Sooooooooooooooooo, I know we've covered this before but just wanted to solicit some opinions here on both the feasibility as well as any potential code issues. Let me start by outlining my system:
First of all the grid tied electrical panel is fed through a main sub-panel which is separated from the main utility pedestal/meter which has only the main breaker installed there. The circuits are distributed through this subpanel and is also where my solar system feeds back into the grid through 2 separate circuits (220V). The solar system is a 4.4KW system installed which utilizes 2 strings of Enphase MicroInverters each feeding into the aforementioned main distribution panel.
On the Generator side I currently have a manual transfer switch installed between the pedestal/meter and the subpanel. I have been using a large portable generator to power the house during outages managing the load by turning off first the solar feed into the system and other circuits as needed, then powering up the generator. This works well and isolates the solar system so no opportunity for energizing the panels and of course backfeeding to the grid as a result of the transfer switch.
I'm now looking to upgrade the generator to an automatic system and I need to isolate the solar system from the distribution panel to eliminate the opportunity to 1) energize the panels and 2) damage the generator with likely potential backfeed.
Sooooooooooooooooooooo, here's what I am thinking: Rewire the solar circuits all the way back to the service pedestal bus with it's own disconnect breaker(s) which would isolate the solar from the rest of the circuits and then replace the manual transfer switch with the automatic transfer switch which would have more power (not to mention convenience of being automatic) powering the main distribution panel with no need for manual power management even though it would still be an option if desired.
It would seem that this would isolate the solar system from the generator power when energized and then re-energized (5 minutes) after the utility power is restored and after the generator shuts itself off automatically.
What say you guys about this idea? Is there a better or safer way to do this......would tying the system to the main bus at the pedestal with it's own disconnect (in addition to the existing AC disconnect that is in the system) work? I realize I'll have to resubmit to the utility and I already have the permit side covered.......are there some hidden issues here that I am missing???
Thanks in advance!
First of all the grid tied electrical panel is fed through a main sub-panel which is separated from the main utility pedestal/meter which has only the main breaker installed there. The circuits are distributed through this subpanel and is also where my solar system feeds back into the grid through 2 separate circuits (220V). The solar system is a 4.4KW system installed which utilizes 2 strings of Enphase MicroInverters each feeding into the aforementioned main distribution panel.
On the Generator side I currently have a manual transfer switch installed between the pedestal/meter and the subpanel. I have been using a large portable generator to power the house during outages managing the load by turning off first the solar feed into the system and other circuits as needed, then powering up the generator. This works well and isolates the solar system so no opportunity for energizing the panels and of course backfeeding to the grid as a result of the transfer switch.
I'm now looking to upgrade the generator to an automatic system and I need to isolate the solar system from the distribution panel to eliminate the opportunity to 1) energize the panels and 2) damage the generator with likely potential backfeed.
Sooooooooooooooooooooo, here's what I am thinking: Rewire the solar circuits all the way back to the service pedestal bus with it's own disconnect breaker(s) which would isolate the solar from the rest of the circuits and then replace the manual transfer switch with the automatic transfer switch which would have more power (not to mention convenience of being automatic) powering the main distribution panel with no need for manual power management even though it would still be an option if desired.
It would seem that this would isolate the solar system from the generator power when energized and then re-energized (5 minutes) after the utility power is restored and after the generator shuts itself off automatically.
What say you guys about this idea? Is there a better or safer way to do this......would tying the system to the main bus at the pedestal with it's own disconnect (in addition to the existing AC disconnect that is in the system) work? I realize I'll have to resubmit to the utility and I already have the permit side covered.......are there some hidden issues here that I am missing???