[QUOTE=windbag;46510]Got into the control box with a torch this time, and can see the connector labels.
All the sensors have a zero and +5V supply (blue & red respectively), with the sensing voltage returning on the green wire.
The +5V supply is fine, reading 5.1V on my DVM.
The working tank sensor is mounted/sealed into a 6mm (
Try our solar cost and savings calculator
Help sought: Panel temp sensor dead in 13-year old flat panel water heater system.
Collapse
X
-
More detailed info
Got into the control box with a torch this time, and can see the connector labels.
All the sensors have a zero and +5V supply (blue & red respectively), with the sensing voltage returning on the green wire.
The +5V supply is fine, reading 5.1V on my DVM.
The working tank sensor is mounted/sealed into a 6mm (Leave a comment:
-
Right, just like with a car, when the ash tray fills up, you find you can't buy a new, empty one, and you have to buy a new car
I love all the non-documented stuff, 3 wire, 2 wire, parts not made anymore - buy a new $500 box because a $4 sensor is not made anymore.Leave a comment:
-
Leave a comment:
-
Most likely it is a PT1000 thermister. I has been the standard through europe for years. Look up Resol UK for a dealer near you.
To be sure, take off one of the good thermisters and measure it at around 25C, then at a colder or hotter temp to see if it goes up or down. That will give you more info.
I did try a basic resistance measurement in situ with no power, and got nothing but an open circuit reading for any combination of probes on the three terminals on any of the three sensors.
I will be trying again when I know which sensor is which & properly disconnected from the controller in an hour or two; will report back.Leave a comment:
-
Leave a comment:
-
Disconnect power! Then
Switch the lower tank thermister wires to the panel connections in the controller. Reconnect power. The temp readout for the panel now should be the same as the lower tank read before you disconnected the wires if the controller is good.Attached FilesLeave a comment:
-
Most likely it is a PT1000 thermister. I has been the standard through europe for years. Look up Resol UK for a dealer near you.
To be sure, take off one of the good thermisters and measure it at around 25C, then at a colder or hotter temp to see if it goes up or down. That will give you more info.Leave a comment:
-
Bummer. Looks like time to buy a new differential controller.Leave a comment:
-
Help sought: Panel temp sensor dead in 13-year old flat panel water heater system.
Hi folks
I have a system semi-professionally installed in July 1999 (13 years ago), which has been running fine until now.
Today, our first proper sunshine day here in the UK since last summer, I found steam issuing from the pressure relief valve.
Looking at the temperature sensor display unit, the problem is the temperature sensor in the panel, which is registering -14C (!)
The lower tank temperature is registering fine.
I'm competent electrically, so I delved into the control box, which is a Suntech "Sunhound 1" unit. It has mains power OK.
The panel sensor is connected via UK phone wire using two cores doubled up for each of the three connections made.
These mirror the two hot water tank sensors in having three connections, each with a green, red & blue colour-coded wires.
What type of sensor are these likely to be?
Can I start diagnosing the fault from the control box end - i.e. tell the difference between a dead sensor or a disconnected cable, for example?
If folk know of a troubleshooting guide to point me at, great, or detailed advice on how to check would also be welcome.
Thanks
PS I manually cooled down the panel by connecting the system pump directly to the mains rather than via the control box relay.
It is basically working OK, just not getting the right logic signal to the mains relay in the control box when the panel is hotter than the tank water.
PPS I say "semi-professionally installed" as it was by a start-up company that no longer exists. They provided scant details of the units I actually received.
The Suntech company who have their name on the "Sunhound 1" unit are nothing to do with the American, Indian or Hong Kong/Chinese companies who currently use the name.
Googling Suntech "Sunhound 1" yields nothing useful!
Copyright © 2014 SolarReviews All rights reserved.
Powered by vBulletin® Version 6.1.0
Copyright © 2025 MH Sub I, LLC dba vBulletin. All rights reserved.
Copyright © 2025 MH Sub I, LLC dba vBulletin. All rights reserved.
All times are GMT-5. This page was generated at 11:03 AM.
Leave a comment: