At this power level of use stay at 12vNABCEP certified Technical Sales Professional
[URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]
[URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)
[URL="http://www.gaisma.com"]www.gaisma.com[/URL]Comment
-
Comment
-
Comment
-
Comment
-
Thanks for all the help guys.
I went to get the battery cable for 50 amps battery and was impressed with the thickness of the cable. Does it really have to be that thick? I was told by the sales person to get a #6 cable.Comment
-
Great minds think alike.
That should be a nice adequate set-up for you.
However, I don't see fuses on your list.
I did a few 10W units with this Lamp... worked well.
10w_washlight03.jpg[CENTER]SunLight @ Night[/CENTER]Comment
-
You don't need #6... because you don't need 50amp cable.
Lamp: 10Watt / 12Volt = .833 amp current .... #18 or #16 (gauge) wire would be sufficient.[CENTER]SunLight @ Night[/CENTER]Comment
-
If you were driving a large inverter and trying to get all of the power from the battery in a short period of time or needed to run a long distance without much of a voltage drop, then #6 would make sense. But you need to size it for your actual DC load since you will not be using an inverter.
Once you have the minimum size wire needed to safely carry the current, you then look at the voltage drop for that wire, that current, and the distance from battery to load and try to keep the voltage drop at 3% or less.
The other consideration is how much current the charging circuit will be delivering at peak. Often (when you discharge over 10 hours and recharge over 3 or 4, for example) the charger connection will require larger wire than the load side.SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
-