Thanks for the info and links. So it seems like to me that what I could do is add another (2) 12v 100 watt panels, and never put a load on the inverter that is over 1,000 watts or just get a new 1,000 watt inverter all together. The paperwork for my 3kw inverter says that it has a no load current of 0.9 amps. I understand that if I max out the inverter that I am risking pulling too much from the battery bank and also my 4 gauge wire I'm using from the batteries to the inverter is too small. But if I use the 3kw inverter like a 1kw inverter common sense tells me that would work safely. I don't see the circuitry in the 3kw inverter being that much higher than a 1kw inverter, in fact my Aims manual says the no load current on their 1500 watt inverter is 0.64 amps.
Try our solar cost and savings calculator
Most Popular Topics
Collapse
How to monitor off grid battery bank state of charge
Collapse
X
-
-
I'm going to stand way back and watch the sparks. 200A fuse is NOT any sort of safety for 4 ga wire.
4 ga wire is generally not safe beyond 75A.
Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
Thanks for the info and links. So it seems like to me that what I could do is add another (2) 12v 100 watt panels, and never put a load on the inverter that is over 1,000 watts or just get a new 1,000 watt inverter all together. The paperwork for my 3kw inverter says that it has a no load current of 0.9 amps. I understand that if I max out the inverter that I am risking pulling too much from the battery bank and also my 4 gauge wire I'm using from the batteries to the inverter is too small. But if I use the 3kw inverter like a 1kw inverter common sense tells me that would work safely. I don't see the circuitry in the 3kw inverter being that much higher than a 1kw inverter, in fact my Aims manual says the no load current on their 1500 watt inverter is 0.64 amps.Comment
-
I'm going to stand way back and watch the sparks. 200A fuse is NOT any sort of safety for 4 ga wire.
4 ga wire is generally not safe beyond 75A.
https://lugsdirect.com/WireCurrentAm...ble-301-16.htmOutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNHComment
-
It sounds reasonable that you could limit your loads to 1000w as long as you can prevent anyone else from plugging in something that exceeds it when you are not around. However, if there is a failure somewhere in your AC load, that inverter will quite happily surge double its rated capacity and maintain its 3kw power even if it means fire.OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNHComment
-
Thanks for the info and links. So it seems like to me that what I could do is add another (2) 12v 100 watt panels, and never put a load on the inverter that is over 1,000 watts or just get a new 1,000 watt inverter all together. The paperwork for my 3kw inverter says that it has a no load current of 0.9 amps. I understand that if I max out the inverter that I am risking pulling too much from the battery bank and also my 4 gauge wire I'm using from the batteries to the inverter is too small. But if I use the 3kw inverter like a 1kw inverter common sense tells me that would work safely. I don't see the circuitry in the 3kw inverter being that much higher than a 1kw inverter, in fact my Aims manual says the no load current on their 1500 watt inverter is 0.64 amps.OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNHComment
-
There are lots of reasons why good intentions to keep a load below 300w won't work in every scenario, especially when components can fail in unexpected ways.Comment
-
What if an automobile was designed to be safe up to 70 miles an hour but its engine would catch fire over 70? Would anyone feel safe if they rationalized that since 70 is the maximum speed limit where they drive, they will never exceed it and be safe?
There are lots of reasons why good intentions to keep a load below 300w won't work in every scenario, especially when components can fail in unexpected ways.OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNHComment
-
I purchased the same items (except I'm 2 panels and 2 batteries short at the moment), but I went with a larger inverter. That is the only difference. I thought if I mimicked their system I would be ok.Comment
-
Comment
-
Thanks everyone. I do have a MPPT controller so I'll get a couple more panels and batteries, then swap out the 200amp fuse with a 75amp. I based my system off the design by Tin Hat Ranch. Here is a link to their schematic: http://tinhatranch.com/wp-content/up...chematicR1.pdf
I purchased the same items (except I'm 2 panels and 2 batteries short at the moment), but I went with a larger inverter. That is the only difference. I thought if I mimicked their system I would be ok.OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNHComment
-
Great so you have a cc capable of 24v and doubled the modules. I would recommend you turn it off, read up a bunch before doing anything more, and consider a course of action around going to 24v as it involves much of what you already plan with just the addition changing the inverter and wiring batteries differently. Has added bonus of being able to add more modules.Comment