I've been searching out this question but haven't had any luck so my question is are rapid shutdown boxes required on ground mounts or is this just when mounting PV panels on a roof? Also if required can you just put one rapid shutdown box on each string of panels or must they be on all the individual panels?
Most Popular Topics
Collapse
Are rapid shutdown boxes required on ground mount installations?
Collapse
X
-
Are rapid shutdown boxes required on ground mount installations?
Last edited by D0T-C0M; 11-05-2020, 08:56 PM. -
I've been searching out this question but haven't had any luck so my question is are rapid shutdown boxes required on ground mounts or is this just when mounting PV panels on a roof? Also if required can you just put one rapid shutdown box on each string of panels or must they be on all the individual panels?
Andy -
Check with your ahj. I just went through this and mine required rapid shutdown on all residential installs. I just put in a ground mount and I had to include rapid shutdown.Comment
-
I hate it when AHJ thinks they are improving things. Sure you can "justify" almost anything, like bubble wrapping your kids to go to school. But it's not always better or rightPowerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
That sucks. May I ask which state and county you are in? Maybe others living in the same area need to check with their county ordinances before installing solar.Comment
-
Ingham county. Michigan. Twp inspector through. Fortunately I was able to add rapid shutdown modules pretty easily and it does make maintenance easier/safer.
Breaks my secure power supply that the sunny boy inverters give
Comment
-
Comment
-
690.12(B)(2) Inside the Array Boundary. The PV system shall comply with one of the following:
(3) PV arrays with no exposed wiring methods, no exposed conductive parts, and installed more than 2.5 m (8 ft) from exposed grounded conductive parts or ground shall not be required to comply with 690.12(B)(2).
I think the above means ground arrays need to be 8 feet or more up in the air.???Last edited by khanh dam; 11-13-2020, 10:48 AM.Comment
-
My interpretation is that rapid shutdown only applies to arrays or DC circuits that are installed on buildings so the entire rapid shutdown shouldn't apply. The purpose is for emergency responders to be able to safely create a a safe entry/exit point without having to worry about live wires.
I suppose one could consider the ground mount framework to be a building. Seems a stretch to me but up the inspector!Comment