    Sizing Inverters & Chrage Controllers??

    Hi,
    I have a question regarding charge controllers and inverters.

    I want to size a charge controller and inverter for a 65kWp system
    The modules used are 34v,165Wp
    and my specification is for a max of 1000v string system


    What would be my charge controller and inverter specs?

    i am using 2v,1500Ah batteries for 4 hours backup (roughly 200 Nos)

    I am a newb when it comes to solar...i am slowly learning..so pls hlep

    Regards,
    Ruroken
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    Questions
    What's KWp
    Whats Nos
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • rurokenshi
      Junior Member
      • May 2010
      • 9

      #3
      kWp - kilo watt peak
      Nos - Number (Not Nitrous Oxide!!)

      Not so obvious uh...

      Comment

      • Mike90250
        Moderator
        • May 2009
        • 16020

        #4
        Well, you are speaking in non-standard terms. Also forgot to ask, what is the battery bank voltage?

        1,000V dc solar string voltage ? YIKES.

        There are no High voltage string controllers for batteries that I know of.

        Pure grid tie inverters can run up to 550VDC from the panels.

        Battery based systems can run up to 48V DC batteries, and about 140VDC on the string.
        (some industrial systems can go to 300VDC, but they have interlocks on the doors to the battery room)

        Systems aren't rated as 65 KWp, they would be listed more like 30KW or 5KW. Any install over 10KW would need special utility permission, as they are not prepared to deal with that about of back feed power. And over 10KW may need to be a 3 phase system.
        Example
        Last edited by Mike90250; 06-23-2010, 01:22 PM.
        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

        solar: http://tinyurl.com/LMR-Solar
        gen: http://tinyurl.com/LMR-Lister

        Comment

        • rurokenshi
          Junior Member
          • May 2010
          • 9

          #5
          Thanks for the info mike...the system used here is a grid tied system.
          Special permissions have been obtained...it is a govt project....

          I have a few questions though:

          How would the solar string be sized?...according to inverter voltage or is it the other way arnd?...size the string first and then select the inverter??

          If this is an off-grid setup...how would you size the batteries?

          Thanks

          Comment

          • Mike90250
            Moderator
            • May 2009
            • 16020

            #6
            Originally posted by rurokenshi
            How would the solar string be sized?...according to inverter voltage or is it the other way arnd?...size the string first and then select the inverter??

            If this is an off-grid setup...how would you size the batteries?
            To size the strings, you select your inverter, and the inverter spec will tell you how the strings should be configured. You will likely have several inverters, and depending on the capacity of each one, will determine how many you will need. As a matter of principal, I'd not go past 80% of an inverters capacity. If it's an 15KW inverter, I'd only feed it 12KW of PV (80%)

            Battery sizing, will the batteries be for daily cycle use, or standby if the power fails?
            Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
            || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
            || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

            solar: http://tinyurl.com/LMR-Solar
            gen: http://tinyurl.com/LMR-Lister

            Comment

            • rurokenshi
              Junior Member
              • May 2010
              • 9

              #7
              Thanks Mike.....the battery is used for standby purposes only...

              battery power is fed only when both solar as well as the grid fail (like in the night..when there's no solar and there are power cuts!!)


              I have another question though.....Can we size the inverter with only the Watt Peak of the solar panel like if its an instantaneous power of 175W from a sharp panel, can we size the inverter based on this...or do we size the inverter after getting the load pattern....because most of the inquiries laid out are sizing inverters given the instantaneous power of the panel!!!...

              Comment

              • Mike90250
                Moderator
                • May 2009
                • 16020

                #8
                size the inverter to the loads you expect it to drive.
                Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                solar: http://tinyurl.com/LMR-Solar
                gen: http://tinyurl.com/LMR-Lister