    Volts but no amps?

    Hi -
    I just hooked up my first home made solar panel, producing about 19 volts to my Koneze CMP12 charge controller and the charge controller to my battery bank - 3 batteries hooked in parallel and at about 11.7 volts. I was expecting to see the "charging" LED come on, but it did not. As I poked around w/my multi-meter it seems like I'm getting no current at all (it won't run a tiny hobby motor that my 9V test panel will run).

    I'm kind of stumped. V=IR... I've got volts, the wire (184' total back-and-forth of 10AWG) will give me some small resistance - why no current?

    Thanks in advance.
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    PV cells will produce VOLTAGE with a low amount of light.

    Amps are developed with strong bright light.

    Cloudy or indoor light will produce less then 10% of rated amps. So until you have FULL Sun, don't expect much amps.

    And there is always the possibility that new out of box no-name controller may be a BoC (Box Of Cra*)
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • SteveC
      Member
      • Mar 2011
      • 55

      #3
      184' of 10 ga. wire is gonna cut that voltage down a bunch.

      Comment

      • Mike90250
        Moderator
        • May 2009
        • 16020

        #4
        Originally posted by SteveC
        184' of 10 ga. wire is gonna cut that voltage down a bunch.
        But it's not going to be 0. 200' of #10 @ 6 amps only drops 2 volts.

        I'm suspecting bad tab wire, or cracked cells. Very difficult to diagnose remotely

        spreadsheet based voltage drop calculator:
        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

        solar: http://tinyurl.com/LMR-Solar
        gen: http://tinyurl.com/LMR-Lister

        Comment

        • robojoe_fl
          Junior Member
          • Jun 2011
          • 2

          #5
          Found the problem

          Or it could be the zener diode that I put in backwards...

          Thanks for the input!