Hello all,
I'll be installing a small semi DIY system (with the help of a pro) in San Jose, CA, using 6 panels and Enphase M215 micro-inverters. The plan is to penetrate the roof under or near the last panel and route the (AC) circuit through the attic. No conduit on the roof. The panels will be on the opposite side of the house from the service entrance. I do power electronics design for a living so I'm no stranger to ohms law and high voltages lol.
The house was built in the late 60s and some of the existing circuits going from the service panel into the attic don't have conduit, but one of them has flexible conduit. The installer guy commented that the city inspector may flag the flexible conduit and require me to rip it out before approving the solar system. He also said that solid conduit is required for the solar branch circuit in the attic.
1) In general (not solar), why is no-conduit OK for some circuits, but flex conduit not OK? It makes no sense to me that either no conduit, or solid conduit, are OK but flex conduit is not OK.
2) Is conduit required for micro-inverter AC output in the attic? Installer says yes. The 6 panels will only put out about 5.5A. I don't understand why 15A lighting branch circuits don't require conduit but micro-inverter outputs would. The micro-inverters will not put out any voltage if they do not sense the presence of the mains. If the breaker feeding it is opened, the micro-inverters will shut down.
3) Installer guy says 10 AWG cable is required, with 8 AWG ground. Why would 10 AWG be required for a circuit that produces < 6A, but 14 AWG is OK for 15A lighting branch circuits?
4) The Enphase M215's are the "IG" (integrated ground) variant, which means they have double insulation internally and do not require a ground connection for Safety to prevent electric shock in the case of internal insulation failure. (Like how some home electronic appliances and laptop chargers have a plug that don't have the third, ground prong). So AFAIK that means only the panel bracketry has to be grounded. Given that the panels themselves are electrically isolated from the mains with double insulation inside the inverter, the only ground needed would be the frame, for lightning protection, like a satellite dish. Therefore (a) the AWG 8 ground wire isn't technically needed (it's like running an extension to a power supply that has no 3rd ground prong, so the extension only needs 2 wires), and, the best way to ground the frame for lightning protection is to drop a wire straight down from the panels along the nearest side of the house into a ground rod or water pipe. (the panels are on the opposite side of the house from the service entrance) However, installer guy says code says it should be grounded all the way back to the service entrance. To me this seems less safe than a shorter connection to a ground rod, for lightning protection.
5) My existing ground rod at the service entrance is 1/2". Installer seems to imply I need to drive in a new 5/8" rod to bring it up to present code. Is this correct?
6) I would like to verify that I can simply connect the solar system via a pair of 240V breakers, and there is no need for a sub panel (a requirement for that would make no sense).
Thanks all.
I'll be installing a small semi DIY system (with the help of a pro) in San Jose, CA, using 6 panels and Enphase M215 micro-inverters. The plan is to penetrate the roof under or near the last panel and route the (AC) circuit through the attic. No conduit on the roof. The panels will be on the opposite side of the house from the service entrance. I do power electronics design for a living so I'm no stranger to ohms law and high voltages lol.
The house was built in the late 60s and some of the existing circuits going from the service panel into the attic don't have conduit, but one of them has flexible conduit. The installer guy commented that the city inspector may flag the flexible conduit and require me to rip it out before approving the solar system. He also said that solid conduit is required for the solar branch circuit in the attic.
1) In general (not solar), why is no-conduit OK for some circuits, but flex conduit not OK? It makes no sense to me that either no conduit, or solid conduit, are OK but flex conduit is not OK.
2) Is conduit required for micro-inverter AC output in the attic? Installer says yes. The 6 panels will only put out about 5.5A. I don't understand why 15A lighting branch circuits don't require conduit but micro-inverter outputs would. The micro-inverters will not put out any voltage if they do not sense the presence of the mains. If the breaker feeding it is opened, the micro-inverters will shut down.
3) Installer guy says 10 AWG cable is required, with 8 AWG ground. Why would 10 AWG be required for a circuit that produces < 6A, but 14 AWG is OK for 15A lighting branch circuits?
4) The Enphase M215's are the "IG" (integrated ground) variant, which means they have double insulation internally and do not require a ground connection for Safety to prevent electric shock in the case of internal insulation failure. (Like how some home electronic appliances and laptop chargers have a plug that don't have the third, ground prong). So AFAIK that means only the panel bracketry has to be grounded. Given that the panels themselves are electrically isolated from the mains with double insulation inside the inverter, the only ground needed would be the frame, for lightning protection, like a satellite dish. Therefore (a) the AWG 8 ground wire isn't technically needed (it's like running an extension to a power supply that has no 3rd ground prong, so the extension only needs 2 wires), and, the best way to ground the frame for lightning protection is to drop a wire straight down from the panels along the nearest side of the house into a ground rod or water pipe. (the panels are on the opposite side of the house from the service entrance) However, installer guy says code says it should be grounded all the way back to the service entrance. To me this seems less safe than a shorter connection to a ground rod, for lightning protection.
5) My existing ground rod at the service entrance is 1/2". Installer seems to imply I need to drive in a new 5/8" rod to bring it up to present code. Is this correct?
6) I would like to verify that I can simply connect the solar system via a pair of 240V breakers, and there is no need for a sub panel (a requirement for that would make no sense).
Thanks all.