    GT grounding question

    Any help with grounding questions shown in pictures appreciated. I have an inspection on 11/27/20 and need to pass.
    IMG_4769.jpgIMG_4766.jpgIMG_4767.jpgIMG_4765.jpgIMG_4768.jpg
  • solarix
    Super Moderator
    • Apr 2015
    • 1415

    #2
    All metal wireways need to be bonded to ground. The conduit does not have to be bonded to the boxes (the old way of bonding), your inspector is going to want grounded bushings on each conduit. Our inspector requires a bond bushing on each end of the DC conduit.

    AC and DC wires can run together (they both have 600V insulation) alhough some inspectors won't allow it.

    You can run the grounding wire either inside or outside the conduit. If outside it needs to be more durable (6awg minimum). If inside on a long conduit run, it is supposed to be bonded at both ends as the conduit acts as a choke to current spikes.

    Ask your inspector what they want on the ground rod question. Opinions vary...

    How come you are installing an ~8 year old inverter? That looks like a second generation SunnyBoy....

    Do the next guy a favor and label your DC wiring please...
    BSEE, R11, NABCEP, Chevy BoltEV, >3000kW installed

    Comment

    • khanh dam
      Solar Fanatic
      • Aug 2019
      • 391

      #3
      THANKS FOR THE ANSWERS. I will have to see if my local electrical supply company has the grounded bushings in stock early monday morning to be compliant with nec 250.97

      . Also need to get proper green colored ground screws NEC says self tapping metal screws I used are not allowed.nec 250.8

      I read that NEC requires the negative PV wires to be taped white to meet code nec 200.6 so will label them more clearly when I do that.

      Still have not figgured out if I need to have a DC ground for each inverter? The sunny boy DC disconnect box has a specific grounding area for that. Any thoughts on that?
      I got several of the new Sunnyboys still in box from a company going out of business several years ago. I think for around $400 each. Only downside is by the time you buy the DC disconnect and monitoring boards that adds about $300 to each inverter. Still cheaper than buying a " current inverter" I've read the old sunny boys are easier to fix as well, so that might be a plus going forward. sunny disconnect.jpg
      Attached Files

      Comment

      • Mike90250
        Moderator
        • May 2009
        • 16020

        #4
        New GT systems may need to meet current NEC requirements, not what was in effect when inverters were built. Maybe all the inverters need is a firmware update. Maybe the inspector won't notice.....
        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

        solar: http://tinyurl.com/LMR-Solar
        gen: http://tinyurl.com/LMR-Lister

        Comment

        • khanh dam
          Solar Fanatic
          • Aug 2019
          • 391

          #5
          2008 sunny boy's meet current NEC standards for anti islanding, GFPD, grounding, etc. you are assuming something that is not an issue.

          Comment

          • Mike90250
            Moderator
            • May 2009
            • 16020

            #6
            Originally posted by khanh dam
            2008 sunny boy's meet current NEC standards for anti islanding, GFPD, grounding, etc. you are assuming something that is not an issue.
            There's the Rule 21, which some areas (Calif & Hawaii) which mandates smart inverters. ( 2017 ) So it's not NEC but different states utilities are imposing this requirement, Look up the requirement for your location/utility. City may let you install gear, but you will be unhappy if the Power Company says you cant connect it to their grid.

            California’s Rule 21 is leading the way for inverters to help support the grid Imagine the nation’s grid. Visualize more solar projects plugging in every

            excerpt :
            Under the UL 1741 safety standard established in 2010, the old interconnection requirements only allowed inverters to operate within a narrow range of IEEE frequency and voltage requirements. “Because of all this, the capability of inverters wasn’t fully utilized,” John Drummond, applications engineer at Chint Power Systems, explained during a recent Solar Power World webinar. “But the revised rule is leading the way to expand that.”

            The revised rule widens the range of conditions during which inverters may operate. The new rule and the addendum to the previous UL safety standard, UL 1741-SA, allow inverters to provide seven grid support functions:
            -Voltage ride-through
            -Frequency ride-through
            -Soft-start reconnection
            -Ramp-rate controls
            -Fixed power factor
            -Dynamic Volt-VAR management
            -Changes to anti-islanding requirements
            Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
            || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
            || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

            solar: http://tinyurl.com/LMR-Solar
            gen: http://tinyurl.com/LMR-Lister

            Comment

            • khanh dam
              Solar Fanatic
              • Aug 2019
              • 391

              #7
              Luckily Duke Energy does not require rule 21 compliant inverters in my area. And since this install is not on a habitable structure, I dont' need rapid shut down.

              Comment

              • bob-n
                Solar Fanatic
                • Aug 2019
                • 569

                #8
                As you route the wire to the ground rod, consider the high current flowing in that wire when your roof gets a near hit or direct hit from lightning. If possible, you want that energy routed to earth without connecting to any other devices along the way. Best case is something like this:
                ground.png
                Attached Files
                7kW Roof PV, APsystems QS1 micros, Nissan Leaf EV

                Comment