    Originally posted by foo1bar

    My guess is string inverters are likely to be a few percent worse in many partial shading situations.
    Under the vast majority of conditions it's likely <1% or possibly even an edge to the string inverter (~no difference). If one cell group is shaded it's the same. If two cell groups are shaded then the benefit could go to the string inverter if 1 of 3 cell groups is unable to maintain the 22v the micro inverter requires. Only when shade falls across all 3 cell groups of the panel does a micro inverter have an edge but at that point it's blood from a stone.

    This is what really irks me about Enphase. In some of their promotional material they insinuate that shading part of one panel will reduce the output of the entire array. If each string is on an independent MPPT which should be true for ~all residential string inverters installed after ~2017 then shading part of a panel will have no effect on the unshaded portion of the array because of the bypass diodes.

    Comment

    • TucsonMCM
      Junior Member
      • Jul 2020
      • 14

      #17
      Hey folks, sorry to disappear on you for a month. Had some urgent distractions.

      I've looked further into the TEP Application process, and after a couple weeks wait I finally got my login credentials etc for their project management webpages. Their system is heavily centered on professional installers, which requires some inobvious "selections" to get a DIY install moving.

      I've confirmed that the export rate $ amount is locked in based on *intitial* application date, and not any subsequent approval dates or other milestones. So all I need to do in the next week or so is get the application submitted. The amount of information I need to submit an application is relatively modest, and changes are permitted (like brand/model of panels) if they don't have a significant impact on scale of system.

      One parameter for the application is a selection of interconnect method, and I could use some tutoring/guidance on this selection.

      The choices in the application system are:
      1) Standard backfed breaker
      2) Solar ready panel with standard backfed breaker
      3) Main disconnect derate with standard backfed breaker
      4) Line side tap - requires TEP performed power kill
      5) Other

      I perceive that my likely selection is either #1 or #3. Although #4 is possible, I perceive it would add cost/hassle and isn't necessary since my PV output is modest relative to my panel/bus. As noted earlier in the thread, I believe I have a 200A service connection and a 200A bus in my panel, with a 100A interior subpanel and a 40A exterior breaker for a/c, so total load currently at 140A. I've attached some photos of my panel for others to review to confirm or correct my interpretation. The primary supply lines are coming from overheard lines in an alley to a conduit/header at the edge of my roof, which runs thru my eave directly into the panel.

      It would be great if folks could clarify the differences between #1 and #3, and also comment on #4 if I'm missing some benefit there. I may want to add another interior subpanel for a future garage/shop circuit, which could increase my load by 20A-40A, so comments also appreciated on the interplay of that and any derating or bus capacity versus PV and load.

      Are backfed breakers always housed in their own box/panel as I've seen in some photos online? Or can the by installed in the main panel similar to my A/C and interior subpanel breakers?
      ElecPanelLabel4mp.jpg

      ElecPanel4mp.jpg

      Comment

      • TucsonMCM
        Junior Member
        • Jul 2020
        • 14

        #18
        Originally posted by foo1bar

        Really - a lot of possible options you have for the backfeed - but I'm making a LOT of guesses about what you have and my guesses are probably wrong.
        Your guesses in your post were largely correct. See my photos above fyi.

        Given my current configuration (200A buss, 200A main breaker, 140A load, and 4kw-ish PV array) it seems that the 120% rule combined with my 60A of unused load capacity translates to a simple backfed breaker as the optimal interconnect, with a huge margin of extra amps for future changes. Unless I'm missing something, I could potentially double the size of my intended PV array to ~8kw (= ~ 50A PV breaker) AND add an additional 40A load circuit to my panel, and still meet the 120% rule. So I'm concluding that there is no need for me to entertain the cost/complexity of a line tap or a change of my main breaker.

        Comment

        • solarix
          Super Moderator
          • Apr 2015
          • 1415

          #19
          The way my local inspector interprets the code, you can't use "unused load capacity" in your backfeed calcs....
          BSEE, R11, NABCEP, Chevy BoltEV, >3000kW installed

          Comment

          • TucsonMCM
            Junior Member
            • Jul 2020
            • 14

            #20
            Originally posted by solarix
            The way my local inspector interprets the code, you can't use "unused load capacity" in your backfeed calcs....
            I was wondering about that. I've seen both approaches in online examples, but hadn't made an effort to correlate to NEC revs or other possible explanations. There is some logic to treating the main breaker as the load number, regardless of actual load breakers. So that interpretation implies that one must "commit" to a lower load via a change/derating of the main breaker *IF* you wish to utilize that buss capacity in your allowed PV backfeed.

