I've been reading for past few weeks about how to ground a solar panel, but I'm still confused. My setup will be fairly simple. I want to install a solar panel on the roof of my rear patio that will charge a battery in my garage (via a charge controller) that can then be connected to an inverter (I'm going to replace the one I have and haven't chosen the new one yet) so I can plug in some small items during a power outage (fan, tv, phone chargers, etc). The inverter's AC output will not in any way be connected to the home's AC power. The inverter will simply be used stand-alone to plug in these items temporarily until utility power is restored.
My understanding thus far is that I must ground the solar panel frame to the earth via a ground rod driven close to the panel (which unfortunately will be on the exact opposite corner of the house than the AC service ground rod by the meter pan) for protection from surges like lightning, in order to have a short path to the earth. I have also read that any new ground rod should be bonded to the home's existing ground rods.
I have attached a diagram of the existing layout of my home and existing ground rod location(s).
pvground.jpg
To explain briefly why my house's grounding system is set up this way: The builder originally drove (now supplimental) ground rod "C" during the build, but electrical service was eventually installed to the opposite side of the house. They ran a #4 wire from the meter through the attic and down the opposite side of the house to the ground rod "C", which also had a UFER ground wire from the foundation connected. After being in the house for several months, I noticed the wire coming out of the foundation for the UFER was partially severed (I didn't do it), so I had an electrician come out to see if it could be repaired (cadweld or some other way). He said it wouldn't be possible due to the condition/length of the UFER wire and it would be easiest just to install two new rods at the service entrance (A & B), which he did, and ran a new #4 from the meter directly to "A" & "B". I read later in the NEC code that "all grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system", so I ran a #4 wire from "A" to "C" as it seemed necessary to bond "all existing grounding electrodes" to meet this requirement. This results in the current configuration shown in the attached diagram.
At this point, I have the following questions:
1) Is it proper to install a new ground rod at proposed location "D" near the solar panel location and run a #6 wire from the panel to that rod? From my reading, it seems it is best to have a ground rod/down wire close to the panel to provide a short direct path (rather than into the house) for lightning and other surges at the solar panel.
2) It also seems I should bond the proposed solar ground rod "D" to the existing ground rod system. If so, can I connect it to supplemental rod "C" or must "D" be bonded directly to "A"?
3) What is the proper connection for an equipment grounding conductor between the inverter and solar panel?
Thanks!
My understanding thus far is that I must ground the solar panel frame to the earth via a ground rod driven close to the panel (which unfortunately will be on the exact opposite corner of the house than the AC service ground rod by the meter pan) for protection from surges like lightning, in order to have a short path to the earth. I have also read that any new ground rod should be bonded to the home's existing ground rods.
I have attached a diagram of the existing layout of my home and existing ground rod location(s).
pvground.jpg
To explain briefly why my house's grounding system is set up this way: The builder originally drove (now supplimental) ground rod "C" during the build, but electrical service was eventually installed to the opposite side of the house. They ran a #4 wire from the meter through the attic and down the opposite side of the house to the ground rod "C", which also had a UFER ground wire from the foundation connected. After being in the house for several months, I noticed the wire coming out of the foundation for the UFER was partially severed (I didn't do it), so I had an electrician come out to see if it could be repaired (cadweld or some other way). He said it wouldn't be possible due to the condition/length of the UFER wire and it would be easiest just to install two new rods at the service entrance (A & B), which he did, and ran a new #4 from the meter directly to "A" & "B". I read later in the NEC code that "all grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system", so I ran a #4 wire from "A" to "C" as it seemed necessary to bond "all existing grounding electrodes" to meet this requirement. This results in the current configuration shown in the attached diagram.
At this point, I have the following questions:
1) Is it proper to install a new ground rod at proposed location "D" near the solar panel location and run a #6 wire from the panel to that rod? From my reading, it seems it is best to have a ground rod/down wire close to the panel to provide a short direct path (rather than into the house) for lightning and other surges at the solar panel.
2) It also seems I should bond the proposed solar ground rod "D" to the existing ground rod system. If so, can I connect it to supplemental rod "C" or must "D" be bonded directly to "A"?
3) What is the proper connection for an equipment grounding conductor between the inverter and solar panel?
Thanks!