Huh! You need to go back and read what you said. Not only can you not interpret what the code says, you do not even know what you wrote.
That is BS. The only time you would physically bond a conductor to both ends is the GEC. Get that through your thick head. There is only one Ground Conductor, everything else is a Bonding
Geez you are dense. No wire of any kind is required, get that through your thick skull.
To the OP I apologize for the diversion. DIY forums are not where you should be getting your information. You can run conduit to protect and route your conductors. If you run a Bonding Conductor if can be bare or insulated, and if insulated needs to be Green in color so it is easily identified.
If the conduit is ran from your service panel, even if it goes through the Inverter first, no bonding jumper is required, the conduit itself acts as the bonding jumper. You are permitted to run a Bonding Jumper inside the conduit (for redundancy), just not required to do so.
However that is not best practice because you are inviting lightning inside your home. Best Practice is to not run metal Conduit the full length of the circuit. Example just to inside the attic, then transition over to PVC. That will Isolate and Float the metal conduit and panel frames electrically. To make that safe and give lightning a place to go is run a Down Conductor straight down to dirt to the Grounding Electrode System your AC Service is bonded too. If the Down Conductor comes down where the Electrodes are not located directly below, trench in line below grade to where the Electrode is. That way if lightning were to directly strike a panel, it is routed outside around your home directly to earth. Otherwise it would go through your home wiring and burn it up. Electrical codes as of now allow both ways. Next Code Cycle, possible even now because your local jurisdiction amended out the option NEC gives you to use Equipment Bonding Conductors because it is flat out dangerous to do it that way. If it has been amended out, your only other option is Best Practice and use a Down Conductor and treat the frames as Air Strike Terminals. Just be sure not to use any ferrous metal Conduit. Well you can but would be required to bond the Conduit to both ends of the Down Conductor to eliminate Magnetic Choking effect.
That is BS. The only time you would physically bond a conductor to both ends is the GEC. Get that through your thick head. There is only one Ground Conductor, everything else is a Bonding
Geez you are dense. No wire of any kind is required, get that through your thick skull.
To the OP I apologize for the diversion. DIY forums are not where you should be getting your information. You can run conduit to protect and route your conductors. If you run a Bonding Conductor if can be bare or insulated, and if insulated needs to be Green in color so it is easily identified.
If the conduit is ran from your service panel, even if it goes through the Inverter first, no bonding jumper is required, the conduit itself acts as the bonding jumper. You are permitted to run a Bonding Jumper inside the conduit (for redundancy), just not required to do so.
However that is not best practice because you are inviting lightning inside your home. Best Practice is to not run metal Conduit the full length of the circuit. Example just to inside the attic, then transition over to PVC. That will Isolate and Float the metal conduit and panel frames electrically. To make that safe and give lightning a place to go is run a Down Conductor straight down to dirt to the Grounding Electrode System your AC Service is bonded too. If the Down Conductor comes down where the Electrodes are not located directly below, trench in line below grade to where the Electrode is. That way if lightning were to directly strike a panel, it is routed outside around your home directly to earth. Otherwise it would go through your home wiring and burn it up. Electrical codes as of now allow both ways. Next Code Cycle, possible even now because your local jurisdiction amended out the option NEC gives you to use Equipment Bonding Conductors because it is flat out dangerous to do it that way. If it has been amended out, your only other option is Best Practice and use a Down Conductor and treat the frames as Air Strike Terminals. Just be sure not to use any ferrous metal Conduit. Well you can but would be required to bond the Conduit to both ends of the Down Conductor to eliminate Magnetic Choking effect.