    Conduit Wire pulls

    All recent posts have merit, regarding my particular situation. My plan calls for four 45 degree bends in the PVC, due to the terracing of my hillside. The final terrace above the house is where the LFMC would be joined to the PVC. If necessary, I could install a riser and junction box to satisfy the bend restriction, but I believe that would violate the rule allowing the entire DC run from the optimizers through the ACE transition box to the inverter to be considered as an inverter input circuit. Regarding pull lubrication, I checked costs, & Southwire's SimPull wire only cost $.02/ft. more than their standard THWN-2 wire. I had, at one time, considered using UF-B direct burial cable, but it only comes in 2-conductor +ground & 3-conductor + ground configurations ( not a show-stopper, but I only need four #8 DC conductors, and a #10 equipment ground ). I am also wary of direct burial plastic-insulated cables, due to a severe gopher problem on my property. Several times over the years, I have had to replace the 24VAC underground irrigation valve control cables, due to gopher damage.

    Comment

    • JFinch57
      Solar Fanatic
      • Feb 2015
      • 159

      #32
      Originally posted by bcroe
      As I recall, we pulled 4 #6 and a #8 through 220' of pretty much straight 1.5" PVC with
      plenty of wire hanging out the ends. I would hate to try pulling that around even one
      right angle. All that was underground, then an angle and 2 foot riser were glued on to
      the ends to bring it out of the ground to a box. Bruce Roe
      I pulled 2 #3/0 for load, 1 #4 for neutral & 1 #6 for ground through 100+' of 1 1/2" schedule 40 PVC with 2-90s and 1-45 degree bend, 270 degrees total and it meets fill requirements. Pre-lubed the PVC with a rag and plenty of synthetic lube and it went like butter. Note that the neutral bypasses the meter pan/shutoff and goes straight to the load center. The friend that helped me was negative from the start, kept saying "where are we digging the new trench". After it worked he said that he'll never question anything that I do again. Sure, if I did it again it would be 2", but I originally put the conduit in the same trench over a year earlier during the backfill of geothermal lines. My thoughts back then were to have the panel inside my house and connect by all #10s, but then I realized the disconnect and outside production meter requirements. It's an Enphase system, so AC is coming back to the panel. The 3/0 will handle 38KW continuous for future expansion. Elect panels.jpg
      Jeff, BSEE, 22.3KW, 45-240W w/M190, 46-260W w/M250

      Comment

      • bcroe
        Solar Fanatic
        • Jan 2012
        • 5222

        #33
        Originally posted by JFinch57
        I pulled 2 #3/0 for load, 1 #4 for neutral & 1 #6 for ground through 100+' of 1 1/2" schedule 40 PVC with 2-90s and 1-45 degree bend, 270 degrees total and it meets fill requirements. Pre-lubed the PVC with a rag and plenty of synthetic lube and it went like butter.

        AC is coming back to the panel. The 3/0 will handle 38KW continuous for future expansion.
        That is a lot of copper. Be sure to show us the 38KW version. Bruce Roe

        Comment

        • JFinch57
          Solar Fanatic
          • Feb 2015
          • 159

          #34
          Originally posted by bcroe
          That is a lot of copper. Be sure to show us the 38KW version. Bruce Roe
          Bruce, Yes, ~$900 worth from what I remember. Currently installing Phase II, 9.4KW on the roof and it's getting trenched back to the 10.8KW ground mount. Phase III will eventually most likely be another ground mount. The 38KW is a continuous rating on the AC side so DC will be substantially more if I expand to 100%. I could also split it with dual production meters with the other for wind. Leaving my options open at this point. Jeff.
          Jeff, BSEE, 22.3KW, 45-240W w/M190, 46-260W w/M250

          Comment

          • SunEagle
            Super Moderator
            • Oct 2012
            • 15186

            #35
            Originally posted by JFinch57
            Bruce, Yes, ~$900 worth from what I remember. Currently installing Phase II, 9.4KW on the roof and it's getting trenched back to the 10.8KW ground mount. Phase III will eventually most likely be another ground mount. The 38KW is a continuous rating on the AC side so DC will be substantially more if I expand to 100%. I could also split it with dual production meters with the other for wind. Leaving my options open at this point. Jeff.
            Do you have some type of agreement with your POCO that allows you to install a 38kw system?

            Comment

            • JFinch57
              Solar Fanatic
              • Feb 2015
              • 159

              #36
              Originally posted by SunEagle
              Do you have some type of agreement with your POCO that allows you to install a 38kw system?
              Like most states they base it on your usage, and we were approved for the additional ~10KW. I don't see any reason why they wouldn't give us at least a total of 30KW. The house is 100% electric, 6,500 sq ft with 9 tons of geothermal and one of the old 5 ton heat pumps is going in the garage soon. Pumping heat to the basement to keep my mother-in-law warm has been a major contributor to the consumption! Eventually we want to add a pool and I would use solar heat collectors backed up with a Waterfurnace heat pump. That would definitely allow us to max out the 38KW. Here's the historical usage and the 10.8KW of solar was turned on July 2014 (partially in June):Delmarva KWh.JPG
              Jeff, BSEE, 22.3KW, 45-240W w/M190, 46-260W w/M250

              Comment

              • SunEagle
                Super Moderator
                • Oct 2012
                • 15186

                #37
                Originally posted by JFinch57
                Like most states they base it on your usage, and we were approved for the additional ~10KW. I don't see any reason why they wouldn't give us at least a total of 30KW. The house is 100% electric, 6,500 sq ft with 9 tons of geothermal and one of the old 5 ton heat pumps is going in the garage soon. Pumping heat to the basement to keep my mother-in-law warm has been a major contributor to the consumption! Eventually we want to add a pool and I would use solar heat collectors backed up with a Waterfurnace heat pump. That would definitely allow us to max out the 38KW. Here's the historical usage and the 10.8KW of solar was turned on July 2014 (partially in June):[ATTACH=CONFIG]6684[/ATTACH]
                That makes sense to me. Glad they allowed you to increase your system. Thanks for the data.

