I think I know the answer, but.... I have two inverters. SE5000 and SE3800. Any reason these cannot have an odd number of panels/optimizers in the string? SE3800 would have 17 and SE5000 would have 23. I want to add 6 more panels, but in order to keep the likely output close to max output I need to add them in this way. It should work right? It will be well lower that the max input of both inverters, but I'd like to avoid clipping which I assume is what will happen if the DC input is higher than the max output. I guess that's another question. Will the inverter just clip if the input is higher than the max output?
Most Popular Topics
Collapse
Solar Edge Inverter Questions
Collapse
X
-
-
Well yes and no. It depends on the max string wattage of 5.25kw and at least 8 modules per string.
if you have multiple faces, adding some modules to one inverter on multiple faces will increase production ( with solaredge).
Do you know how the two inverters are currently strung?
OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH -
SE3800 - One string 14(275 Solarworld) 2(300 LG) with 8 facing West with rest facing south. SE 5000 one string. 18(275 Solarworld) all facing south. all 6 new panels will face west and be LG 305sComment
-
are they both one string each? What optimizers do you have?
you can add one of the LG 305s as planned to the SE3800
the SE5000 if it is a single string then you can't add an LG305 to it. You would have to break it up into two strings of at least 8 optimizers each.OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNHComment
-
all optimizers are p300s. the SE3800 has a sting of 16 panels. 14 SW275s and 2 LG 300s for 4.45kw. The SE5000 has one string of 18 SW275s. I don't understand why the se5000 needs two strings? Is there a max number of optimizers that can be in a string? besides I want to add 5 more LG305s to the SE5000 for a total of 23 panels/optimizers for a total of 6.475kw.Comment
-
all optimizers are p300s. the SE3800 has a sting of 16 panels. 14 SW275s and 2 LG 300s for 4.45kw. The SE5000 has one string of 18 SW275s. I don't understand why the se5000 needs two strings? Is there a max number of optimizers that can be in a string? besides I want to add 5 more LG305s to the SE5000 for a total of 23 panels/optimizers for a total of 6.475kw.OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNHComment
-
Comment
-
adding a new string sounds difficult. Is that terribly hard? I have a combiner box on the roof. I guess I could create a new sting of 8 using the new 5 and 3 from the existing and bring it into the box?Last edited by easye; 01-08-2017, 08:07 PM.Comment
-
If the wire from the roof down is sufficient to handle the amps then you can combine on the roof, if not bring a separate wire down to the inverter it has two DC attachement locations.
There is no need for fusing with solaredge or with just two strings.OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNHComment
-
hmmm. Maybe is just a weatherproofing box for the wires to come down into the attic. I'll have to go take a look at it. otherwise I would have to drop wires down and I guess I'm probably out on that. I'm guessing splicing those wires together is a bad idea. This project is getting to be more than it might be worth. Maybe just pay the $20 electric bill lol.Comment