I'm having a hard time making a decision that works the best. I upgraded my service from 100am to 200am. I'm going to install a Sunny Boy 3.0 and 6.0. My calculations say I can't connect to the breaker because I would be over the allowed current.
Could I connect one inverter to the load side and then the second to with a tap on the supply side?
Or should I combine both into a dedicated service and connect them to the supply side with a tap? If I do this I would need a 100amp service with a 100amp breaker correct?
6.0SB: 6,000w/240v=25A 1.25x25A=31.25A 35ABreaker
3.0SB: 3,000w/240v=12.5A 1.25x12.5A=15.63A 20A Breaker
What are your thoughts?
Could I connect one inverter to the load side and then the second to with a tap on the supply side?
Or should I combine both into a dedicated service and connect them to the supply side with a tap? If I do this I would need a 100amp service with a 100amp breaker correct?
6.0SB: 6,000w/240v=25A 1.25x25A=31.25A 35ABreaker
3.0SB: 3,000w/240v=12.5A 1.25x12.5A=15.63A 20A Breaker
What are your thoughts?