    Adding panels to an older existing system

    We have an existing 4.2 Kw grid tied system with an approx 10 yr old Sunny Boy inverter. I think the existing panels are Sharps but I'm not 100% sure.

    I'm doing a bunch of landscaping in the backyard and will be building a 12x12 pergola. It occurred to me that this would be a good opportunity to add some 2-3 Kw of new solar panels to our system. However I'm reading that it's probably not feasible to do so with an older inverter.

    I'd like to know if this is really possible. I'd prefer not having two separate systems if possible.

    Can I:
    1) Add 300 watt plus panels using microinverters. Is this possible and how would it be added to the existing system?
    2) Purchase a new central inverter and then add new panels to the system. However the new panels would not match the old panel outputs exactly. Is this an issue that can be overcome?
    3) Some other option.

    Here are some photos of the tag from my existing inverter:
    Disconnect.jpg
    Sunny Boy tag.jpg
  • foo1bar
    Solar Fanatic
    • Aug 2014
    • 1833

    #2
    With 4.2kw DC and 3.8kW inverter, there's probably not a lot of room to expand that with just more DC power.

    Adding a new inverter side by side with it is almost certainly possible...
    But may or may not be economically wise..

    Questions that I think you have to look at:
    Will increasing this put me into a different rate bracket than what I'm grandfathered into now?
    Can I add more power coming in to the main panel without a main panel upgrade or having to do a line side tap? (or how much will those cost)
    Will I use that additional power or am I basically gifting the power company the extra kwh's?

    Comment

    • TheLex
      Junior Member
      • Jan 2014
      • 17

      #3
      My true up at the end of the year is usually about $1300-1400. So I would get a return on my money within 2-3 yrs.

      What if I were to just upgrade the string inverter with a 7+ Kw version instead? Do I still have to match the output of the new panels with that of the new panels?

      Can I use microinverters on the new panels and combine that with the string inverter system?

      I need to investigate the panel situation. We have a 400 amp main panel and the solar system current runs to a 200 amp subpanel that's already used up all the breaker positions.

      Originally posted by foo1bar
      With 4.2kw DC and 3.8kW inverter, there's probably not a lot of room to expand that with just more DC power.

      Adding a new inverter side by side with it is almost certainly possible...
      But may or may not be economically wise..

      Questions that I think you have to look at:
      Will increasing this put me into a different rate bracket than what I'm grandfathered into now?
      Can I add more power coming in to the main panel without a main panel upgrade or having to do a line side tap? (or how much will those cost)
      Will I use that additional power or am I basically gifting the power company the extra kwh's?

      Comment

      • Mike90250
        Moderator
        • May 2009
        • 16020

        #4
        If you swap inverters, you may have to negotiate a new agreement with the power company and new building permits.

        Many newer inverters have several MPPT inputs, the existing array can use one, the new array (would not need to match) can use a different one.

        You do need to insure the arrays are within the MPPT ratings of the inverter
        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

        solar: http://tinyurl.com/LMR-Solar
        gen: http://tinyurl.com/LMR-Lister

        Comment

        • SunEagle
          Super Moderator
          • Oct 2012
          • 15123

          #5
          Originally posted by TheLex
          My true up at the end of the year is usually about $1300-1400. So I would get a return on my money within 2-3 yrs.

          What if I were to just upgrade the string inverter with a 7+ Kw version instead? Do I still have to match the output of the new panels with that of the new panels?

          Can I use microinverters on the new panels and combine that with the string inverter system?

          I need to investigate the panel situation. We have a 400 amp main panel and the solar system current runs to a 200 amp subpanel that's already used up all the breaker positions.


          I have never heard of a system that had both micro and string inverters. But then again if you have separate AC connections at the main panel it might be doable. The biggest hurdle is for you to get permission from your POCO and AHJ concerning the additional generating system. One area that may be a show stopper is the size of your Main Panel bus rating. That will limit the total AC connection from solar.

          Comment

          • scrambler
            Solar Fanatic
            • Mar 2019
            • 500

            #6
            I don't see any issue mixing a regular string inverter with Micro.
            What is important is to make sure you comply with the 120% rule in the Breaker panel where they will be connected.

            If both the string inverter and the Micro inverters breaker are going to be in the same panel, the sum of their breakers should meet the 120% rule and they should be at the end of the busbar.

            Let us say the 120% rule says you can have 50A of solar in your panel, and your string inverter already has a 30A breaker, you could have a 20A breaker connected to microinverters.

            Comment

            • TheLex
              Junior Member
              • Jan 2014
              • 17

              #7
              If the sub panel to which the existing solar is hooked up to is already maxed out, is it permissible to add an independent breaker say on the outside of the house before the new system merges with the old one? Or does the whole sub panel need to be replaced with a larger capacity unit?

              Originally posted by scrambler
              I don't see any issue mixing a regular string inverter with Micro.
              What is important is to make sure you comply with the 120% rule in the Breaker panel where they will be connected.

              If both the string inverter and the Micro inverters breaker are going to be in the same panel, the sum of their breakers should meet the 120% rule and they should be at the end of the busbar.

              Let us say the 120% rule says you can have 50A of solar in your panel, and your string inverter already has a 30A breaker, you could have a 20A breaker connected to microinverters.

              Comment

              • Mike90250
                Moderator
                • May 2009
                • 16020

                #8
                The one advantage of being off grid - I don't have to worry about this.
                Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                solar: http://tinyurl.com/LMR-Solar
                gen: http://tinyurl.com/LMR-Lister

                Comment

                • scrambler
                  Solar Fanatic
                  • Mar 2019
                  • 500

                  #9
                  Here is some reading for you.
                  https://www.altestore.com/blog/2018/.../#.XyxNIa-Sl7c
                  Next would be to make a small schematic of your existing Panels(s) from meter to house panel(s) with their busbar rating and the feeding breaker size.