    Technical Question About Grid-Tied Panels

    You make more electricity than you use during the day, especially in the summer. We all know this. But there's another question I haven't seen discussed anywhere.

    I have been under the impression that, when you make more juice than you're using, solar panels sent only the excess production to the grid. But a discussion in an e-mail list I'm part of suggests that, no, you send everything you generate the grid, and get everything you use back from the grid, and that the accounting is done according to (in most cases) a net metering formula that gives you a kWh for each one you send.

    I hadn't thought about this detail until now. When you think it through, it would make sense that you'd send everything to the utility and get everything from them, because we could expect that panels might have considerable voltage swings that would make a direct connection to the end user problematic for appliances that require stable voltage.

    Does anyone know? Thanks much in advance.
  • PNPmacnab
    Solar Fanatic
    • Nov 2016
    • 425

    #2
    You send everything to the house. The electrons magically know where to go. Net metering will be a thing of the past. You will soon be billed in 15 minute intervals. Demand pricing will encourage people to start placing their panels facing west. Utilities only agreed to the present metering because they thought it would never take off. Excess noon production is a menace to the utilities.

    Comment

    • bcroe
      Solar Fanatic
      • Jan 2012
      • 5213

      #3
      You have a lot to learn, and thanks PNP. The panels generate DC voltage which cannot be
      connected to the grid. DC is fed to a GRID TIE INVERTER which finds the best panel operating
      point (MPPT) at any time, then uses the input to generate AC output power matching up to the grid.

      For those of us with only a single meter, the PoCo only sees the DIFFERENCE between what
      AC energy you generate, and what you consume. Grid power may flow in either direction
      depending on your generation and consumption. Bruce Roe

      Comment

      • sdold
        Moderator
        • Jun 2014
        • 1466

        #4
        Originally posted by Charlie W
        it would make sense that you'd send everything to the utility and get everything from them,
        It makes no sense, in a basic NEM system with a single meter, because if your house is using 6 kW and your panels are generating 4 kW, the grid is delivering 2 kW to your house to make up the shortfall. You can see this on your meter, which tells you how much power is going in which direction. It's easy to understand if you switch everything to DC. DC current can't go in two directions at once.
        Last edited by sdold; 03-25-2018, 03:22 PM. Reason: Starting to sound too much like Russ

        Comment

        • Charlie W
          Member
          • Oct 2016
          • 60

          #5
          I had thought that only the excess went into the grid, but the post I had seen left some doubt. As it turns out, that post was ambiguously worded and open to varying interpretations, hence my question to this group.

          Past that, I am curious as to how the utilities manage the variability of solar, and especially of wind.

          By the way, PNP, the sarcasm doesn't help. If I can't ask an honest question here without that kind of crap in return, where do you suggest I go to find knowledgeable people who aren't condescending jerks?

          Comment

          • Mike90250
            Moderator
            • May 2009
            • 16020

            #6
            Originally posted by Charlie W
            .............
            By the way, PNP, the sarcasm doesn't help. If I can't ask an honest question here without that kind of crap in return, where do you suggest I go to find knowledgeable people who aren't condescending jerks?
            Charlie, wait till you meet Sunking. He just drives the roads up north, needs no snowplow or chains. (snowflakes sublimate in front of him)

            This is the internet, and if you were offended by something you imagined PNP wrote (I read it over a couple times, and looked to see if he edited something out) you are going to be in sad shape in a couple days. This forum speaks truth, unlike many forums that are sales driven. This is the straight from the hip shooting , not "well, if you think it's right for you, maybe the laws of physics will accommodate you in this case" style of forum. If you are going to be hands on with solar, you are going to learn about proper connections here (we'll scald you in oil if you think your hammer crimper is going to work on your 1/O cable), the hazards of medium voltage DC, and the dreaded AHJ. (Authority Having Jurisdiction - building code inspector).
            Last edited by Mike90250; 03-25-2018, 05:50 PM. Reason: typo
            Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
            || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
            || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

            solar: http://tinyurl.com/LMR-Solar
            gen: http://tinyurl.com/LMR-Lister

            Comment

            • Charlie W
              Member
              • Oct 2016
              • 60

              #7
              Originally posted by Mike90250

              Charlie, wait till you meet Sunking. He just drives the roads up north, needs no snowplow or chains. (snowflakes sublimate in front of him)

              This is the internet, and if you were offended by something you imagined PNP wrote (I read it over a couple times, and looked to see if he edited something out) you are going to be in sad shape in a couple days. This forum speaks truth, unlike many forums that are sales driven. This is the straight from the hip shooting , not "well, if you think it's right for you, maybe the laws of physics will accommodate you in this case" style of forum. If you are going to be hands on with solar, you are going to learn about proper connections here (we'll scald you in oil if you think your hammer crimper is going to work on your 1/O cable), the hazards of medium voltage DC, and the dreaded AHJ. (Authority Having Jurisdiction - building code inspector).
              I wasn't arguing with anyone in this thread, and don't think my question deserved the treatment the one poster gave it. I'll certainly live, but I see nothing wrong with calling him out. Trust me, my pushback was mild by my own standards. "Snowflake" isn't something I'm called too often, that's for sure. Other names, yes, but not that one.

