracting.
In the case of flooded lead acid cells, this method is reasonably accurate as long as the terminal voltage does not go above the gassing voltage. At that point another parallel current path becomes available which is not present during discharge.Leave a comment:
-
Leave a comment:
-
Leave a comment:
-
Leave a comment:
-
I'll see if I can get the official specs from them. Stand by.Leave a comment:
-
Leave a comment:
-
Their specs have been a moving target. If you find the internal resistance published, please let us know. There was an Aquion person lurking here - maybe they would be kind enough to post it.Leave a comment:
-
However, if all the specs they post hold true, especially considering cycle life and predicted cost reductions, then they may just be the best option. That is yet to be seen.
The best option is the one that costs less in the long run! At the same time the AHI batteries are environmentally friendly and require no maintenance.Leave a comment:
-
Back to Aquion - from the start they never intended these batteries to be EV or even general purpose replacements. The major market seems to be grid-stabilization, and perhaps we are shoe-horning it into our application.
I think it is pretty neat - but like LFP, you've got to really understand and want those battery characteristics to fit your application.
I find the flat charge curve of LFP very attractive, but others don't. There isn't a lot to think about, other than staying away from the two ends. I need the fast charge time for my location. I like the low weight. The cost, as long as it isn't way out of whack, isn't so much a criteria for me. I agree totally with your statement of "understanding and wanting particular battery characteristics," and it applies across the board for all chemistries, from what I have seen so far. Of course, there is another route of just going out and buying large batteries at WalMart, if you like to fly by the seat of your pants.Leave a comment:
-
Unless the battery bank is so massive that you are only ever using 1/40 of its capacity per cycle, I do not see the point.
On the other hand, if you do not care much about cyclic energy efficiency, you could choose to pull higher current from the battery bank and accept as much as a 50% voltage drop provided you care most about short term stabilization and have output conversion equipment that can tolerate a wide range of input voltages.
That is, if you are willing to accept a voltage sag of 40% instead of 2%, you would be able to use a C/2 discharge rate. That is probably good enough for a voltage stabilization application. For the charging process you could limit it to C/12 or even C/20 and have a useful recharge in the stabilization application.
For comparison, I have seen statements that pumped water storage has a cyclic efficiency of 50% or lower, so there may be a place for a storage system that can be deployed anywhere, with the option of a relatively small and inexpensive system size.
Maybe.....Last edited by inetdog; 01-15-2015, 04:05 AM.Leave a comment:
-
Back to Aquion - from the start they never intended these batteries to be EV or even general purpose replacements. The major market seems to be grid-stabilization, and perhaps we are shoe-horning it into our application.
I think it is pretty neat - but like LFP, you've got to really understand and want those battery characteristics to fit your application.Leave a comment:
-
OK Amy here is my issue. Internal Resistance is way too high. Using the product sheet for the M100-L082 which is a 48 volt 540 AH battery we can determine Ri from the Voltage vs Capacity curve of 75 milli-ohms. I know to most folks that means nothing to them, but that is significant. For low voltage systems one of the design goals is to limit voltage sag at the battery post to 2% of less. Using a nominal voltage 48 volts and 540 AH capacity means you can only draw .96 volts / .075 ohms = 12.8 amps. On a 540 AH battery that is a miserable C/40 discharge. That is unusable. Basically means you got this huge battery that can only supply a 650 watt load.
Now take something like a Rolls 4CS17PS a 4 volt 540 AH battery. It has a Ri of 1.03 milliohms. It would take 12 of them in series to equal 48 volts giving you a total of lets just say 13 millohms. Using the same 2% design goal you can draw .96 volts / .013 ohms = 74 amps or roughly C/7 discharge current. Using the Rolls equivalent you can supply a 3500 watt load.
Now here is where it really gets ugly. If you can only discharge at a maximum of C/40 means you can only charge at a max of C/40. Again most folks are clueless what that means. But in essence makes it completely unusable because there is not enough Sun Hours in a day to recharge. Bare minimum winter sun hours for a FLA is 3 Sun hours before you exceed a C/8 charge current. For these batteries bare minimum is 16 sun hours. No place on the face of the planet gets 16 Sun Hours. In the lower 48 states Tuscon has the best in summer at 7 Sun Hours.
Sorry I do not see any application these batteries can be used for other than extremely low power application for telemetry in extremely remote locations where is cost is not a factor. Good grief if ever fully discharged would take two full days of commercial power to recharge. On solar more than a week on the equator, 2 or 3 weeks anywhere else. Heck even FLA batteries are a challenge with their relatively high Ri, but these are outrageous now that I see the real data. No wonder they hide it.Attached FilesLeave a comment: