X
 
  • Time
  • Show
Clear All
new posts
  • sdold
    Moderator
    • Jun 2014
    • 1484

    #76
    Originally posted by Sunking
    You ran the bonding wire in PVC? Is it bare or insulated?
    It's bare, and runs alongside the coax in the same PVC conduit. It was done that way years ago by whoever sold DOT the systems. These are highway advisory radios.

    Originally posted by Sunking
    If bare get it out and run in dirt. You want bare to shunt off lightning current to earth as much as possible. Not to mention it could get warm enough to damage coax. Doubt it but possible.
    I'll tell them that is what is needed. Thanks for the suggestion. I think you talked about this in the QRZ.COM articles, it sounds familiar.

    Comment

    • Mike90250
      Moderator
      • May 2009
      • 16020

      #77
      Originally posted by gvl
      ....Thanks, interesting info. No, at least not without breaking of some concrete at one of the rods.
      Won't be a good ground. For a rebar to be a good ground, it's got to be a 20' length, no way to know poking around if it's a long piece, or a short stub, that won't perform.
      Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
      || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
      || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

      solar: http://tinyurl.com/LMR-Solar
      gen: http://tinyurl.com/LMR-Lister

      Comment

      • SunEagle
        Super Moderator
        • Oct 2012
        • 15192

        #78
        Originally posted by sdold
        I wouldn't use EMT, but what's wrong with PVC?
        Nothing wrong as long as you use a dedicated and properly sized ground wire.

        What Sunking was referring to was that if the conduit installed underground was rigid galvanized steel conduit then you are allowed to use "it" as the ground path instead of the ground wire.

        Comment

        • gvl
          Solar Fanatic
          • Mar 2015
          • 293

          #79
          Originally posted by Sunking
          Yes using a water Auger.
          Won't work, there is about 25 feet of concrete I need to go under with some pool piping in the way, plus I still need to cut just to get under it. Can I just run armored bonding wire along the house wall and not below ground?

          Comment

          • Sunking
            Solar Fanatic
            • Feb 2010
            • 23301

            #80
            Originally posted by sdold
            II'll tell them that is what is needed. Thanks for the suggestion. I think you talked about this in the QRZ.COM articles, it sounds familiar.
            Yes Sir. By code it works, just not best practice to run in PVC. The more copper in contact with dirt, the lower the impedance.
            MSEE, PE

            Comment

            • pellets4fuel
              Member
              • Oct 2014
              • 35

              #81
              Hi,
              So I read through quite a bit of this thread, (though I admit not all) I am trying to determine if I need to run 3 wires from my solar panel combiner box at the array to the house, or just two. From what I am gathering in the earlier part of the thread is that it needs to be 3. Later it gets a little confusing. Especially when the topic of electric fencing, towers, etc all get brought up. I have electric fencing. I also am putting up a tilt up wind generator tower with guide cables 4 ways. It is a 3phase AC axial flux unit. I was told to ground the tower at the base, and bond each set of guide cables together to 4 separate ground rods at the cables anchor points. My solar is going to be near my tower area as well. The location of the tower and array are 400plus feet from the house. So 3 wires (one for bonded ground) or just two that 400plus feet? If I do need the bonded ground wire that can be smaller can't it, and just be a bare wire in the same conduit with the two PV panel wires? On a different note can the wires from combiner box to house through plastic conduit be THHN, or is USE-2 wire required?
              David

              Comment

              • radareclipse
                Member
                • Jul 2015
                • 61

                #82
                Tagged for later.

                Comment

                Working...