What is min. PV Power ( Watts) that is needed fire up a Xantrex GT 3.0 ??

Collapse
X
 
  • Time
  • Show
Clear All
new posts

  • Mike90250
    replied
    I had a GT3.8 and it would producing power at about 50 watts, but you have to meet it's input voltage spec.

    Leave a comment:


  • Sunking
    replied
    Wrong question. You must meet minimum/maximum voltage requirement, and stay under maximum power input.

    Leave a comment:


  • Robert1234
    replied
    I think SunEagle is pointing you in the correct direction. I had a GT5 at the last house. It would wake up and run just fine while producing just a few hundred watts on a cloudy / rainy day. What voltage are your panels? and how do you have them wired?

    Leave a comment:


  • SunEagle
    replied
    Originally posted by Sparkskard
    Have Xantrex GT3.0 with about 1Kw of VP Panel ( later I well add more) well it work ( start ) with lower Power of PV Panels.. I know SMA and Sharp JH-3500 handle the low power just fine, some times only put out about 300 W,,~~the Xantrex come out with error msg "Insufficient Solar Energy"..~~ I don't know if it a faulty inv. or just not designed to start with low of a power input ???,,,~~ Yes, I know it may be size wrong but I got the inv. at good price and don't have $$$ to get more panels ~~~~ any one have any used ,, rebuild-able Panels ???

    Looking for sparks in all the wrong places ~~~~
    I downloaded the O&M manual and did not see an error msg "Insufficient Solar Energy" but there is a Sleep State called "Insufficient PV Voltage" which keeps the inverter in sleep mode.

    I did see a "Bus Under Voltage" fault code which is looking at the DC voltage level from the panels.

    I also saw that the default setting for the Wakeup Voltage was 300VDC but can be lowered to 180VDC.

    Maybe check what yours is set for.

    Leave a comment:


  • What is min. PV Power ( Watts) that is needed fire up a Xantrex GT 3.0 ??

    Have Xantrex GT3.0 with about 1Kw of VP Panel ( later I well add more) well it work ( start ) with lower Power of PV Panels.. I know SMA and Sharp JH-3500 handle the low power just fine, some times only put out about 300 W,,~~the Xantrex come out with error msg "Insufficient Solar Energy"..~~ I don't know if it a faulty inv. or just not designed to start with low of a power input ???,,,~~ Yes, I know it may be size wrong but I got the inv. at good price and don't have $$$ to get more panels ~~~~ any one have any used ,, rebuild-able Panels ???

    Looking for sparks in all the wrong places ~~~~