I really hope the RGMTR isn't old and obsolete, it was installed in April. -
↵jandrese , solaredge must have obsoleted the SE-RGMTR-3Y-277V-A because there isn't any documentation on their website at all. Not even in the support section. You didn't say how your system is wired up. Are you split phase, three phase?
scottbenson is suggesting that the installation of the revenue grade meter be verified. This means CT location/wiring/direction, power tap matches CT (CT1 to L1, etc), verify all extension wire splicing/wire colors/insulation/no shorts, verify cable shielding for extension wires if run in AC conduit, verify grounding, verify RS-485 communication wiring/termination settings/inverter settings. You could start by getting pictures of CT's.
I suspect your installer will have to verify the installation.
In the meantime, you can collect better data.
Over the past month I count:
15 days where the consumption traced the production closely as per the second graph.
7 days where the consumption traced production for only part of the day (almost always in the morning), but some production was shown. An example of such a day is shown above.
9 days where production seemed mostly normal.
I was not monitoring every appliance in my house constantly for the month, but the usage patterns are pretty regular so it's not hard to spot when the consumption figure is anomalously high.
I do have one theory. In my neighborhood there are three other homes with solar panels. I'm guessing the substation can't feed back on the main grid, so if there is no other demand in the neighborhood the lines become fully saturated and the power has nowhere to go on mild days with lots of sun.Leave a comment:
-
Hello Jandrese, I am a owner of a Solar Installation company in Costa Rica. We have installed hundreds of SE systems and was the first company to install the meters back in 2013 or so in the Northern Hemisphere.
First things first, confirm the CTS are placed correctly that is about 90% of the problems. With the new inverters it is getting simpler and simpler with more automation. The CTs of course measure the import and export the inverter shows the production. All the rest is calculated in the portal such as self consumption. You can see by this photo, this system is zero export. Using the battery and solar they are 88% self consumption. We will be getting that closer to the 99% by using soft starters on his well pump.
Screen shot ph.jpgLeave a comment:
-
I do have one theory. In my neighborhood there are three other homes with solar panels. I'm guessing the substation can't feed back on the main grid, so if there is no other demand in the neighborhood the lines become fully saturated and the power has nowhere to go on mild days with lots of sun.Leave a comment:
-
solar_self_consumption_partial.png
The Inverter is a SE11400H-US000BNU4
The Consumption Meter is a SE-RGMTR-3Y-277V-A
Over the past month I count:
15 days where the consumption traced the production closely as per the second graph.
7 days where the consumption traced production for only part of the day (almost always in the morning), but some production was shown. An example of such a day is shown above.
9 days where production seemed mostly normal.
I was not monitoring every appliance in my house constantly for the month, but the usage patterns are pretty regular so it's not hard to spot when the consumption figure is anomalously high.Last edited by jandrese; 05-27-2021, 07:41 PM.Leave a comment:
-
Another happy SolarEdge user.Leave a comment:
-
What model inverter and consumption meter do you have?
What do you mean by it works for a few days? How many days working out vs not working?Leave a comment:
-
Power company not accepting production power
I have a grid tie system using a SolarEdge Inverter and consumption meter. With the consumption meter I'm seeing values that don't make sense on most days. Even though my usage should be very low with a few spikes here and there (hot water, dish washer, etc...) what I see instead is the "self consumption" figure tracking closely my production and relatively little power being put on the grid. My assumption is that the consumption meter simply subtracts the "production" figure from the inverter by the total current going over the main line out to the grid. If the power company isn't accepting the power then it shows as consumption even though it's not actually being produced. This is a concern because we balanced our system on the assumption of building up kWh credits during the spring and fall to pay off during the summer and winter. If we can't build up credits it changes the payoff horizon considerably.
Is this expected? My contractors seems to be baffled by this, and nobody I've talked to claims to have seen it before. Some people have suggested it is due to improperly installed equipment, especially the consumption meter, but it seems to track what I got on my power bill, plus it does work as expected on a few days.
This is what I expect to see: solar_self_consumption_working.png
Instead I get this: solar_self_consumption.png
Note how the "self consumption" follows the production curve almost exactly, including the dip around 10 when a lonely cloud passed overhead. The little hitch around 8:15 is also shown on both graphs.
I'm really not sure how to verify this. Is there a particular question I can ask my solar installer or power company to verify what is happening? My power company is Dominion Virginia Power.Last edited by jandrese; 05-26-2021, 08:07 PM.