disabling frost protection

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • steff503
    Junior Member
    • Aug 2013
    • 29

    #1

    disabling frost protection

    Have a First Solar water heater 40 gallon. We have work station SP106. And SP24 controller http://www.solar-water-heater-pro.co...fsp-sp106.aspx

    It has a frost protection feature which circulates through the panels when the outside temp(T1) hits 2C. I can only change it between 2 and 8C.

    We have Glycol in the panels so it will not freeze.
    As a result it is circulating antifreeze from the coil through the array and cooling down the water in the tank.

    Can I disable this feature or any other ideas.
    We have the manual but it does not help.
    Steff
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    If it has a motor, it has wires to the motor. add a switch, but if you frost your collectors, I didn't do it.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • inetdog
      Super Moderator
      • May 2012
      • 9909

      #3
      Originally posted by Mike90250
      If it has a motor, it has wires to the motor. add a switch, but if you frost your collectors, I didn't do it.
      If he needs this to be automatic, he would have to add one or more temperature sensors with a controller to operate a relay to cut off the motor just when the panels are cold.
      If he puts in just a switch, he then risks cooking his panels if he forgets to turn it back on.
      SunnyBoy 3000 US, 18 BP Solar 175B panels.

      Comment

      • Naptown
        Solar Fanatic
        • Feb 2011
        • 6880

        #4
        How about a remote bulb cooling thermostat it switches off at just above the set point on the controller and turns on when above
        Honeywell among others make many of these for refrigeration applications
        NABCEP certified Technical Sales Professional

        [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

        [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

        [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

        Comment

        • steff503
          Junior Member
          • Aug 2013
          • 29

          #5
          Am I roght in thinking that 8C is way too warm to freeze anything.

          I feel like if there is a changeable set point it should go much lower than 35F

          Yes I could put a switch but after spending hundreds on this unit I would like for it to work. Don't mind a little tweek but to start re wiring will be a last resort.

          Comment

          • LucMan
            Solar Fanatic
            • Jul 2010
            • 628

            #6
            Originally posted by steff503
            Am I roght in thinking that 8C is way too warm to freeze anything.

            I feel like if there is a changeable set point it should go much lower than 35F

            Yes I could put a switch but after spending hundreds on this unit I would like for it to work. Don't mind a little tweek but to start re wiring will be a last resort.

            Contact your installer and ask him if it can be turned off in the controller, most can.

            Comment

            • steff503
              Junior Member
              • Aug 2013
              • 29

              #7
              We are the installer.

              Comment

              • J.P.M.
                Solar Fanatic
                • Aug 2013
                • 15030

                #8
                Originally posted by steff503
                We are the installer.
                I'd get a different controller that allows the freeze protection to be turned off. Or, as a poor 2d choice, because it's closed loop glycol (w/ absolutely NO danger of freezing), depending on climate, put it on a timer and turn the controller off at night. Most collectors will stay (stagnate) 15-30 deg. F above ambient most of the day in cloudy weather if irradiance is not enough to actuate the pump. This may be high enough to keep the collector sensor above the freeze trip temp.