Question on wire usage:
I want to run my main #8 wires through my attic, down my walls, into the back of my disconnect, next to my service panel. Can I use Romex/NM 8/3 wire? I don't believe there's an issue with the wire in the attic or walls, but the wire will need to penetrate the roof.
My current plan is to use about a one foot long piece of EMT through the roof sheathing, flashed and terminated underneath my disconnect box. Will this fly? Essentially, I will have about one foot of Romex in conduit, above roof, in a wet location. How is this situation usually handled?
Thanks!Comment
-