                Comment

                • bcroe
                  Solar Fanatic
                  • Jan 2012
                  • 5222

                  #38
                  Originally posted by JFinch57
                  Like most states they base it on your usage, and we were approved for the additional ~10KW. I don't see any reason why they wouldn't give us at least a total of 30KW. The house is 100% electric, 6,500 sq ft with 9 tons of geothermal and one of the old 5 ton heat pumps is going in the garage soon. Pumping heat to the basement to keep my mother-in-law warm has been a major contributor to the consumption! Eventually we want to add a pool and I would use solar heat collectors backed up with a Waterfurnace heat pump. That would definitely allow us to max out the 38KW. Here's the historical usage and the 10.8KW of solar was turned on July 2014 (partially in June):[ATTACH=CONFIG]6684[/ATTACH]
                  My estimate is you are running 35,000 to 45,000 KWH a year, so about a 30 KW PV system would
                  handle that in the SW desert. I'm wondering how much things are degraded by clouds in MD, do
                  you have a handle on that now? Here there are extra strings of panels to raise cloudy output; they
                  are facing the rising and setting sun, so under good sun they deliver their peak power at a different
                  time than the south array. Overall this about matches a desert sky output. This is actually fairly
                  economical since inverters and everything downstream don't need to increase in size, but that is
                  only true with a simple string system.

                  And then there is the snow. One approach is do well enough in 9 months to write off the snow
                  months. Not happening here; most snow at night was cleared at dawn. That can become a
                  time consuming project with a large system, and you may also need to bring equipment to move
                  the piles of snow if they become high enough to block the panels. Guess you have experience at
                  work on this scale, how did that go? My conclusion is all panels will be set near or at vertical for
                  the snow season, but that will take rework here. I also plan to mount panels landscape with a gap,
                  so snow will only slide 39" and off, instead of 63" and onto another panel. Bruce Roe

                  Comment

                  • JFinch57
                    Solar Fanatic
                    • Feb 2015
                    • 159

                    #39
                    Originally posted by bcroe
                    My estimate is you are running 35,000 to 45,000 KWH a year, so about a 30 KW PV system would
                    handle that in the SW desert. I'm wondering how much things are degraded by clouds in MD, do
                    you have a handle on that now? Here there are extra strings of panels to raise cloudy output; they
                    are facing the rising and setting sun, so under good sun they deliver their peak power at a different
                    time than the south array. Overall this about matches a desert sky output. This is actually fairly
                    economical since inverters and everything downstream don't need to increase in size, but that is
                    only true with a simple string system.

                    And then there is the snow. One approach is do well enough in 9 months to write off the snow
                    months. Not happening here; most snow at night was cleared at dawn. That can become a
                    time consuming project with a large system, and you may also need to bring equipment to move
                    the piles of snow if they become high enough to block the panels. Guess you have experience at
                    work on this scale, how did that go? My conclusion is all panels will be set near or at vertical for
                    the snow season, but that will take rework here. I also plan to mount panels landscape with a gap,
                    so snow will only slide 39" and off, instead of 63" and onto another panel. Bruce Roe
                    Bruce, It looks like we've pretty much hijacked this thread while awaiting the final pictures! The 38KW AC rating was based on maxing out the conduit for load and then deciding if I was wasting money or possibly with the pool addition we would need that much. I went with the latter, bit the bullet, and put in the 3/0. (I was waiting for the electrical inspector to question the #4 neutral but he never did. Annotated it on the line diagram as balanced generation and neutral needed for Enphase Envoy communications only. Could have used something even smaller if it fit the lug). It would be a real bear to change it down the road and the savings about $100-150 to go with 2/0. I was able to deal with the snow on the ground mounted system, only loosing a couple days production. The roof mount will be a different story, even at a fairly low pitch doubt I'll be going up there with snow. The Phase II roof panels will be battling about 20-30% shade unless I can convince my wife to top the trees and I don't see that happening. Should be complete in about 1 month. Eventually Phase III will be east facing ground mounted and if needed Phase IV west facing ground mounted. I have to recover a bit from Phase II before doing any more. Here's a picture of the 3/0 feed connecting to the 400A generator transfer switch. The two white wires through the knockout are for the Envoy receptacle and go back to the outside load center. I tagged one as black (didn't have any black on hand). Jeff200A Feed.jpg
                    Jeff, BSEE, 22.3KW, 45-240W w/M190, 46-260W w/M250

                    Comment

                    • bcroe
                      Solar Fanatic
                      • Jan 2012
                      • 5222

                      #40
                      Originally posted by JFinch57
                      Bruce, It looks like we've pretty much hijacked this thread

                      Eventually Phase III will be east facing ground mounted and if needed Phase IV west facing ground
                      mounted. I have to recover a bit from Phase II before doing any more. Jeff
                      Yea, hijacked, don't know how to change that. I'll be watching for your east & west facing, to
                      compare to mine. If they are strings, one smaller inverter should handle both. That also
                      presents a lower total (peak) output to the PoCo, IV will add nothing. Bruce

                      Comment