            Comment

            • TucsonMCM
              Junior Member
              • Jul 2020
              • 14

              #21
              So approaching this from the other direction, the 120% rule applied to my 200A panel & 200A breaker results in a maximum 40A backfeed breaker. And if I understand correctly that the backfeed breaker must be 125% of the incoming load that means I can have a maximum 32A @ 240V = 7680W system. And I assume this would be a CEC-AC measurement of the system?

              If I accept the TEP application systems computations for system CEC-AC (using my enterred components, tilts, azimuth, etc) then 7680 translates to 26 panels (of my tentative make/model), versus the 14 or so panels (= 4.06kw CEC-AC) that I was intending to use. So without any change/derate to my main breaker, I still have ~ +85% future upsize capacity, for example if I purchase an elec vehicle in the future + PV on carport to support it.

              Seems like I can confidently proceed w/ the standard backfed breaker as the interconnect selection, and it won't meaninfully constrain me for future changes.

              Comment

              • foo1bar
                Solar Fanatic
                • Aug 2014
                • 1833

                #22
                Originally posted by TucsonMCM
                So approaching this from the other direction, the 120% rule applied to my 200A panel & 200A breaker results in a maximum 40A backfeed breaker. And if I understand correctly that the backfeed breaker must be 125% of the incoming load that means I can have a maximum 32A @ 240V = 7680W system. And I assume this would be a CEC-AC measurement of the system?
                It would be the AC wattage of the inverter (really it's the AC amperage of the inverter has to be 32A or less)

                This is the reason you'll see "7600W" as one a model size for a lot of manufacturers. (ex. Solaredge has SE7600A and SE7600H,
                SMA has "Sunny Boy 7.7-US", Fronius has "Primo 7.6-1", etc.) All of their installation instructions say 32A max output current

                If I accept the TEP application systems computations for system CEC-AC (using my enterred components, tilts, azimuth, etc) then 7680 translates to 26 panels (of my tentative make/model), versus the 14 or so panels (= 4.06kw CEC-AC) that I was intending to use. So without any change/derate to my main breaker, I still have ~ +85% future upsize capacity, for example if I purchase an elec vehicle in the future + PV on carport to support it.
                Probably more, because usually it usually makes sense to have more DC watts than what the inverter is sized for. Again - installation instructions / data sheet for the inverter will tell you the maximum PV power.

                BTW - your POCO (TEP) may have a maximum size they'll allow you to install based on your historical usage. You may be able to get around that by showing them your plans to buy an EV.

                Also - there may be a limit at 10kW.
                Some places have a 10kW limit for residential installations.
                (You might be able to do a 10kW DC array with a 7.6kW inverter - but that might be oversized for your usage.)

                Comment

                • foo1bar
                  Solar Fanatic
                  • Aug 2014
                  • 1833

                  #23
                  Originally posted by TucsonMCM
                  Although #4 is possible,
                  #4 (line side tap) is probably not possible with that panel, unless adding a socket adapter thingy. And that'd probably fall under "Other"

                  At least I think it's highly likely that the conductor from the socket to the main breaker is a metal bar - not a wire.
                  And therefore it isn't something you can tap.

                  IMO #1 (standard backfeed breaker) is likely to be what you'll want to do.
                  If you want >40A, you could replace the main with a smaller breaker, which would be #4.

                  Comment

                  • rtr688
                    Junior Member
                    • Jul 2021
                    • 2

                    #24
                    Resurrecting old Tucson post.

                    TucsonMCM I'm going to be tackling a DIY and have similar questions to what you've aske here (Pima County DIY/remote inspections/rapid shutdown requirements, TEP interconnection, etc) and I'd love to pick your brain. This winter I'm going to tackle a 8-10kw project on the NE side of town.

                    Apparently we can't send direct messages through the site. If you're still around let me know. Thanks!

                    Comment

                    • sonoran
                      Junior Member
                      • Dec 2021
                      • 14

                      #25
                      Originally posted by rtr688
                      Resurrecting old Tucson post.

                      TucsonMCM I'm going to be tackling a DIY
                      RTR has MCM reappeared ? ...also a TEP customer

                      Comment

                      • rtr688
                        Junior Member
                        • Jul 2021
                        • 2

                        #26
                        Nope! But I'm well along the way of my 12.3kW install.

                        Did all my own drawings for TEP, then after their approval went to county. They had a few small comments.

                        Marked where I wanted to install my disconnect and production meter, TEP approved, and away I go.

                        Comment

                        • sonoran
                          Junior Member
                          • Dec 2021
                          • 14

                          #27
                          Originally posted by rtr688
                          well along the way of my 12.3kW install
                          Fantastic! and thank you for writing back
                          Would you mind contacting me in regards to the TEP portion of the equation
                          Thank you

                          Code:
                          sonoranaz @ protonmail.com

                          Comment

                          Working...