    Does this "plan" make practical sense? Please identify flaws.

    Hi All!

    I am trying to setup a solar system in the coming months mostly on my own (setup of ground mount, mounting the panels, sourcing the parts, etc). I plan on getting 2 EVs and hopefully a powerwall (or whatever for storage) in the future. More people will live with me at home in the future as well. I consume about 30kwh a day on my own and its only going to increase with time.

    I wanted to get as many panels as I could accounting for future load requirements. Nothing here is set in stone which is why im coming back on here to get advice from you guys. Keep in mind I am still new to this so be gentle.

    plan:setup.PNG

    I have some questions:
    1) is my "design" feasible ?

    ground mount with wiring going through existing buried conduit all the way some 230ft to the closet where i hope to place the inverters then on to the main panel.

    2) if you had to chose between these two which would you choose? (pretty sure i have 3-phase as my meter says 3W on it)

    Not sure if I would even be allowed to use the 30kw commercial inverter, but its cheaper than 2 sunny boys with double the capacity, the only issue being lack of SPS (solar power during grid down scenario)

    a) 30kwh (no SPS) SMA SUNNY TRIPOWER 30000TL-US-10 = $2,437.50



    b) 15.4kwh (2k watt SPS, grid down support) SMA SunnyBoy 7.7-1SP-US-40 = $2939.24

    https://www.wholesalesolar.com/cms/m...2304485795.pdf

    3) if you had 40-45 panels knowing what you know given the scenario what would be your panel wiring strategy be?

    Electrical specifications:
    Module Watts STC: 345 Watts
    Max Power Voltage (Vmpp): 38.6 Volts
    Max Power Current (Impp): 8.94 Amps
    Open Circuit Voltage (Voc): 46.1 Volts
    Short Circuit Current (Isc): 9.44 Amps
    Max System Voltage: 1500V (IEC/UL) or 1000V (IEC/UL)
    Series Fuse Rating: 30 Amps
    Module Efficiency: 17.39%

    4) In Miami-Dade, where i live, you are required to submit a design and hire a certified electrician to do all the electrical wiring so I will have to hire someone for that, any advise for finding the right people to do that part ?

    I have a quote for around 6k that includes the design, permit submitting , electrical connecting - basically all the things I cant do.


    5) Is it true that you have to get a certain type of insurance if you go over a 10kw system before the electrical company will give you the netmeter ??


    The parts run about $14k-16k for a grand total of $20-22k for a 14.5 - 15.5 Kw system.

    Do you guys think it's decent pricing? I don't even know if I would save much money over having someone do everything themselves but I was quoted 20k for a 9Kw system in the past so i thought 20-22k wasnt too bad given the extra 6kw I would be getting.

    Any advice is welcome. Thank you in advance.
    Last edited by NothingInCommon; 03-31-2019, 08:21 AM.
  • ButchDeal
    Solar Fanatic
    • Apr 2014
    • 3802

    #2
    Those inverters are rated in kW not kWh. Almost everyolace you wrote kWh should be kW.

    what voltage is your house on from leg to leg?

    you need to determin if you are on 3 phase or split single phase. And if 3 phase do you have all three legs or just two legs.

    you need to look up the net metering requirments for your power company and determin the rules for large systems.

    is the powerwall 2 certified for 3 phase?

    you need to plan for a line side tap ...