              Comment

              • SunEagle
                Super Moderator
                • Oct 2012
                • 15166

                #8
                Basic knowledge is that electricity will take the shortest path to the load. So you house loads get all they want from the solar and then the excess goes to the grid. If there is no excess solar generation to send to the grid then the house loads takes what they need from the grid.

                Electricity 101.

                Comment

                • azdave
                  Moderator
                  • Oct 2014
                  • 796

                  #9
                  Originally posted by Charlie W
                  ...a discussion in an e-mail list I'm part of...
                  People are still using e-mail lists?




                  Dave W. Gilbert AZ
                  6.63kW grid-tie owner

                  Comment

                  • solarix
                    Super Moderator
                    • Apr 2015
                    • 1415

                    #10
                    The grid is essentially a voltage controlled power source - it will supply (or absorb) as much current as needed to keep the voltage (240Vac for your house) constant (or at least stable). So now with the voltage fixed, all you need to think about are the current flows. A grid-tied solar inverter is a current source - it will follow the grid voltage and produce as much current as needed at that voltage to expend the DC power it is receiving from the array. The current is injected (or backfed) into your breaker box with the house absorbing as much of it as it wants and the excess then is pushed out into the grid (and measured by the utility's revenue meter). To push the excess power back to the grid, yes it has to boost the voltage a bit (but the grid being very low impedance (resistance), just a tenth of a volt or so).
                    If you want to read up on this - it is basic electric theory called "Thevenin equivalent" circuits where you model the system as simple elements such as voltage and current sources, loads and resistances etc. Think of your breaker box as a node with the grid as a voltage source, the solar inverter as a current source and your house as a load. Now imagine it with the house loads changing all the time, the solar power adjusting to a cloud going by and your neighbor's A/C kicking on and off.....
                    Yes, the grid current is ac and is oscillating back and forth, but the power flow (volts times amps) is directional, flowing into your house when the solar power is less than what your house needs and flowing out when there is excess.
                    BSEE, R11, NABCEP, Chevy BoltEV, >3000kW installed

                    Comment

                    • ButchDeal
                      Solar Fanatic
                      • Apr 2014
                      • 3802

                      #11
                      Originally posted by Charlie W
                      You make more electricity than you use during the day, especially in the summer. We all know this.
                      SOME people make more than they use during the day. You are making an assumption both on generation (a likely assumption) and on consumption (not always true though).



                      Originally posted by Charlie W
                      I have been under the impression that, when you make more juice than you're using, solar panels sent only the excess production to the grid.
                      this is true for MOST NET metering installs.


                      Originally posted by Charlie W
                      But a discussion in an e-mail list I'm part of suggests that, no, you send everything you generate the grid, and get everything you use back from the grid, and that the accounting is done according to (in most cases) a net metering formula that gives you a kWh for each one you send.
                      This is true in a FEW areas and is more commonly known as dual metering. It is much less favorable and make bimodal systems impossible
                      I have seen it only in coop utility zones and even then only a few of them.


                      Originally posted by Charlie W
                      I hadn't thought about this detail until now. When you think it through, it would make sense that you'd send everything to the utility and get everything from them, because we could expect that panels might have considerable voltage swings that would make a direct connection to the end user problematic for appliances that require stable voltage.

                      Does anyone know? Thanks much in advance.
                      No this makes zero logic. Yes lots of people know this. Solar Produces DC and the Votage variability is easily handled with MPPT and Inverters, which make nice stable power.
                      If you understand the word NET in an accounting sense then you would know that net metering means that you use your own power and send excess to the grid.
                      OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

                      Comment

                      • PNPmacnab
                        Solar Fanatic
                        • Nov 2016
                        • 425

                        #12
                        What sarcasm? Electrons always know where to go. They flow from a higher potential to a lower. Within the same cycle you could be pulling or sourcing numerous times to the grid. You can only understand the average movement.

                        Comment

                        • SunEagle
                          Super Moderator
                          • Oct 2012
                          • 15166

                          #13
                          Originally posted by PNPmacnab
                          What sarcasm? Electrons always know where to go. They flow from a higher potential to a lower. Within the same cycle you could be pulling or sourcing numerous times to the grid. You can only understand the average movement.
                          Good point. Instantaneous movement of electrons is very hard to accurately measure. Even most meters perform an average measurement over a specific time period.

                          Comment

                          • JSchnee21
                            Solar Fanatic
                            • May 2017
                            • 522

                            #14
                            When I was a small boy, maybe 7 or 8 years old, I was down in the basement with my Dad who was brazing a water line for a utility sink. Son he said, "The only thing you need to know about plumbing is that Shxt runs down hill." 35 years later I cannot tell you how many college graduates I've had to teach that basic message to when it comes to electricity -- or any moving fluid or potential energy source. Electrons, like water molecules follow the path of least resistance and thus flow down hill from high potential to low potential. The same is true for heat, solvent and solute gradients for osmolarity and osmolality, ions (like sodium, potassium, and calcium) across cell membranes, etc. Yes, purists and theorists will cringe, but at the end of the day, maybe that little electron does in fact know where he's going.

                            Comment

                            • bcroe
                              Solar Fanatic
                              • Jan 2012
                              • 5213

                              #15
                              Originally posted by JSchnee21
                              Electrons, like water molecules follow the path of least resistance and thus flow
                              down hill from high potential to low potential.
                              If you want to be precise, electrons take every path available. However, most of them take the path with
                              best conductance (least resistance). Bruce Roe