AC disconnect and correct wiring for Micro inverter
The situation may be different in Canada, though.Last edited by inetdog; 02-16-2019, 07:05 AM.SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
It gets very hard for the next guy when you keep switching cable sizes. Someone might see the bigger wire and think they can increase the breaker size, but in reality when done and the other end of the wire it is small it is dangerous. In this situation it could cause a house fire. Upsize the THWN to match the Romex if possible. I am sure the cost is not worth a life. Correct me if I am wrong.
sizing a run to reduce voltage drop? I have been plotting getting back most of the 1000 KWH a year
a 600 foot 240VAC loop costs me in resistive losses. A piece of the loop has already been replaced with
1/0 for the pair of 240VAC wires, while the circuit breaker and hardly used neutral remain for 2 gauge.
I will probably not be the last person to own the equipment.
Now that I own a trencher, the possibility of replacing the longest segment (between buildings, more
circuit breakers along the way) is practical. 1/0 or aluminum 2/0 would do the job of reducing voltage
loss, using a neutral and breaker just sized for the actual currents. Bruce RoeComment